Hello everyone,
I’m looking for first-hand experience with a Victron installation using Enphase microinverters. My goal is to understand how to use Frequency Shifting and whether automatically disconnecting the AC input could be a solution to prevent export to Enedis.
My installation:
-
Inverter/charger: Victron MultiPlus-II 48/5000/70-50.
-
Solar PV installation: around 6 kWp, with 20 Enphase IQ7-60-2-FR microinverters ( rated power: 240 W) giving 4800W in total.
-
Enphase relays: 2 IQ Relays.
-
Gateway: Envoy-S Standard, non-Metered.
-
Battery: LiFePO4, 16 cells of 314 Ah in series, giving approximately 16 kWh.
-
Monitoring: Raspberry Pi running Venus OS 3.66, connected to the MultiPlus-II via MK3-USB.
Current wiring;
The connection is as follows:
Enedis → AC-IN on the MultiPlus-II → AC-OUT on the MultiPlus-II → the home’s main electrical panel.
The panels are connected as follows:
PV → Enphase microinverters → IQ Relays → solar protection → main panel.
The Enphase units are therefore connected on the AC-OUT side of the MultiPlus-II. This can power the entire house when the Enedis supply is disconnected.
I use ESS mode and have enabled the zero feed-in option in Venus OS. However, despite these settings, I still see power being exported to the grid when the battery is almost full.
I don’t have a dedicated Victron energy meter on the grid connection: I use the MultiPlus-II’s internal measurement on AC-IN. The Enphase gateway is a non-Metered version.
Automatic disconnection of the AC input:
Apparently, as long as AC-IN (Enedis) is connected, the frequency on AC-OUT is synchronised with that of the grid, which would prevent the MultiPlus-II from applying Frequency Shifting; this would therefore only be possible in island mode, when AC-IN is disconnected.
In VictronConnect, I noticed that it is possible to configure the AC input to disconnect under certain conditions, including:
-
Disconnect AC input on: battery voltage (other options available…)
-
AC input disconnected if battery voltage is above: an adjustable value.
Can this function be used to automatically disconnect Enedis when the battery reaches a certain voltage, then run the MultiPlus-II in island mode and thus use "Frequency Shifting"?
Does this method seem suitable for preventing grid export, or is there a better solution?