MultiPlus II 3000 GX was off for a few days; the fuse trips when I start it

Hello.

I have a small system consisting of a Victron MultiPlus II 3000 GX and a Pytes V5 battery with a capacity of 5 KW/h.

The system operates on the AC side.

The system was switched off for a few days because of electrical work (for the first time). When I bring the MultiPlus 2 back into operation in the following order:

  1. Battery
  2. MultiPlus
  3. Circuit breaker

The system starts up, but after 20 to 30 seconds the circuit breaker trips. However, I haven’t changed anything on the MultiPlus’s dedicated circuit.

Could it be that I switched the circuit breaker on too soon after turning on the MP2?

The VRM Portal briefly showed a low battery charge level. If I switch it on again, the same thing happens. The circuit breaker trips.

It’s a Hager MBS116. It was newly installed when the system was commissioned. Could the B curve be too sensitive?

You can always fit a bigger fuse — an M12 bolt definitely won’t blow.

Finding out what’s drawing the current is more interesting. Is the fuse on the input or output? How is the system configured? What loads are connected on the protected side? Is the battery charging at full power? Is the charging current set sensibly?

A B16 is fine for an MP2-3000. A B/C25 is better, though. But that mainly depends on the cable cross-section.

Hello.

The MultiPlus is connected via AC-in. The supply cable is 3 m long, NYM 3x2.5mm². No loads are connected to the MultiPlus. I haven’t changed any of the settings. Since the initial setup:

  • GRID tab
    • Germany VDE-AR-N-4105:2018-11, internal NS protection
    • WARNING, CAN ONLY BE SET ONCE!!
  • Inverter tab
    • DC input low – shut down:49
    • DC low – restart:51
    • DC input low pre-alarm51
    • PowerAssist enabled
  • Charger tab
    • Enable charger
    • Battery type:Lithium Iron Phosphate (LiFePo4)
    • Absorption:56,80 V
    • Float voltage:56,00 V
  • Virtual switch tab
    • Do not use VS
  • Assistants tab
    • ESS (Energy Storage System)

I had set the battery discharge limit to 40% via the console, specifically for those few days.

I’ve integrated an OpenDTU solely to display the PV yield.

The thing that has changed
So needs to be checked. If you don’t think it’s the inverter related circuit.

However, that is a contradiction something was changed in the circuit. Did you swap it back to the other 16A to troubleshoot?

Nothing at all is connected to the Multiplus II circuit. Its own fuse, with no upstream RCD etc.

Meter

Main switch

Multiplus fuse

Multiplus.

Can you clarify. Is it the fuse between the battery and the inverter that is tripping?

Or this one? And this Type B is on the input of the inverter not the output

Have you measured at the Multi’s DC terminals to see what the Pytes batteries are actually reporting? A Multi without a decent DC supply can easily trip the upstream fuse… It could of course also be that the Multi is trying to charge the batteries and causing the B16 to trip. I’d be surprised if the breaker were tripping thermally rather than because of a short circuit, but you could try turning the charging current down…

As Netrange already mentioned, that sounds more like a lack of DC voltage at the Multi.

This is what I was wondering as is is happening after 20-30seconds so it suggests thermal. So most likely a 9kw load for that long…
So unless someone has changed the input current limit and the breaker is on the input, I cannot think of why this would happen. Even then if there is no load on the output reaching that on charge alone is not possible on a 3kVA.
If it was inrush/short circuit it would be an almost almost immediate trip.

Then there is this which back up the idea

:+1: I’m pleasantly surprised by how accurately the translation handles even technically “detailed” comments. In the past, it was always difficult to translate them from … in my case, from German … into English. :+1: