MultiPlus II 4k5 doesn't seem to follow my grid setpoint in ESS

MultiPlus-II 4k5 doesn’t seem to be following my grid setpoint in ESS

Whatever value I set, the AC input goes straight through to AC out

Could you please add some more information about your system and maybe a screenshot?

what settings do you want to see ?

It is a standard installation multiplus II 4k5 AC in to grid, AC out 1 to my own home. No energie meter but that shouldn’t be a problem I think since all ac loads are at AC out 1 and with the following settings

I have another multiplus II 5000 and that on works for years. Settings look all the same

There are a lot more settings than that screen. What is the inverter configuration? Detail the components, wiring etc.
At the moment it is guesswork.
The quality of an answer is determined by the quality of the question.

I understand but there are so manu sub menu’s. What settings should I paste ?

image

A difference with my other multiplus is the external current clamp but that is because there are ac loads in front of the multi what is not the case for this multi

Start with the inverter configuration file and how the system is built.

This is te ve config ESS configuration

What battery do you have? Is it visible in dvcc and selected as the managing battery? The battery monitor is the multiplus. This should be a managed battery, or if an unmanaged battery, you should use a shunt as the multiplus is inaccurate with internal dc measurements.


There is no BMS connected but that is the same with my other multiplus. My other installation does have two shunts available.
In this config I don’t have them yet. The connection to the batteries is instable so removed them from this installation.

The charge voltage setting only applies to a bms, no value choosing this with an unmanaged battery.
What do you mean by unstable connection?
ESS relies on a reliable soc, without a shunt that won’t be the case.
You need to post console screenshots showing the issue you are seeing. It really is unclear, but if you have an unstable system with an inaccurate soc ess won’t work. Best to fix all the challenges first.

I removed the connection to the battery since it disconnects all the time. WIthout this battery connected all notifications are gone so multiplus should be in control

Just changed the battery monitor to

image

but since there is only one device is expect that automatic would be the same

I suggest you get a professional to help you, there seems to be an underlying issue with the installation. If you lack a stable foundation, the battery is critical, then problems will follow. This isn’t something we can troubleshoot over the internet.

The current setup should be stable since there is only the multiplus. No other devices, no notifications so looks like a setting I missed.

Hmm, it looks that changing the battery monitor from automatic to the multiplus did the trick but it took a while before it started acting on the grid set point.

image

Hi Nick,

Thanks a lot. Sorry for the confusion but you kept me searching and finally it started working. Learned that I need some patience when I change values.

WIth my other multiplus I’m used it starts acting immediatly when changing the grid set point but here it looks like change the battery monitor takes some time before the multiplus starts acting on it.

Always a good idea to set the monitor manually, if there was a change in the system, I have seen it get stuck on an incorrect setting. Easy fix fortunately :slight_smile: