Complex AC and bonding system on a yacht; interaction between the PE (Protective Earth) paths, a Isolation Transformer, a Rotary Switch, a MultiPlus, and a Generator
Concern about the Multiplu’s cyclic rejection of generator power and the PE paths during inversion-
1. PE Paths and Bonding System Current Setup,
PE Bar #1 connects:
-
Isolation transformer output (PE IN = PE OUT, 0Ω)
-
MultiPlus input
-
Air conditioners
-
Generator
Bonding Bar #2 connects:
-
Battery negative
-
All metal masses on the boat (isopotential) Before Interconnect PE Bar #1 and Bonding Bar #2, to eliminate potential voltage differences between the AC and DC grounding systems.
Timing and method matter.
-–
2. MultiPlus Behavior and Generator Rejection
OBSERVATIONS
- Cyclic rejection of generator power only occurs when:
-
The generator is the source.
-
Air conditioners are running.
- No cycling occurs when:
-
The transformer is the source.
-
The generator is the source but air conditioners are off.
-
The generator is the source, the inverter in in “charge only”, snd the Air Conditioners are runing.
POSIBLE CAUSES:
A. PE Path Differences During Inversion**
When the MultiPlus inverts, it disconnects the source PE (from the transformer/generator) and bonds its output PE to neutral.
This creates two separate PE paths:
-
Air conditioners: PE → Generator → PE Bar #1.
-
MultiPlus output**: PE → Bonded to neutral (floating relative to generator PE).
As PE Bar #1 and Bonding Bar #2 are not interconnected yet, this can create a potential difference between the generator PE and the MultiPlus output PE, leading to:
Ground loops
Noise or voltage fluctuations
The Multiplus detecting “poor energy quality” and cycling
B. Generator Power Quality
- Generators (especially AVR types) can have voltage/frequency fluctuations under load.
- The MultiPlus may be sensitive to these fluctuations, especially if the PE reference is unstable due to the split PE paths.
C. Load Imbalance
- Air conditioners are inductive loads and can cause voltage drops or phase shifts.
- If the generator struggles ( not the case it is 12 KVA)with these loads, the MultiPlus may detect instability and switch to inversion.
-–
Recommended actions?