Multi RS not charging batteries from AC IN

I’ve a Multi RS that is grid connected. It is working with a brand new Cerbo; the firmware on the Multi RS Solar is up to date. When theres an AC grid connection present, it can see the AC, but it doesn’t charge the battery, even when ‘keep batteries charged’ is selected. If an AC load is present then the AC input ramps up to match the AC load, less about 150W.
I’ve tried resetting the RS multi to defaults, and no change. The battery is a Dyness Powerbox G2, correct CAN Cable, is communicating properly.
Am I missing something, this has to be a settings issue. I’ve seen similar before with a generator and the ESS settings cured it but not this time.
Its an older Multi RS Solar.

Is the battery voltage at full voltage (ignore soc for now and check that)

Check on the VRM (or the gx under the device) it could be the battery saying no charge. (CCL and CVL)

Check the manual

Switch off Dvcc (temporarily) and see if is the battery causing the no charge condition

So the battery voltage of 51.92 seems consistent with its SOC (27%), so I’ll check the CCL and CVL. It’s a Dyness Powerbox G3 and I’ve used them with Multiplus II installs with no issues so I can’t imagine its the battery but will investigate it in case.

Solved. It was a DVCC setting from an older pylontech battery to cap the maximum voltage that was overlooked. The Dyness has much higher charge parameters and so of course it couldn’t charge. An easy fix in the end, don’t know how it was missed.