Multi RS Solar higer AC consumption in OFF mode after firmware upgrades
Hi all,
After updating my Multi RS Solar 48/6000 from v1.24 to v1.31, its standby draw in Off mode roughly doubled, measured on the AC input.
Setup
  • Multi RS Solar 48/6000. The built-in MPPT has no PV connected.
  • Cerbo GX, Venus OS v3.80. ESS in external control (Hub4Mode 3).
  • The unit is switched to Off (Mode 4) from the GX during long idle periods at night.
  • An Eastron energy meter on the Multi’s AC input logs every few seconds.
Measurements (Off mode, AC input while Off)
v1.24: 2.9 W (2.4–3.2 W)
v1.31: 6.6 W (6.3–6.8 W)
The previous MultiPlus-II in the same position measured 0.3 W in Off but higher DC current. I read the changelogs for v1.25 to v1.32 and found nothing about standby consumption or a new power-saving setting.
Has anyone noticed this?
Thanks!
I don’t quite understand how a powered off device could be affected by firmware as its microcontroller is very much not running and the AC input relays would be wide open. This is not the same as standby, where the unit is powered.
I don’t know either but firmware can have an effort. Off isn’t exactly entirely off, it still listens. So it can be the sleep state of the CPU, the bluetooth radio now running where before it wasn’t, a relay that is now powered that wasn’t before. The sources aren’t public, unfortunately the binaries aren’t either, otherwise I’d have set codex to work on some reverse engineering to see what’s what :slight_smile:
I think you need to review the block diagram.
When the AC relays open (when you set the system to off) the system is disconnected from mains, it cannot draw AC power as the components are on the other side of the open relays.
It could theoretically draw DC power, but even in this case, when physically off at the switch, only the capacitor bank and internal PV chargers are connected, so no, firmware cannot affect what you are doing, unless they added wireless charging recently :wink: