# SmartSolar MPPT not responding

**URL:** <https://community.victronenergy.com/t/mppt-smart-solar-keine-reaktion/64550>\
**Category:** DIY\
**Tags:** mppt\_controllers, vrm, diy\
**Created:** [30 October 2026 07:07 UTC](https://community.victronenergy.com/t/mppt-smart-solar-keine-reaktion/64550 "2026-10-30T07:07:36Z")\
**Posts on this page:** 20\
**Page:** 1

<div class="post-metadata">

**Author:** ![WernerKr](https://avatars.discourse-cdn.com/v4/letter/w/96bed5/32.png) [@WernerKr](https://community.victronenergy.com/u/WernerKr)\
**Post date:** [30 October 2026 07:07 UTC](https://community.victronenergy.com/t/mppt-smart-solar-keine-reaktion/64550/1 "2026-10-30T07:07:36Z")

</div>

Hello everyone, I have a question about a solar charge controller today.

The following system: I run three 100 W/18 V/5.56 A solar panels in series via an isolator switch to a SmartSolar MPPT 100/30. Its output is connected via 16 mm² cable and a 40 A SI fuse to the positive busbar, and from there to the battery.

I have the same system a second time, also connected to the positive busbar. A Victron IP43 smart charger and a Victron DC-DC charger are also connected to the positive busbar via fuses. This system worked perfectly for several weeks.

Last week, one of the solar chargers disappeared from the VRM Portal. What I was able to find out was:

Neither LED on the unit lights up or flashes; it seems to be dead. According to VRM, it went offline at 2026-10-16 04:38:58, which was the last connection.

What else can I do? What could be wrong?

Best regards,  
Werner

---

<div class="post-metadata">

**Author:** ![VictRon54](https://avatars.discourse-cdn.com/v4/letter/v/54ee81/32.png) [@VictRon54](https://community.victronenergy.com/u/VictRon54)\
**Post date:** [30 October 2026 09:19 UTC](https://community.victronenergy.com/t/mppt-smart-solar-keine-reaktion/64550/2 "2026-10-30T09:19:34Z")

</div>

If the MPPT is connected to the battery, the blue LED should at least be flashing.

You say that absolutely nothing is happening. The first thing to check, then, is whether there is voltage at the battery input on the controller.

---

<div class="post-metadata">

**Author:** ![WernerKr](https://avatars.discourse-cdn.com/v4/letter/w/96bed5/32.png) [@WernerKr](https://community.victronenergy.com/u/WernerKr)\
**Post date:** [30 October 2026 10:28 UTC](https://community.victronenergy.com/t/mppt-smart-solar-keine-reaktion/64550/3 "2026-10-30T10:28:58Z")

</div>

There are 13.5 V at the MPPT’s battery terminal; I’ve already measured it.

---

<div class="post-metadata">

**Author:** ![VictRon54](https://avatars.discourse-cdn.com/v4/letter/v/54ee81/32.png) [@VictRon54](https://community.victronenergy.com/u/VictRon54)\
**Post date:** [30 October 2026 10:37 UTC](https://community.victronenergy.com/t/mppt-smart-solar-keine-reaktion/64550/4 "2026-10-30T10:37:21Z")

</div>

If nothing is flashing on the controller, it will be faulty.

Was the battery accidentally connected the wrong way round? The larger controllers aren’t protected against that and will break immediately.

---

<div class="post-metadata">

**Author:** ![WernerKr](https://avatars.discourse-cdn.com/v4/letter/w/96bed5/32.png) [@WernerKr](https://community.victronenergy.com/u/WernerKr)\
**Post date:** [30 October 2026 10:49 UTC](https://community.victronenergy.com/t/mppt-smart-solar-keine-reaktion/64550/5 "2026-10-30T10:49:21Z")

</div>

No, the MPPT did work for a few weeks.

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [30 October 2026 11:02 UTC](https://community.victronenergy.com/t/mppt-smart-solar-keine-reaktion/64550/6 "2026-10-30T11:02:36Z")

</div>

> [@WernerKr](#):
>
> There are 13.5 V at the MPPT’s battery terminal; I’ve already measured it.

With the solar off or on?

---

<div class="post-metadata">

**Author:** ![WernerKr](https://avatars.discourse-cdn.com/v4/letter/w/96bed5/32.png) [@WernerKr](https://community.victronenergy.com/u/WernerKr)\
**Post date:** [30 October 2026 11:08 UTC](https://community.victronenergy.com/t/mppt-smart-solar-keine-reaktion/64550/7 "2026-10-30T11:08:28Z")

</div>

With the solar panels disconnected, i.e. switched off, 0 V was measured at the solar input.

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [30 October 2026 11:27 UTC](https://community.victronenergy.com/t/mppt-smart-solar-keine-reaktion/64550/8 "2026-10-30T11:27:28Z")

</div>

Check your fuse then. There is no connection to the battery side

---

<div class="post-metadata">

**Author:** ![WernerKr](https://avatars.discourse-cdn.com/v4/letter/w/96bed5/32.png) [@WernerKr](https://community.victronenergy.com/u/WernerKr)\
**Post date:** [30 October 2026 11:32 UTC](https://community.victronenergy.com/t/mppt-smart-solar-keine-reaktion/64550/9 "2026-10-30T11:32:55Z")

</div>

> [@lxonline](#):
>
> Fuse

Why am I getting 13.5V at the battery terminals on the MPPT, then?

---

<div class="post-metadata">

**Author:** ![dennibu](https://avatars.discourse-cdn.com/v4/letter/d/7c8e57/32.png) [@dennibu](https://community.victronenergy.com/u/dennibu)\
**Post date:** [30 October 2026 11:42 UTC](https://community.victronenergy.com/t/mppt-smart-solar-keine-reaktion/64550/10 "2026-10-30T11:42:18Z")

</div>

Hi, probably a small misunderstanding. If, with the solar panels disconnected, there is 0 V on the PV side but 13.5 V on the battery side and no LED is lit, it seems the MPPT is faulty.

If you measure 0 V on the battery side with the solar panels disconnected, the DC fuse on the battery side seems to be faulty.

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [30 October 2026 11:47 UTC](https://community.victronenergy.com/t/mppt-smart-solar-keine-reaktion/64550/11 "2026-10-30T11:47:21Z")

</div>

The mppt can power up from the solar side (black start) and will then output float or close to it at the battery terminals.  
Some batteries will then wake up again.

So if you disconnect the solar and then there is nothing and the unit is off. The battery is not sending voltage to the mppt.  
That is the side you must check now.

If you connect with Victron connect there will be more information most likely

---

<div class="post-metadata">

**Author:** ![WernerKr](https://avatars.discourse-cdn.com/v4/letter/w/96bed5/32.png) [@WernerKr](https://community.victronenergy.com/u/WernerKr)\
**Post date:** [30 October 2026 11:49 UTC](https://community.victronenergy.com/t/mppt-smart-solar-keine-reaktion/64550/12 "2026-10-30T11:49:19Z")

</div>

That’s how I saw it too, [dennibu](https://community.victronenergy.com/u/dennibu). Maybe you can find a bit more in VRM?

---

<div class="post-metadata">

**Author:** ![WernerKr](https://avatars.discourse-cdn.com/v4/letter/w/96bed5/32.png) [@WernerKr](https://community.victronenergy.com/u/WernerKr)\
**Post date:** [30 October 2026 12:05 UTC](https://community.victronenergy.com/t/mppt-smart-solar-keine-reaktion/64550/13 "2026-10-30T12:05:44Z")

</div>

> [@lxonline](#):
>
> If you connect to VictronConnect, you’ll probably get more information.

I can’t connect to the MPPT; it’s no longer there.

I haven’t seen it in VRM since the last connection on 16 October.

---

<div class="post-metadata">

**Author:** ![VictRon54](https://avatars.discourse-cdn.com/v4/letter/v/54ee81/32.png) [@VictRon54](https://community.victronenergy.com/u/VictRon54)\
**Post date:** [30 October 2026 12:52 UTC](https://community.victronenergy.com/t/mppt-smart-solar-keine-reaktion/64550/14 "2026-10-30T12:52:48Z")

</div>

If you measure the voltage on the wires going into the battery regulator and get no reading, the regulator is faulty.

If necessary, remove the wires from the regulator and measure directly on them.

---

<div class="post-metadata">

**Author:** ![WernerKr](https://avatars.discourse-cdn.com/v4/letter/w/96bed5/32.png) [@WernerKr](https://community.victronenergy.com/u/WernerKr)\
**Post date:** [30 October 2026 13:15 UTC](https://community.victronenergy.com/t/mppt-smart-solar-keine-reaktion/64550/15 "2026-10-30T13:15:03Z")

</div>

> [@VictRon54](#):
>
> If you measure the voltage on the cables inside the battery controller and nothing happens, the controller is faulty.

Would this therefore be a warranty claim? What does the community think?

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [30 October 2026 13:52 UTC](https://community.victronenergy.com/t/mppt-smart-solar-keine-reaktion/64550/16 "2026-10-30T13:52:51Z")

</div>

Yes.

You have performed the basic function tests.

> **[5. Pre-RMA test form - Smart charger - 5. Pre-RMA test form - Smart charger](https://www.victronenergy.com/media/pg/Pre-RMA_Bench_Test_Instructions/en/pre-rma-test-form---smart-charger.html#UUID-cef79e4b-ea1e-1381-03eb-a61f63e0b086)**
>
> Product, system and fault information

---

<div class="post-metadata">

**Author:** ![Ernst6a](https://avatars.discourse-cdn.com/v4/letter/e/ee59a6/32.png) [@Ernst6a](https://community.victronenergy.com/u/Ernst6a)\
**Post date:** [31 October 2026 17:11 UTC](https://community.victronenergy.com/t/mppt-smart-solar-keine-reaktion/64550/17 "2026-10-31T17:11:14Z")

</div>

Hello,

a completely different approach:

Is it a smart controller?

Did you password-protect the controller?

A friendly fellow citizen once switched off my unprotected controllers.

It took me a long time to get it up and running again.

---

<div class="post-metadata">

**Author:** ![VictRon54](https://avatars.discourse-cdn.com/v4/letter/v/54ee81/32.png) [@VictRon54](https://community.victronenergy.com/u/VictRon54)\
**Post date:** [31 October 2026 18:52 UTC](https://community.victronenergy.com/t/mppt-smart-solar-keine-reaktion/64550/18 "2026-10-31T18:52:05Z")

</div>

Werner says it’s the smartsolar.

The smartsolar now has its own PIN code.

You can always change the PIN code using the PUK code printed on the device; that can’t be too difficult.

---

<div class="post-metadata">

**Author:** ![WernerKr](https://avatars.discourse-cdn.com/v4/letter/w/96bed5/32.png) [@WernerKr](https://community.victronenergy.com/u/WernerKr)\
**Post date:** [31 October 2026 18:54 UTC](https://community.victronenergy.com/t/mppt-smart-solar-keine-reaktion/64550/19 "2026-10-31T18:54:50Z")

</div>

> [@Ernst6a](#):
>
> Did you protect the controller password?

Yes, I did. What I can’t stop thinking about is the time of the outage, too. Surely nobody fiddles with that any more.

---

<div class="post-metadata">

**Author:** ![WernerKr](https://avatars.discourse-cdn.com/v4/letter/w/96bed5/32.png) [@WernerKr](https://community.victronenergy.com/u/WernerKr)\
**Post date:** [3 November 2026 15:31 UTC](https://community.victronenergy.com/t/mppt-smart-solar-keine-reaktion/64550/20 "2026-11-03T15:31:12Z")

</div>

Hello everyone, and have a good day at work. After a bit of back and forth with the delivery company, I got a return label today to send it back to the supplier. They want to carry out their own fault analysis, so let’s see what comes of it.

I’ll keep you posted.

Cheers,  
Werner