Yesterday evening, I noticed the following behavior in my system:
L1 was importing around 2100W, while L2 was exporting a similar amount of power back to the grid.
I have no idea why the system felt the need to compensate for the phases in this way. It doesn’t seem efficient at all when you consider the charge and discharge efficiency losses. Has anyone seen this before or knows what might be happening here?
System details:
• Situation: The battery bank was balancing at the time, so “Keep batteries charged” was active (due to a new EVE MB56 battery being added to the bank).
• Battery capacity: 64.4 kWh
• Inverters: 3x Multi RS Solar (running firmware V1.31)
• GX Device: Cerbo GX running DESS with “Keep batteries charged” active (firmware V3.80)
Are you referring to the phase rotation? I’ve already checked those connections.
There are no other loads or power sources connected between the energy meter and the Multi RS. When I compare the voltage and current readings from the energy meter with those at the AC input of the Multi RS, everything seems to indicate that the phases are connected correctly.
Last weekend, I observed this same behavior in another installation, and I think I have found the root cause. However, I am not sure how the Multi RS is officially supposed to handle this in a 3-phase configuration. For now, I suspect it might be a system bug, as I have never encountered this behavior with MultiPlus-II (MP-II) variants.
In this system, the BMS (a JK-BMS in this case) is selected as the battery monitor for both current and voltage sensing. Due to small voltage drops (caused by minor differences in cable lengths and busbar resistance), the three Multi RS units start compensating continuously to keep the voltage at the BMS correct. This creates a loop where L1 is importing power while another phase is exporting power simultaneously.
As soon as I change the battery monitor source from the BMS to one of the Multi RS units or the system itself, this behavior disappears immediately. I am not sure if this same issue would occur when using a SmartShunt as the battery monitor source.