I have 2 Multiplus II’s in 3-phase setup (1 phase unused). Suddenly this morning they stopped working with a disco of LED lights. How do i start to debug this?
I tried turning on and of both multiplusses and the cerbo GX but no improvement.
Have you carried out any updates?
What changes were made to the system?
Have there been any building works in your area?
The grid power dropped around the same time. But I have still 80% of battery so don’t understand why that would be a problem.
If the utility company connected one of the phases incorrectly, L1 could now be L2.
Please check the wiring and post photos of your wiring (the MP connection) here.
Are the LEDs of the slave flashing ? If yes: its an boot loader problem of this device.
The Master then reports missing device.
Try to reflash the slave via VEFlash. If this does not work you have a faulty MP2.
No slave just has all leds on, no blinking.
The network operator only offers a single phase. Connected to both MPs.
So not supported.
If the MPs are programmed as 2 of three phases they are expecting a phase angle between them and with one feed that would not be happening. Are you sure they are not in parallel
You have 3 error codes there.
The last 2 (error 1 and 3). First one. Not sure there. But will be the most important one. Don’t think I have ever seen it with all three flashing with the inverter led.
The other also with all LEDs lit is unusual.
What was listed on the GX?
I can no longer access the GX because the power is out, and so is the internet connection.
This system has been running successfully like this for 1.5 years. Why would it suddenly be showing this error now?
Is this US or UK?
Could be a split-phase system that’s no longer working properly due to a substation failure.
we can only make progress here with a wiring diagram and more information.
This isn’t a three-phase system, nor one “with a phase missing”. If there’s actually only one phase coming from the utility, then these are two MultiPlus units in parallel, but it’s still only a single-phase system.
So please also provide a screenshot from Ve.config showing the system configuration.
The B MultiPlus has apparently ended up in the bootloader — something must have happened before that.
The A won’t start because it’s missing the B (which can also happen with MultiPlus units connected in parallel on one phase).
Kind regards,
Broesel
Could it be the lightning? ![]()
So its not a 3 phase system
Its just two inverters on 1 ac input and both separate output, if configured wrong its unsuported
lightning could be the problem
I did set it up as 3-phase system in VE.Bus System Configurator.
What could be the solution?
Dude, I don’t think it was ever really right when you set it up. They should have just been in parallel. Anyway. It was working but now it’s not. I suspect having such a long run and lightning has killed one of the units. Do you still have ve config adaptor?
I would try to establish comms and get the one without all the warnings to work as a single unit for the time being to get some power back on.
The other may well need replacing, let us know if you can get it talking.
Yes, on Blitzortung.org or aldis.at you can see any lightning strikes in your area or request data (insurance companies use this to assess alleged damage).
A single-phase parallel system needs both MPs to function, so remove the apparently faulty Multi from the system.
You can’t have a 3-phase system, you have two inverters and a single-phase grid.
You cannot configure it this way.
Victron also do not support two independent systems on one common battery, you can’t parallel with loads split.
It is never going to work, please get a professional to help you and configure it to a supported topology.
It’s possible an EMP cause a disruption. I have experienced that before. But a simple shut down of all components and restart cleared the issue
Your battery at 80% with a 49v is a bit low even if that is 15s battery. At least it doesn’t look accurate.