# Multi RS Smart 48V/6000VA/100A entlädt die Batterie nicht

**URL:** <https://community.victronenergy.com/t/multi-rs-smart-48v-6000va-100a-entladt-die-batterie-nicht/29795>\
**Category:** Deutschsprachiger Bereich\
**Created:** [23 April 2025 06:46 UTC](https://community.victronenergy.com/t/multi-rs-smart-48v-6000va-100a-entladt-die-batterie-nicht/29795 "2025-04-23T06:46:41Z")\
**Posts on this page:** 16\
**Page:** 1

<div class="post-metadata">

**Author:** ![Larsoist](https://avatars.discourse-cdn.com/v4/letter/l/3be4f8/32.png) [@Larsoist](https://community.victronenergy.com/u/Larsoist)\
**Post date:** [23 April 2025 06:46 UTC](https://community.victronenergy.com/t/multi-rs-smart-48v-6000va-100a-entladt-die-batterie-nicht/29795/1 "2025-04-23T06:46:41Z")

</div>

Schönen Guten Morgen zusammen,

**Ich habe einen Multi RS Smart 48V/6000VA/100A in Kombination mit zwei Voltsmile Classic-Speichern à 5,12 kWh installiert.**  
Vor dem Update, mit dem ESS-Funktionalität und die Netzeinspeisung für den Multi RS freigeschaltet wurden, hat das System die Batterie regulär entladen.  
Seit dem Update jedoch wird **am Abend nur noch der Back-Up-Ausgang** aus der Batterie versorgt – **alle anderen Verbraucher werden nicht mehr über AC-In** bedient.

Mit freundlichen Grüßen

Lars Tepper-Simon

---

<div class="post-metadata">

**Author:** ![d\_ferdi](https://avatars.discourse-cdn.com/v4/letter/d/48db29/32.png) [@d\_ferdi](https://community.victronenergy.com/u/d_ferdi)\
**Post date:** [23 April 2025 08:16 UTC](https://community.victronenergy.com/t/multi-rs-smart-48v-6000va-100a-entladt-die-batterie-nicht/29795/2 "2025-04-23T08:16:14Z")

</div>

hallo,  
update bei einem multi bedeutet normalerweise immer neu konfigurieren oder gespeicherte info wiederherstellen. ich kann mir gut vorstellen, dass das beim rs genaus ist und dir dabei deine konfig verloren gegegangen ist und das teil nicht mehr als ess arbeitet.

tschuess

---

<div class="post-metadata">

**Author:** ![Larsoist](https://avatars.discourse-cdn.com/v4/letter/l/3be4f8/32.png) [@Larsoist](https://community.victronenergy.com/u/Larsoist)\
**Post date:** [23 April 2025 08:48 UTC](https://community.victronenergy.com/t/multi-rs-smart-48v-6000va-100a-entladt-die-batterie-nicht/29795/3 "2025-04-23T08:48:37Z")

</div>

Guten Morgen Dieter,

die Einstellung wurde nach dem Update neu ins Gerät geladen.  
Der Grid Code von Deutschland wurde geladen. Und unter den Netzeinstellungen wurde die Einspeisung erlaubt.  
Die Batterie Einstellungen habe ich mal als Bild angehangen.

 ![Batterieeinstellungen](https://europe1.discourse-cdn.com/victron/original/3X/5/2/5291cbfb2e321b637348a58a3c433ec1f2a80f46.png)

Grüße Lars

---

<div class="post-metadata">

**Author:** ![Larsoist](https://avatars.discourse-cdn.com/v4/letter/l/3be4f8/32.png) [@Larsoist](https://community.victronenergy.com/u/Larsoist)\
**Post date:** [23 April 2025 08:51 UTC](https://community.victronenergy.com/t/multi-rs-smart-48v-6000va-100a-entladt-die-batterie-nicht/29795/4 "2025-04-23T08:51:31Z")

</div>

Und hier sieht man die Problemstellung

 ![Voltsmile Batterie](https://europe1.discourse-cdn.com/victron/original/3X/6/c/6c4af051cfd3fe69da71b303edc61606e2af2704.png)

---

<div class="post-metadata">

**Author:** ![d\_ferdi](https://avatars.discourse-cdn.com/v4/letter/d/48db29/32.png) [@d\_ferdi](https://community.victronenergy.com/u/d_ferdi)\
**Post date:** [23 April 2025 08:57 UTC](https://community.victronenergy.com/t/multi-rs-smart-48v-6000va-100a-entladt-die-batterie-nicht/29795/5 "2025-04-23T08:57:38Z")

</div>

hallo,  
kennt der rs den netzzaehler? und welcher netzzaehler ist verbaut?

tschuess

---

<div class="post-metadata">

**Author:** ![Larsoist](https://avatars.discourse-cdn.com/v4/letter/l/3be4f8/32.png) [@Larsoist](https://community.victronenergy.com/u/Larsoist)\
**Post date:** [23 April 2025 09:11 UTC](https://community.victronenergy.com/t/multi-rs-smart-48v-6000va-100a-entladt-die-batterie-nicht/29795/6 "2025-04-23T09:11:33Z")

</div>

Es ist das Energy Meter VM-3P75CT verbaut und wird auch vom System erkannt.  
Die klassische Einspeisung wenn der Solarregler überschüssige Energie hat funktioniert.

 ![Screenshot 2025-04-23 111116](https://europe1.discourse-cdn.com/victron/original/3X/d/8/d892fc68ba7483a33887ba579dd480a2299551be.png)

---

<div class="post-metadata">

**Author:** ![M\_Lange](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/m_lange/32/16_2.png) [@M\_Lange](https://community.victronenergy.com/u/M_Lange)\
**Post date:** [23 April 2025 09:24 UTC](https://community.victronenergy.com/t/multi-rs-smart-48v-6000va-100a-entladt-die-batterie-nicht/29795/8 "2025-04-23T09:24:05Z")

</div>

Deaktiviert heißt “volle Pulle” - alles was geht/der Akku zulässt.

---

<div class="post-metadata">

**Author:** ![Larsoist](https://avatars.discourse-cdn.com/v4/letter/l/3be4f8/32.png) [@Larsoist](https://community.victronenergy.com/u/Larsoist)\
**Post date:** [23 April 2025 09:24 UTC](https://community.victronenergy.com/t/multi-rs-smart-48v-6000va-100a-entladt-die-batterie-nicht/29795/9 "2025-04-23T09:24:37Z")

</div>

Ja laut VRM Portal ist in den Batterien, dann ein Entladestrom von 190A möglich.

---

<div class="post-metadata">

**Author:** ![d\_ferdi](https://avatars.discourse-cdn.com/v4/letter/d/48db29/32.png) [@d\_ferdi](https://community.victronenergy.com/u/d_ferdi)\
**Post date:** [23 April 2025 09:38 UTC](https://community.victronenergy.com/t/multi-rs-smart-48v-6000va-100a-entladt-die-batterie-nicht/29795/11 "2025-04-23T09:38:02Z")

</div>

hallo,  
hast du den zaehler per can-bus angeschlossen oder uebers netzwerk?

tschuess

---

<div class="post-metadata">

**Author:** ![Larsoist](https://avatars.discourse-cdn.com/v4/letter/l/3be4f8/32.png) [@Larsoist](https://community.victronenergy.com/u/Larsoist)\
**Post date:** [23 April 2025 09:49 UTC](https://community.victronenergy.com/t/multi-rs-smart-48v-6000va-100a-entladt-die-batterie-nicht/29795/13 "2025-04-23T09:49:33Z")

</div>

Per Can-Bus

---

<div class="post-metadata">

**Author:** ![Larsoist](https://avatars.discourse-cdn.com/v4/letter/l/3be4f8/32.png) [@Larsoist](https://community.victronenergy.com/u/Larsoist)\
**Post date:** [23 April 2025 09:52 UTC](https://community.victronenergy.com/t/multi-rs-smart-48v-6000va-100a-entladt-die-batterie-nicht/29795/14 "2025-04-23T09:52:38Z")

</div>

Ich habe für den Versuch 100A eingegeben. Könnte mir einer Erklären, was die Fernsteuerung über ein 2 Draht BMS bei Victron Connect bedeutet? Oder sollte ich es lieber auf der Einstellung: Fernbedienung Ein/Aus lassen ?

 ![Screenshot 2025-04-23 115139](https://europe1.discourse-cdn.com/victron/original/3X/8/8/88acaf4f6289b6bd0115f0a6cf6d2998adcad1ed.png)

---

<div class="post-metadata">

**Author:** ![M\_Lange](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/m_lange/32/16_2.png) [@M\_Lange](https://community.victronenergy.com/u/M_Lange)\
**Post date:** [23 April 2025 10:00 UTC](https://community.victronenergy.com/t/multi-rs-smart-48v-6000va-100a-entladt-die-batterie-nicht/29795/15 "2025-04-23T10:00:31Z")

</div>

> [@Larsoist](#):
>
> Könnte mir einer Erklären, was die Fernsteuerung über ein 2 Draht BMS bei Victron Connect bedeutet? Oder sollte ich es lieber auf der Einstellung: Fernbedienung Ein/Aus lassen ?

Ich denke wenn du diese Frage stellst, brauchst du es nicht und solltest es auf der Standardeinstellung belassen.  
Der Akku/das BMS kommuniziert doch mit dem GX Gerät, oder?

> **[5. Einrichtung, Konfiguration und Bedienung von VictronConnect](https://www.victronenergy.com/media/pg/Multi_RS_Solar/de/victronconnect-setup,-configuration-and-operation.html#UUID-7b234edb-cba5-70df-8791-ea7609acb2ed)**

---

<div class="post-metadata">

**Author:** ![Larsoist](https://avatars.discourse-cdn.com/v4/letter/l/3be4f8/32.png) [@Larsoist](https://community.victronenergy.com/u/Larsoist)\
**Post date:** [23 April 2025 10:02 UTC](https://community.victronenergy.com/t/multi-rs-smart-48v-6000va-100a-entladt-die-batterie-nicht/29795/16 "2025-04-23T10:02:13Z")

</div>

Ja das BMS kommuniziert mit dem Cerbo. Danke für die Hilfestellung.

---

<div class="post-metadata">

**Author:** ![Larsoist](https://avatars.discourse-cdn.com/v4/letter/l/3be4f8/32.png) [@Larsoist](https://community.victronenergy.com/u/Larsoist)\
**Post date:** [23 April 2025 10:41 UTC](https://community.victronenergy.com/t/multi-rs-smart-48v-6000va-100a-entladt-die-batterie-nicht/29795/17 "2025-04-23T10:41:15Z")

</div>

Anscheinend war die Einstellung

 ![Screenshot 2025-04-23 122833](https://europe1.discourse-cdn.com/victron/original/3X/e/d/ed758008af70233b0bdc0bb0c8d8368bb5098362.png)  
“Unterstützung von Energiezählern” der Ausschlaggebende Punkt warum es nicht funktionierte.  
Nach dem ich diese Einstellung aktiviert hatte lief die Anlage sofort.

---

<div class="post-metadata">

**Author:** ![Larsoist](https://avatars.discourse-cdn.com/v4/letter/l/3be4f8/32.png) [@Larsoist](https://community.victronenergy.com/u/Larsoist)\
**Post date:** [23 April 2025 10:42 UTC](https://community.victronenergy.com/t/multi-rs-smart-48v-6000va-100a-entladt-die-batterie-nicht/29795/18 "2025-04-23T10:42:33Z")

</div>

Danke für die aktive Beteiligung an meinem Problem und das gemeinsame Brainstormen

---

<div class="post-metadata">

**Author:** ![system](https://europe1.discourse-cdn.com/victron/original/1X/21a9a7b5db7c6339715f993568736a7053199995.png) [@system](https://community.victronenergy.com/u/system)\
**Post date:** [7 May 2025 10:43 UTC](https://community.victronenergy.com/t/multi-rs-smart-48v-6000va-100a-entladt-die-batterie-nicht/29795/19 "2025-05-07T10:43:07Z")

</div>

Closed on 7 May 2025 10:43 UTC

This topic was automatically closed 14 days after the last reply. New replies are no longer allowed.