# MPPT will not turn on

**URL:** <https://community.victronenergy.com/t/mppt-will-not-turn-on/60913>\
**Category:** DIY\
**Tags:** smartshunt, cerbo\_gx, multiplus-ii, mppt\_controllers, cerbo-gx\
**Created:** [26 July 2026 00:18 UTC](https://community.victronenergy.com/t/mppt-will-not-turn-on/60913 "2026-07-26T00:18:13Z")\
**Posts on this page:** 20\
**Page:** 3

<div class="post-metadata">

**Author:** ![Fadi](https://avatars.discourse-cdn.com/v4/letter/f/ecae2f/32.png) [@Fadi](https://community.victronenergy.com/u/Fadi)\
**Post date:** [29 July 2026 14:15 UTC](https://community.victronenergy.com/t/mppt-will-not-turn-on/60913/41 "2026-07-29T14:15:52Z")

</div>

Hi Richard,

I have a question regarding your solar panel configuration.

According to your specifications, you are using four 200 W solar panels, and each panel has an open-circuit voltage (Voc) of 24.3 V. If all four panels are connected in series, the maximum open-circuit voltage should be:

24.3 V × 4 = **97.2 V**

Could you please clarify how you are obtaining **122 V** at the output of the solar panel array? I would appreciate it if you could explain the configuration or provide any additional information that accounts for this higher voltage.

---

<div class="post-metadata">

**Author:** ![Rtmumper](https://avatars.discourse-cdn.com/v4/letter/r/3e96dc/32.png) [@Rtmumper](https://community.victronenergy.com/u/Rtmumper)\
**Post date:** [29 July 2026 22:39 UTC](https://community.victronenergy.com/t/mppt-will-not-turn-on/60913/42 "2026-07-29T22:39:33Z")

</div>

Here are the full specs for the **[Renogy 200W 25% High-Efficiency N-Type Solar Panel](https://www.amazon.com/dp/B08CRJYJ22)**:

Maximum Power | 200W | | Module Efficiency | 25% (N-Type 16BB cells) | | Open-Circuit Voltage (Voc) | 37.44V | | Optimum Operating Voltage | 31.03V | | Optimum Operating Current | 6.45A | | Short-Circuit Current (Isc) | 6.85A | | Max Series Fuse Rating | 15A | | Max System Voltage | 600V DC | | Output Voltage | 24V DC |

---

<div class="post-metadata">

**Author:** ![DaveD](https://avatars.discourse-cdn.com/v4/letter/d/bcef8e/32.png) [@DaveD](https://community.victronenergy.com/u/DaveD)\
**Post date:** [30 July 2026 02:05 UTC](https://community.victronenergy.com/t/mppt-will-not-turn-on/60913/43 "2026-07-30T02:05:06Z")

</div>

Hi Richard,

I might have missed it in the comments, but did you try bypassing the breaker on the battery side of the MPPT? Those breakers are notoriously poor in quality.

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [30 July 2026 05:07 UTC](https://community.victronenergy.com/t/mppt-will-not-turn-on/60913/44 "2026-07-30T05:07:43Z")

</div>

> [@Rtmumper](#):
>
> eliminated the PV 15A breaker as a cause. I have continuity when closed and when open I have no continuity. I have also bypassed the breaker with the same results.

Yeah, he said he had.

> [@lxonline](#):
>
> next stage a PRE RMA test.

So the next step is this.

---

<div class="post-metadata">

**Author:** ![DaveD](https://avatars.discourse-cdn.com/v4/letter/d/bcef8e/32.png) [@DaveD](https://community.victronenergy.com/u/DaveD)\
**Post date:** [30 July 2026 05:36 UTC](https://community.victronenergy.com/t/mppt-will-not-turn-on/60913/45 "2026-07-30T05:36:58Z")

</div>

I’m asking about the breaker on the battery side of the charge controller which I believe his drawing indicates is a 70 amp. He says he bench tested the 250/60 and it worked as it should, which again indicates a problem with the installation.

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [30 July 2026 05:52 UTC](https://community.victronenergy.com/t/mppt-will-not-turn-on/60913/46 "2026-07-30T05:52:25Z")

</div>

Yeha those breaker types… Interesting idea you have there.

> [@Rtmumper](#):
>
> The voltage drops from 122V to 12.3V (same battery voltage)

He said he has battery voltage at the terminals but that doesn’t always mean it can move amps.  
The part that has been of great focus has been the disappearing panel voltage.

---

<div class="post-metadata">

**Author:** ![RoarPowerNZ](https://avatars.discourse-cdn.com/v4/letter/r/8c91f0/32.png) [@RoarPowerNZ](https://community.victronenergy.com/u/RoarPowerNZ)\
**Post date:** [30 July 2026 21:29 UTC](https://community.victronenergy.com/t/mppt-will-not-turn-on/60913/47 "2026-07-30T21:29:41Z")

</div>

Exactly @lxonline

I haven’t seen any suggestion so far that the panel array has been commissioned or recommissioned; Checking Voc is not the same. Kudos to those suggesting focusing on getting a clamp or similar to check current.

I would strongly suspect that there is a fault in the array, and that measuring the array Voc is misleading you. An array can easily have an active fault (poor connection, faulty breaker, faulty panel) and still produce an apparently correct Voc. This Voc will collapse to either zero or battery voltage as soon as power is (tried to be) drawn. This seems to be exactly what OP is seeing.

My advice would be for the OP to follow this method, recommission the array. My bet is that either this finds the fault, or it rules out the array and you can move on with confidence to downstream parts of the system.

> [@A call to all panel experts and installers - checklist for checking arrays](https://community.victronenergy.com/t/a-call-to-all-panel-experts-and-installers-checklist-for-checking-arrays/20774):
>
> It seems to me that it would be easier to help users with problems if we had a standardised list of array checks we could point users to. For computer issues (my previous occupation a lifetime ago) there are a number of forums where they point users to a standardised bunch of commands they can run which collect all the data that answers almost all the forum expert’s questions. The forum experts won’t touch a user’s issue unless they have attempted to collect that info, and it really cuts down on…

---

<div class="post-metadata">

**Author:** ![Justin](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/justin/32/24_2.png) [@Justin](https://community.victronenergy.com/u/Justin)\
**Post date:** [30 July 2026 23:17 UTC](https://community.victronenergy.com/t/mppt-will-not-turn-on/60913/48 "2026-07-30T23:17:10Z")

</div>

> [@lxonline](#):
>
> Yeha those breaker types…

The breaker _type_ is one thing, the breaker brand is another. T-Tocas is an Amazon-special Chinese knockoff of the Bussmann Series 285 breaker, and while the Bussmann 285 and 187 breakers are pretty solid (can’t be used on the PV side of course, but good on bat side), T-Tocas and other counterfeits like Red Wolf and so forth are definitely known to be trash - going on 5 years or more, you can find reports of those brands causing severe system issues on this forum, the old forum, and just about every other forum and FB group and etc that has anything to do with electrical systems.

---

<div class="post-metadata">

**Author:** ![Rtmumper](https://avatars.discourse-cdn.com/v4/letter/r/3e96dc/32.png) [@Rtmumper](https://community.victronenergy.com/u/Rtmumper)\
**Post date:** [1 August 2026 00:07 UTC](https://community.victronenergy.com/t/mppt-will-not-turn-on/60913/49 "2026-08-01T00:07:03Z")

</div>

I am fairly certain that the problem all along was the manner in which the battery cables were installed (the 250/60 MPPT tested and found to function perfectly). The first battery on the left at the cabin was connected to the system with a 4/0 cable while the other two batteries were connected with much smaller cables in parallel off the leftmost battery. The negative cable from the leftmost battery to the smartshunt with a 2/0 cable and the leftmost was also connected similar to the positive side. All of the charge went into the first battery and damaged it to the point that the MPPT is sensing something and not turning ON and charging.

I am switching out the batteries for one Deca 300Ah lithium battery with a built in BMS and redoing all of the cables with the same size 4/0 cables with the same lengths off the main bus and will use some means such as single or dual lug buses to make the 90 degree turns instead of cable bends. The surge capability of the Victron switch is well over 400A so I will keep it and will also keep the 400A fuses due to the battery chosen. The 4/0 cables will all be as straight as possible and the run to the two buses will be virtually identical if I have my way. Any ideas for facilitate running the cables without bending would be appreciated. I know it is a simple 12V system but it is all I have room for. Any comments on the following revised rough sketch of a re-cabling, upgrade of fuses to MidNite brand, and a new Deca 300Ah, 300A lithium-Ion battery with built in BMS rated for -5F.:

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/1/6/16670baead1e428655725a1ebb89523bccbd0759.jpeg)

---

<div class="post-metadata">

**Author:** ![Rtmumper](https://avatars.discourse-cdn.com/v4/letter/r/3e96dc/32.png) [@Rtmumper](https://community.victronenergy.com/u/Rtmumper)\
**Post date:** [1 August 2026 00:19 UTC](https://community.victronenergy.com/t/mppt-will-not-turn-on/60913/50 "2026-08-01T00:19:42Z")

</div>

See below. The problem is not with the PV arrays. Both have been very dependable and the test one is still working. All the breakers were tested and bypassed with the same results. I will be taking the new battery and cables with me, voltage generator and I will hopefully determine what caused the MPPT’s not to turn on. I am fairly certain it is a damaged battery that caused the problem, but we will see. I am also going to upgrade all the breakers in the system. I was thinking of going with MidNite breakers.

Ideas are appreciated.

---

<div class="post-metadata">

**Author:** ![Rtmumper](https://avatars.discourse-cdn.com/v4/letter/r/3e96dc/32.png) [@Rtmumper](https://community.victronenergy.com/u/Rtmumper)\
**Post date:** [1 August 2026 20:01 UTC](https://community.victronenergy.com/t/mppt-will-not-turn-on/60913/51 "2026-08-01T20:01:10Z")

</div>

The Victron Energy Battery Switch 275A surge/cranking rating is **1,250A (10 second peak)**.

Here are the full current specifications:

**Continuous rating:** 275A (sustained draw)

**One-minute rating:** 455A

**Cranking rating:** 1,250A (10 second surge)

---

<div class="post-metadata">

**Author:** ![Rtmumper](https://avatars.discourse-cdn.com/v4/letter/r/3e96dc/32.png) [@Rtmumper](https://community.victronenergy.com/u/Rtmumper)\
**Post date:** [2 August 2026 00:38 UTC](https://community.victronenergy.com/t/mppt-will-not-turn-on/60913/52 "2026-08-02T00:38:14Z")

</div>

I am switching to MidNite breakers. But, yes, I did bypass the Tocas breakers to make sure none of them were the problem.

Also, does anyone know whether the new SmartSolar MPPT’s (mine is a new 250/60-Tr) has a relay or something else to protect against PV voltage shorting to battery voltage?

---

<div class="post-metadata">

**Author:** ![Rtmumper](https://avatars.discourse-cdn.com/v4/letter/r/3e96dc/32.png) [@Rtmumper](https://community.victronenergy.com/u/Rtmumper)\
**Post date:** [2 August 2026 01:17 UTC](https://community.victronenergy.com/t/mppt-will-not-turn-on/60913/53 "2026-08-02T01:17:10Z")

</div>

I am switching to MidNite breakers and getting rid of the cheap Tocas breakers.

---

<div class="post-metadata">

**Author:** ![ira251166](https://avatars.discourse-cdn.com/v4/letter/i/4bbf92/32.png) [@ira251166](https://community.victronenergy.com/u/ira251166)\
**Post date:** [2 August 2026 05:49 UTC](https://community.victronenergy.com/t/mppt-will-not-turn-on/60913/54 "2026-08-02T05:49:30Z")

</div>

I had a quick look at the schematic. The graphic is NOT very clear. BUT you should only have ONE panel pos connected to the MPPT(+).

If I have read your schematic correctly, then you currently have a string of THREE panels in parallel with ONE panel.

Panels 1 Positive goes to MPPT. Panel 1 Neg goes to Panel 2 Pos. Panel 2 Neg goes to panel 4 Pos. Panel 4 neg goes to MPPT.

Panel 3 Pos goes to MPPT. Panel 3 neg goes to MPPT.

In this configuration the three panels would be shorted by the single panel and all the current from the three panels, (Isc), will be flowing through panel 3. This MAY have caused it some harm, depending on it’s internal current rating.

If you were trying for 4 in series, then it’s…

Pos panel one to the MPPT(+).

Neg panel 1 to Pos panel 2.  
Neg 2 to Pos 3.

Neg 3 to Pos 4.  
And Neg 4 to the MPPT(-)

---

<div class="post-metadata">

**Author:** ![ira251166](https://avatars.discourse-cdn.com/v4/letter/i/4bbf92/32.png) [@ira251166](https://community.victronenergy.com/u/ira251166)\
**Post date:** [2 August 2026 05:58 UTC](https://community.victronenergy.com/t/mppt-will-not-turn-on/60913/55 "2026-08-02T05:58:59Z")

</div>

4 x 37.44 is real close to the 150V limit of the MPPT. On a cold day, once the batteries are fully charged OR if the MPPT is forced off due to a generator charging the batteries via the Inverter, then this voltage limit could be exceeded.

I’m sure that they won’t be fried at 0.1V above the stated limit but you are probably too close to the voltage limit with the 150 MPPT, (good call to go up to the higher rated unit).

---

<div class="post-metadata">

**Author:** ![Rtmumper](https://avatars.discourse-cdn.com/v4/letter/r/3e96dc/32.png) [@Rtmumper](https://community.victronenergy.com/u/Rtmumper)\
**Post date:** [2 August 2026 15:33 UTC](https://community.victronenergy.com/t/mppt-will-not-turn-on/60913/56 "2026-08-02T15:33:43Z")

</div>

![image](https://europe1.discourse-cdn.com/victron/original/3X/e/6/e6aa43042d5f737cc4bd4fbcec31409db1844d45.png)

The above is how the cables are run. The Voc in incorrect on the drawing though (see the specs above). Only one positive and one negative MC4 cable is connected to the MPPT PV terminals. Only one cable per +/- emanates from the battery side of the MPPT to the buses. The handwritten sketch I shared above I drew two lines to simulate the 4/0 and 2/0 cables, mainly because I want in the re-cable to eliminate the bends and differences between the +/- sides when we re-cable everything properly. My electrical engineer son built the cables and installed them for several years for a photon therapy company. Unfortunately, he was not available before but has agreed to do this job. His cabling in his previous job had to be perfect in every sense or they could suffer millions of dollars in damage. He said their rules were: same brand, same cable characteristics, same length, same connections, no bends. I was attempting to come up with a design to discuss with him today actually. I am looking forward to his take on how he will want to do it. I have not purchased all the components and cable yet. Update: My son likes the new cable install design.

---

<div class="post-metadata">

**Author:** ![Rtmumper](https://avatars.discourse-cdn.com/v4/letter/r/3e96dc/32.png) [@Rtmumper](https://community.victronenergy.com/u/Rtmumper)\
**Post date:** [2 August 2026 15:35 UTC](https://community.victronenergy.com/t/mppt-will-not-turn-on/60913/57 "2026-08-02T15:35:08Z")

</div>

The same thing happened with a 250/60-Tr MPPT, which I am now going to reinstall after replacing the 150/60-Tr.

---

<div class="post-metadata">

**Author:** ![ira251166](https://avatars.discourse-cdn.com/v4/letter/i/4bbf92/32.png) [@ira251166](https://community.victronenergy.com/u/ira251166)\
**Post date:** [3 August 2026 04:01 UTC](https://community.victronenergy.com/t/mppt-will-not-turn-on/60913/58 "2026-08-03T04:01:02Z")

</div>

Well that cabling schematic looks better than the earlier version. The same current will be flowing in all cables, if the lengths aren’t too long, you could probably use 4mm2 solar cabling for all these runs. The current is around 10 Amps, voltage drop should not be a problem.

This might be a strange question but have you set the battery voltage of the MPPT unit? The manual tells you how to do this, and to reset it if you have a different voltage by default or from the supplier, etc.

And have you set the MPPT charge properties? ie set for your battery type, your charge profile and durations etc. I’m not sure that leaving this blank will cause problems, it will probably just adopt the settings from the hardware switch if not set in software.

With regard to cable bends, the current will not know if the cable is bent or straight, just as long as you don’t wind a large inductor or wrap the cable around a steel/ferrite rod etc. The current is generally DC, (with only a little switching hash from the MPPT unit superimposed), so the cable shape generally won’t matter. With regard to cable lengths, they are NOT required to be the same length, short is good, just make sure that you leave a suitable amount for terminations and in case you need to remake a termination at a later date, better to be looking at the cable than looking for the cable.

---

<div class="post-metadata">

**Author:** ![Rtmumper](https://avatars.discourse-cdn.com/v4/letter/r/3e96dc/32.png) [@Rtmumper](https://community.victronenergy.com/u/Rtmumper)\
**Post date:** [3 August 2026 19:45 UTC](https://community.victronenergy.com/t/mppt-will-not-turn-on/60913/59 "2026-08-03T19:45:13Z")

</div>

I did. And, reset everything again. I currently have set everything up using the MK3-USB but will have to change the battery settings from gel batteries to the new LIFePO4 battery. I think the biggest problem with the current installation was most of the charge was going into the first battery due to the cabling size mismatch 4/0 +, 2/0 - for leftmost battery, smaller gauge yet going in parallel to the other two batteries. All of the issues noted in the above posts will be addressed later this month when I and my son return to determine the root problem that caused the MPPT’s not to turn to Bulk before, redo the cabling, reinstall the new 250/60-Tr MPPT, and the new 300Ah Deca LiFePO4 heated battery (see below) which communicates via cable directly with my Cerbo GX (which eliminates the need for a new 500A SmartShunt. Any thoughts on this battery?

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/d/0/d0dc7f695ab64d029de990d50af50457b4f7526d.png)

---

<div class="post-metadata">

**Author:** ![Rtmumper](https://avatars.discourse-cdn.com/v4/letter/r/3e96dc/32.png) [@Rtmumper](https://community.victronenergy.com/u/Rtmumper)\
**Post date:** [23 September 2026 18:09 UTC](https://community.victronenergy.com/t/mppt-will-not-turn-on/60913/60 "2026-09-23T18:09:08Z")

</div>

We found the problem during our last trip to our remote cabin. We recabled the system, resulting in a very clean system (see photo below). We reinstalled the Victron 250/60 MPPT and installed a new Deca 300Ah battery. The Victron Smart Shunt was removed since the battery communicates directly to the Cerbo GX. We switched to Midnite breakers. We also installed a Victron display for cabin visitors to more readily monitor the cable percentage charge. After attempting to start up the system again. the same issue arose. However, this time we determined that the portable 200W Grecell panels were wired backwards–black cable positive and red cable negative. We then checked the main panel cabling and found the faulty cable segment and replaced it. The MPPT turned on immediately. The system has been working great ever since. Portable panel manufacturer Grecell was contacted and they would do nothing after exchanging several emails. They say their product has functioned fine for a year despite being cabled differently than their own literature! Unfortunately, the Anker battery we now charge with the portable panels and original Renogy solar controller both compensated for the manufacturing defect, so the issue went undetected for over a year. I wrongly assumed the portable panels were cabled properly and did not note the negative polarity. The 0.6V reading at the MPPT when connected also was also overlooked. Live and learn! Thank you all for your input.

[Previous page](https://community.victronenergy.com/t/mppt-will-not-turn-on/60913.md?page=2)

[Next page](https://community.victronenergy.com/t/mppt-will-not-turn-on/60913.md?page=4)