# Multiplus (I) will not switch on

**URL:** <https://community.victronenergy.com/t/multiplus-i-will-not-switch-on/26345>\
**Category:** Q&A and troubleshooting\
**Tags:** expert, offgrid, multiplus\
**Created:** [24 March 2025 08:47 UTC](https://community.victronenergy.com/t/multiplus-i-will-not-switch-on/26345 "2025-03-24T08:47:48Z")\
**Posts on this page:** 14\
**Page:** 1

<div class="post-metadata">

**Author:** ![selwyn](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/selwyn/32/24068_2.png) [@selwyn](https://community.victronenergy.com/u/selwyn)\
**Post date:** [24 March 2025 08:47 UTC](https://community.victronenergy.com/t/multiplus-i-will-not-switch-on/26345/1 "2025-03-24T08:47:48Z")

</div>

I have a new installation with a Multiplus 48/3000/35-16 (brand new older model) and a CCGX. I updated everything to the latest production versions (as at 8 March 2025 - not Beta versions), but when I installed it (on a remote off-grid site in Hwange Game Reserve without internet), I had to unplug the VE.bus cable to get the Multiplus to start. Once started, it seemed to work fine when I plugged the cable back in.

Multiplus 48/3000/35-16 version 555  
CCGX version 3.54  
BlueSolar 150/45 version 1.64  
8 x 350W ARTsolar solar panels (4 strings of 2) 2800Wp  
BlueNova B52V-154-8k (Pre-NG but refurbished to NG) 154Ah version 5.5  
Generator was not connected

The settings I used:  
Battery monitor enabled at 95%  
Other grid code with wide input frequency and voltage ranges  
Shut down on SOC enabled (10%/20%), no power assist, AES not enabled  
Lithium battery  
No VS  
No assistants

I need a solution. I cannot expect my customer to disconnect cables to switch the system on.

The problem seems similar to this post: [Firmware upgrade on Quattro to latest version 555 - With Beta 3.60-25](https://community.victronenergy.com/t/firmware-upgrade-on-quattro-to-latest-version-555-with-beta-3-60-25/24000)

---

<div class="post-metadata">

**Author:** ![nickdb](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/nickdb/32/51440_2.png) [@nickdb](https://community.victronenergy.com/u/nickdb)\
**Post date:** [24 March 2025 10:18 UTC](https://community.victronenergy.com/t/multiplus-i-will-not-switch-on/26345/3 "2025-03-24T10:18:20Z")

</div>

The important thing to check is the remote multi software switch on the GX is not set to “off”  
If that is indeed set to ON, then there is a different issue.  
If this ccgx was used before, you may be advised to reset it to default in case there are conflicting settings enabled.  
For the most part this shouldn’t happen and isn’t a known problem on production versions.

The GX also provides comms from the battery, so if it is seeing something that conflicts with the rest of the system then it could cause this issue.

Mixing old gear is always a challenge, but this does sound possibly like a configuration problem.

---

<div class="post-metadata">

**Author:** ![selwyn](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/selwyn/32/24068_2.png) [@selwyn](https://community.victronenergy.com/u/selwyn)\
**Post date:** [24 March 2025 11:11 UTC](https://community.victronenergy.com/t/multiplus-i-will-not-switch-on/26345/5 "2025-03-24T11:11:04Z")

</div>

Thank you, I will try this when I can get to the site

---

<div class="post-metadata">

**Author:** ![nickdb](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/nickdb/32/51440_2.png) [@nickdb](https://community.victronenergy.com/u/nickdb)\
**Post date:** [24 March 2025 11:12 UTC](https://community.victronenergy.com/t/multiplus-i-will-not-switch-on/26345/6 "2025-03-24T11:12:04Z")

</div>

You are also welcome to pull the remote config file and post it here, helps with detail.

---

<div class="post-metadata">

**Author:** ![selwyn](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/selwyn/32/24068_2.png) [@selwyn](https://community.victronenergy.com/u/selwyn)\
**Post date:** [24 March 2025 11:42 UTC](https://community.victronenergy.com/t/multiplus-i-will-not-switch-on/26345/7 "2025-03-24T11:42:07Z")

</div>

[2025-03-09 Kapula\_Platform\_7c386652082a\_inst\_ttyO1\_Interfaces\_Mk2\_Tunnel.rvsc](https://community.victronenergy.com/uploads/short-url/eDjifqWQVqzieaagwOvFaJv9bJJ.rvsc) (4.4 KB)

---

<div class="post-metadata">

**Author:** ![nickdb](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/nickdb/32/51440_2.png) [@nickdb](https://community.victronenergy.com/u/nickdb)\
**Post date:** [24 March 2025 11:50 UTC](https://community.victronenergy.com/t/multiplus-i-will-not-switch-on/26345/8 "2025-03-24T11:50:13Z")

</div>

Do you recall what the SOC/Voltage of the battery was at the time, or if it was reporting low/no DCL etc?  
The config is fairly vanilla, nothing obvious.

---

<div class="post-metadata">

**Author:** ![selwyn](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/selwyn/32/24068_2.png) [@selwyn](https://community.victronenergy.com/u/selwyn)\
**Post date:** [24 March 2025 12:57 UTC](https://community.victronenergy.com/t/multiplus-i-will-not-switch-on/26345/9 "2025-03-24T12:57:11Z")

</div>

The battery was at 97% when I installed the system. There were no alarms.  
I ran the system overnight before taking it to site and was able to record this on VRM. The battery started at 99% (53.51V) and ended at 97% (53.13V).

> **[VRM Portal - Victron Energy](https://vrm.victronenergy.com/installation/731939/share/941b8d02)**
>
> VRM by Victron Energy gives realtime insights into your energy. Monitor complete energy systems, tanks and temperatures remotely.

---

<div class="post-metadata">

**Author:** ![selwyn](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/selwyn/32/24068_2.png) [@selwyn](https://community.victronenergy.com/u/selwyn)\
**Post date:** [24 March 2025 14:04 UTC](https://community.victronenergy.com/t/multiplus-i-will-not-switch-on/26345/11 "2025-03-24T14:04:11Z")

</div>

Yes, everything powers up when the VE.bus cable is unplugged, and keeps running when it is plugged back in.

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [24 March 2025 15:03 UTC](https://community.victronenergy.com/t/multiplus-i-will-not-switch-on/26345/13 "2025-03-24T15:03:38Z")

</div>

I would start with the CCGX downgrade to 3.42 or 3.40. the older units struggle for space and other resources on the newer FW.  
Maybe downgrade the inverter to 449 (available on professional)

The other option to [try is cut pin 7 on the ve bus cable but this is a last resort](https://www.victronenergy.com/media/pg/CCGX/en/troubleshooting.html#UUID-3b79e679-4b70-7be3-b25a-2dbf49cd3dac) stab on the dark idea.

---

<div class="post-metadata">

**Author:** ![nickdb](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/nickdb/32/51440_2.png) [@nickdb](https://community.victronenergy.com/u/nickdb)\
**Post date:** [24 March 2025 15:08 UTC](https://community.victronenergy.com/t/multiplus-i-will-not-switch-on/26345/14 "2025-03-24T15:08:20Z")

</div>

LOM is irrelevant to the system starting or not. There is no ESS either which would rely on it.  
It could affect a running genset from being accepted, but since it was disconnected, there’s no assistant, its irrelevant in this case and unrelated to why an inverter with charged battery would not start.

---

<div class="post-metadata">

**Author:** ![selwyn](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/selwyn/32/24068_2.png) [@selwyn](https://community.victronenergy.com/u/selwyn)\
**Post date:** [24 March 2025 15:20 UTC](https://community.victronenergy.com/t/multiplus-i-will-not-switch-on/26345/15 "2025-03-24T15:20:19Z")

</div>

I do have LOM(B) enabled.

---

<div class="post-metadata">

**Author:** ![selwyn](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/selwyn/32/24068_2.png) [@selwyn](https://community.victronenergy.com/u/selwyn)\
**Post date:** [25 March 2025 16:41 UTC](https://community.victronenergy.com/t/multiplus-i-will-not-switch-on/26345/16 "2025-03-25T16:41:08Z")

</div>

> [@nickdb](#):
>
> The important thing to check is the remote multi software switch on the GX is not set to “off”

I can confirm that the remote multi software switch is set to “on”

---

<div class="post-metadata">

**Author:** ![selwyn](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/selwyn/32/24068_2.png) [@selwyn](https://community.victronenergy.com/u/selwyn)\
**Post date:** [14 May 2025 10:57 UTC](https://community.victronenergy.com/t/multiplus-i-will-not-switch-on/26345/17 "2025-05-14T10:57:40Z")

</div>

In the Cerbo Manual FAQs (19.2.20 Q20) you can remove pin 7 from the VE.Bus connector to allow the Multiplus to startup with the cable to the GX device connected.

This fixed my problem, but I cannot explain why I had a problem as the GX device is powered from the battery.

---

<div class="post-metadata">

**Author:** ![system](https://europe1.discourse-cdn.com/victron/original/1X/21a9a7b5db7c6339715f993568736a7053199995.png) [@system](https://community.victronenergy.com/u/system)\
**Post date:** [28 May 2025 10:57 UTC](https://community.victronenergy.com/t/multiplus-i-will-not-switch-on/26345/18 "2025-05-28T10:57:43Z")

</div>

Closed on 28 May 2025 10:57 UTC

This topic was automatically closed 14 days after the last reply. New replies are no longer allowed.