Hello Community,  
I have 4x ET112 Energy Meters.  
I changed the ID of 4 of the units to 2,3,4,5. I am leaving 1 open for the 5th meter which is yet to arrive. The 4 all are displayed in the UCS software and not conflicting.  
When I plug them in to the Cerbo GX via the same RS485 to USB adapter, nothing happens, they are not seen at all. Removing 3 and retaining one allows the communication to return to the 1 device. Plugging the other 3 in again stops the communication.  
What’s the deal here? Anyone actually had this working with multiple units on one rs485 to USB adapter as stated in the manual? I tried adding terminating resistor, but it shouldn’t be required because it works flawlessly on my pc.

Here’s the section from the manual i’m refering to:

> 2.4. Multiple Energy Meters in one system  
> To connect multiple Energy Meters, wire each meter to a separate RS485 to USB interface, which are then each plugged into a separate USB socket on the GX device.  
> Connecting multiple meters to the same RS485 to USB interface cable is not possible.  
> Please note that you can connect the ET112 in parallel, but need to change the modbus address to another number using the  
> UCS Desktop configuration software from the supplier, which is free to download from the Carlo Gavazzi Web site.

---

<div class="post-metadata">

**Author:** ![DuivertNL](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/duivertnl/32/279_2.png) [@DuivertNL](https://community.victronenergy.com/u/DuivertNL)\
**Post date:** [9 November 2024 07:18 UTC](https://community.victronenergy.com/t/multiple-et112-in-parallel-on-single-usb/10977/2 "2024-11-09T07:18:10Z")

</div>

Hi that is not possible, all in the manual of the et 112

Only 2 is possible at adress 1 and 2

If you need to connect more use another usb to rs485 cable and also adress them as 1 and 2

Also keep in mind to use a good quality powered usb hub

---

<div class="post-metadata">

**Author:** ![michaelm](https://avatars.discourse-cdn.com/v4/letter/m/3be4f8/32.png) [@michaelm](https://community.victronenergy.com/u/michaelm)\
**Post date:** [9 November 2024 07:35 UTC](https://community.victronenergy.com/t/multiple-et112-in-parallel-on-single-usb/10977/3 "2024-11-09T07:35:39Z")

</div>

Thanks for the prompt reply,  
Ok so 2 per adapter, sounds fine.  
Where is this documented? or is it just a trial-and-error thing?  
I reset their ID’s to 1 & 2, can confirm 2 showing now.

---

<div class="post-metadata">

**Author:** ![DuivertNL](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/duivertnl/32/279_2.png) [@DuivertNL](https://community.victronenergy.com/u/DuivertNL)\
**Post date:** [9 November 2024 07:46 UTC](https://community.victronenergy.com/t/multiple-et112-in-parallel-on-single-usb/10977/4 "2024-11-09T07:46:11Z")

</div>

The part with the adresses is not really documented, the CG energy meters are all on adress 1 by default

but its a question that is asked a lot, the 2 pieces is in the manual (the part you already posted)

---

<div class="post-metadata">

**Author:** ![Spazpeker](https://avatars.discourse-cdn.com/v4/letter/s/9de0a6/32.png) [@Spazpeker](https://community.victronenergy.com/u/Spazpeker)\
**Post date:** [9 November 2024 11:42 UTC](https://community.victronenergy.com/t/multiple-et112-in-parallel-on-single-usb/10977/5 "2024-11-09T11:42:17Z")

</div>

I have 2 meters and 2 usb leads one set to address 1 the other to address 2  
I have been trying to add a third meter with its own usb set to address 3,  
Just saw this post set the address back to 1 and at last have 3 working meters.  
Never saw anywhere about only mod bus 1&2 can be used,  
Glad I saw this post before posting my own question

---

<div class="post-metadata">

**Author:** ![DuivertNL](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/duivertnl/32/279_2.png) [@DuivertNL](https://community.victronenergy.com/u/DuivertNL)\
**Post date:** [9 November 2024 13:45 UTC](https://community.victronenergy.com/t/multiple-et112-in-parallel-on-single-usb/10977/6 "2024-11-09T13:45:48Z")

</div>

You can sort off find it in the modbus adress list, but im not shure its really documented anywhere

[https://www.victronenergy.com/upload/documents/CCGX-Modbus-TCP-register-list-3.50.xlsx](https://www.victronenergy.com/upload/documents/CCGX-Modbus-TCP-register-list-3.50.xlsx)