Hello everyone, I have a question about a solar charge controller today.
The following system: I run three 100 W/18 V/5.56 A solar panels in series via an isolator switch to a SmartSolar MPPT 100/30. Its output is connected via 16 mm² cable and a 40 A SI fuse to the positive busbar, and from there to the battery.
I have the same system a second time, also connected to the positive busbar. A Victron IP43 smart charger and a Victron DC-DC charger are also connected to the positive busbar via fuses. This system worked perfectly for several weeks.
Last week, one of the solar chargers disappeared from the VRM Portal. What I was able to find out was:
Neither LED on the unit lights up or flashes; it seems to be dead. According to VRM, it went offline at 2026-10-16 04:38:58, which was the last connection.
Hi, probably a small misunderstanding. If, with the solar panels disconnected, there is 0 V on the PV side but 13.5 V on the battery side and no LED is lit, it seems the MPPT is faulty.
If you measure 0 V on the battery side with the solar panels disconnected, the DC fuse on the battery side seems to be faulty.
The mppt can power up from the solar side (black start) and will then output float or close to it at the battery terminals.
Some batteries will then wake up again.
So if you disconnect the solar and then there is nothing and the unit is off. The battery is not sending voltage to the mppt.
That is the side you must check now.
If you connect with Victron connect there will be more information most likely
Hello everyone, and have a good day at work. After a bit of back and forth with the delivery company, I got a return label today to send it back to the supplier. They want to carry out their own fault analysis, so let’s see what comes of it.