# Multiple fronius ac couple

**URL:** <https://community.victronenergy.com/t/multiple-fronius-ac-couple/6741>\
**Category:** DIY\
**Tags:** fronius, 3-phase, offgrid\
**Created:** [7 October 2024 17:44 UTC](https://community.victronenergy.com/t/multiple-fronius-ac-couple/6741 "2024-10-07T17:44:09Z")\
**Posts on this page:** 7\
**Page:** 1

<div class="post-metadata">

**Author:** ![offgrideu](https://avatars.discourse-cdn.com/v4/letter/o/45deac/32.png) [@offgrideu](https://community.victronenergy.com/u/offgrideu)\
**Post date:** [7 October 2024 17:44 UTC](https://community.victronenergy.com/t/multiple-fronius-ac-couple/6741/1 "2024-10-07T17:44:09Z")

</div>

Hello,

I came across 2 fronius symo 12.5 3 phase basically free, i have 30 kwp panels that the fronius will connect to.

Can 2 fronius ac couple with my 3x 48/15000kva multiplus ii off grid victron and use the microgrid frequency shifting?

Thanks!

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [7 October 2024 18:06 UTC](https://community.victronenergy.com/t/multiple-fronius-ac-couple/6741/2 "2024-10-07T18:06:11Z")

</div>

@offgrideu  
Yes.  
And you already are observing the 1:1 rules.

---

<div class="post-metadata">

**Author:** ![offgrideu](https://avatars.discourse-cdn.com/v4/letter/o/45deac/32.png) [@offgrideu](https://community.victronenergy.com/u/offgrideu)\
**Post date:** [7 October 2024 18:56 UTC](https://community.victronenergy.com/t/multiple-fronius-ac-couple/6741/3 "2024-10-07T18:56:07Z")

</div>

Yes you and i already discussed that, thank you for all the support!

---

<div class="post-metadata">

**Author:** ![grua](https://avatars.discourse-cdn.com/v4/letter/g/ec9cab/32.png) [@grua](https://community.victronenergy.com/u/grua)\
**Post date:** [7 October 2024 19:22 UTC](https://community.victronenergy.com/t/multiple-fronius-ac-couple/6741/4 "2024-10-07T19:22:10Z")

</div>

Please also note the minimum requirements for the battery size with regard to the factor 1 rule

---

<div class="post-metadata">

**Author:** ![offgrideu](https://avatars.discourse-cdn.com/v4/letter/o/45deac/32.png) [@offgrideu](https://community.victronenergy.com/u/offgrideu)\
**Post date:** [7 October 2024 19:39 UTC](https://community.victronenergy.com/t/multiple-fronius-ac-couple/6741/5 "2024-10-07T19:39:03Z")

</div>

Thank you, yes that was discussed in a seperate post.

Will the cerbo see both inverters? Or treat them as one? (for vrm monitoring display and logging purposes)

---

<div class="post-metadata">

**Author:** ![dognose](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/dognose/32/968_2.png) [@dognose](https://community.victronenergy.com/u/dognose)\
**Post date:** [8 October 2024 06:42 UTC](https://community.victronenergy.com/t/multiple-fronius-ac-couple/6741/6 "2024-10-08T06:42:34Z")

</div>

The cerbo will show both inverters individually as two devices, you can create custom dashboard-graphs etc.

However, on the Dashboard there is only “One” PV-Inverter tile (One on the AC-IN side, one on the AC-out side), that will always be the sum of all connected PV - Inverters on the respective side.

---

<div class="post-metadata">

**Author:** ![system](https://europe1.discourse-cdn.com/victron/original/1X/21a9a7b5db7c6339715f993568736a7053199995.png) [@system](https://community.victronenergy.com/u/system)\
**Post date:** [27 November 2024 13:50 UTC](https://community.victronenergy.com/t/multiple-fronius-ac-couple/6741/7 "2024-11-27T13:50:38Z")

</div>

Closed on 27 November 2024 13:50 UTC

This topic was automatically closed 14 days after the last reply. New replies are no longer allowed.