Multi RS went over my battery’s discharge limit—is this normal?
Hi all, hoping someone can help me understand an alarm I had this evening.
I have one Multi RS 6000 on firmware 1.31, with a Fogstar 16.1 kWh battery. It’s BMS controlled through CAN, and DVCC is on. Both the battery and Multi RS discharge limits are set to 100 A.
I put the washing machine on, possibly with the kettle running too, and got a high discharge current warning. The battery reached about 105.6 A, and its warning is set at 105 A.
The house was using about 5.3 kW, but the grid was only supplying around 240 W. It wasn’t doing any scheduled battery export at the time.
I thought it would take more from the grid once it reached the battery limit. Is a small overshoot like this normal, or is there something I should check?
I use Node-RED for charging and export times, but it was in normal self-consumption when this happened.
Thanks for any advice.
What DCL is the battery sending?
Is the bms visible and configured as the battery monitor?
The RS is capable of 9kW transients, that is 180A @ 50V. The AC loads exclude losses which will come from the battery.
  • The battery’s BMS is connected to my Victron system by CAN cable and shows as the controlling BMS (Fogstar 16.1kWh battery).
  • The battery is telling the system its discharge limit (DCL) is 100A. Charge limit is 110A and charge voltage 56.0V. Battery was 24°C and about 46% charged.
  • I have a Node-RED flow controlling ESS (the setting says External control).
  • At 19:17 tonight I got a high discharge current alarm. It lasted 1 min 38 secs
  1. I expected the grid to supply any extra power when the battery limit is reached. Is it normal to briefly go over the limit like this and give an alarm?
Thanks for your help.
Certainly for non-RS systems this is normal. On multis this is a common experience when the battery is sized beneath the inverter’s transient limits. If the inverter has to lean on the battery it appears to be undersized.
Ok thx for the info
And then sometimes our own controls mess with it as well.