I have a small system consisting of a Victron MultiPlus II 3000 GX and a Pytes V5 battery with a capacity of 5 KW/h.
The system operates on the AC side.
The system was switched off for a few days because of electrical work (for the first time). When I bring the MultiPlus 2 back into operation in the following order:
Battery
MultiPlus
Circuit breaker
The system starts up, but after 20 to 30 seconds the circuit breaker trips. However, I haven’t changed anything on the MultiPlus’s dedicated circuit.
Could it be that I switched the circuit breaker on too soon after turning on the MP2?
The VRM Portal briefly showed a low battery charge level. If I switch it on again, the same thing happens. The circuit breaker trips.
It’s a Hager MBS116. It was newly installed when the system was commissioned. Could the B curve be too sensitive?
You can always fit a bigger fuse — an M12 bolt definitely won’t blow.
Finding out what’s drawing the current is more interesting. Is the fuse on the input or output? How is the system configured? What loads are connected on the protected side? Is the battery charging at full power? Is the charging current set sensibly?
A B16 is fine for an MP2-3000. A B/C25 is better, though. But that mainly depends on the cable cross-section.
The MultiPlus is connected via AC-in. The supply cable is 3 m long, NYM 3x2.5mm². No loads are connected to the MultiPlus. I haven’t changed any of the settings. Since the initial setup:
Have you measured at the Multi’s DC terminals to see what the Pytes batteries are actually reporting? A Multi without a decent DC supply can easily trip the upstream fuse… It could of course also be that the Multi is trying to charge the batteries and causing the B16 to trip. I’d be surprised if the breaker were tripping thermally rather than because of a short circuit, but you could try turning the charging current down…
This is what I was wondering as is is happening after 20-30seconds so it suggests thermal. So most likely a 9kw load for that long…
So unless someone has changed the input current limit and the breaker is on the input, I cannot think of why this would happen. Even then if there is no load on the output reaching that on charge alone is not possible on a 3kVA.
If it was inrush/short circuit it would be an almost almost immediate trip.