Hi,
I have an off-grid MultiPlus-II 48/5000 with Cerbo GX, DVCC and two Skanbatt 51.2 V/100 Ah LiFePO4 batteries. Generator is a Hyundai DHY8600SE 230 V/50 Hz AVR diesel generator.
The issue is intermittent generator acceptance.
The Multi sometimes:
- accepts generator AC normally,
- starts charging,
- then drops AC/charging,
- but generator continues running and its breaker remains on,
- and the Multi may then remain disconnected for 5–10+ minutes.
Sometimes it eventually reconnects by itself and subsequently charges completely normally. Earlier I often saw it “hunt” between charging/disconnected states but it would normally reconnect quite quickly.
Generator voltage/frequency appear stable. I also tested a 2 kW resistive heater directly on the generator without problems.
BMS CCL has been stable at 40 A for weeks. I haven’t observed a CCL change coinciding with the problem. I have previously found that lowering the manual DVCC charge-current limit sometimes seems to help it connect.
Original factory Multi settings included:
- Wide frequency 45–65 Hz: ON
- UPS: ON
- Dynamic Current Limiter: OFF
- Weak AC: OFF
- AC input limit: 25 A
I’ve now changed:
- UPS: OFF
- Dynamic Current Limiter: ON
On the latest test it connected and charged at approximately 1 kW, then dropped out again and didn’t reconnect for several minutes. I eventually got “Power not detected at AC input.”
Questions:
- Should a MultiPlus continuously retry/reconnect if generator AC becomes acceptable again?
- Does “Power not detected at AC input” necessarily mean 0 V physically at AC-in, or can it occur when AC is present but rejected?
- Could DVCC/Controlling BMS influence this even with constant CCL?
- Is Weak AC ON the next sensible test?
- Is there any diagnostic/log showing the actual reason MultiPlus rejects AC, beyond displayed voltage and frequency?
My next test will be to check AC-in voltage/frequency and Active Input status immediately after the disconnect.
Thanks for any suggestions.