Multi RS 48/6000/1000 - The effect of 12A limit on MPPT tracker

Hi Victron Community,

I need to know some information regarding the MPPT limitation for high current PV module, I am working on a project where I have the inverter from Victron which is Multi RS 48/6000/100 and it has dual MPPT trackers. Each tracker is compatible to connect 1 PV string each.

So, I have designed my PV string with the panel from Jinko which has a model name: JKM620N-66HL4M-BDV, The STC of the panel are as follows:

P(max): 620W

V(mp): 40.74V

I(mp): 15.22A

I have connected 5 panels series to make a single string, so the string STC will be as follows:

P(max): 3100W

V(mp): 203.7V

I(mp): 15.22A

However the MPPT adjust the PV operating point based on the I-V curve of the panel, still I have some concerns, as follows

  • When the available PV current exceeds 12 A, does the Multi RS Solar limit the current by moving the array away from its maximum-power point to a different voltage and current operating point?
  • Or, will it keep the voltage at V(mp) of the string and results in a reduction in power?

My objective is to quantify any potential energy loss caused by the MPPT current limitation and confirm the compatibility of this module with the Multi RS Solar before finalising the design.

I would appreciate clarification from Victron technical support or community members who have experience with this inverter and similar high-current PV modules.

Yes at STC test conditions of 1000W/m2 irradiance and 25C cell temp you will “lose” power otherwise available over 12A.

However, generally you may find your panels are delivering NOCT values in day to day actual operation that are close to that 12A figure (488W)

Hi Brucey

This is a scenario where the panels are delivering NOCT values in a day, but let’s consider a condition where the panels are operating in STC conditions; in that case, if the tracker limits the current at 12A and the Vmp at 203.7V, I am going to get a maximum power of 2444.4W, but if the tracker can move the Vmp value more than 203.7V, it can attain more power. May I know whether the MPPT can do this?

The tracker can never exceed the string Voc/Vmp. It can only pull voltage down from there. So yes there will be losses during cloud edge effect etc, from an ideal situation where it could momentarily peak for a few seconds at stc or even beyond.

So one option is to add a sixth panel to each tracker, to better utilise the trackers 3kW limit versus what you get with NOCT with 5s. Basically a very light overpanelling.

Interesting question. I’m also not entirely sure what exactly the MPPT tracker does when the current is limited to 12 amps. I find it unlikely that the MPPT tracker wouldn’t move towards the highest possible voltage. With a 12 A limit, the operating point automatically shifts to the far right of the curve.

In my previous message, I was confused because the power curve is plotted on the same graph.

That doesn’t help as far as being able to use the panels maximum output is concerned, in fact it makes things worse…

Under STC conditions (16A maximum panel output current) the MPPT will move the panel/string voltage up to around 45V (above the peak power tracking point of 40.7V/15.2A) to lower the current to 12A, at which point power will be around 540W/panel instead of 620W, which is 13% lower. So for 5 panels in series you’ll get 225V/12A which is 2.7kW, 400W lower than the 3.1kW rating.

Adding a sixth panel would increase the voltage (under STC conditions) to 270V@12A which is 3240W, above the MPPT 3kW maximum power rating – so it will increase the voltage even further to push the current down to about 11A, now you’ll only get 3000W out of 6x620=3720W of panels which is 20% lower than rated. Adding the sixth panel under these conditions has only given 300W extra output.

This obviously won’t reduce overall solar yield by this much because the limits will only be hit when the panel output exceeds 87% or 80% of rated output (870W/m2 or 800W/m2 irradiance). But from my observations in summer I do often see the rated output (or even a little bit higher) on sunny days, certainly in the middle of the day.

Yes, fundamentally you have to decide whether to design for stc output, so that you never “lose” any momentary cloud edge effect power. If thats what you need then a 12A limit and 620W nameplate panels arent a good fit.

But then for vast majority of solar day and solar year, you’ll be sitting at around 80% of stc (for any panel or scc). On average you will get much more output/utilization of the 3k per tracker with 6s.

Otherwise:

Are the two strings in different directions? Maybe two 250/60s running 3s2p on each? And get the rs inverter without integrated solar?

Agreed, for overall solar yield 6S will be better than 5S.

Of course 6S (or 5S) with a 16A MPPT instead of the Multi RS Solar would be better still, then you never throw any potential power away… :wink:

The fundamental problem is that the Multi RS Solar was designed maybe 6-7 years ago (introduced in 2021?) when 400W/12A panels were the norm (for the now-standard 54-cell 1762mm x 1134mm size). Since then efficiency and output has gone up, and the best panels are now around 500W/15A which is too much for the Multi RS Solar to cope with in STC conditions.

(higher output panels like 60-cell or bigger are the same current but higher voltage, however these are much less common)

Yes you can oversize panels to get more output when the sun isn’t so bright – which is the case a lot of the time – but the fact remains that you’re not using the panels to their full capability on sunny summer days. Even more so if you oversize them… :wink: