SmartSolar MPPT not responding

Hello everyone, I have a question about a solar charge controller today.

The following system: I run three 100 W/18 V/5.56 A solar panels in series via an isolator switch to a SmartSolar MPPT 100/30. Its output is connected via 16 mm² cable and a 40 A SI fuse to the positive busbar, and from there to the battery.

I have the same system a second time, also connected to the positive busbar. A Victron IP43 smart charger and a Victron DC-DC charger are also connected to the positive busbar via fuses. This system worked perfectly for several weeks.

Last week, one of the solar chargers disappeared from the VRM Portal. What I was able to find out was:

Neither LED on the unit lights up or flashes; it seems to be dead. According to VRM, it went offline at 2026-10-16 04:38:58, which was the last connection.

What else can I do? What could be wrong?

Best regards,
Werner

If the MPPT is connected to the battery, the blue LED should at least be flashing.

You say that absolutely nothing is happening. The first thing to check, then, is whether there is voltage at the battery input on the controller.

There are 13.5 V at the MPPT’s battery terminal; I’ve already measured it.

If nothing is flashing on the controller, it will be faulty.

Was the battery accidentally connected the wrong way round? The larger controllers aren’t protected against that and will break immediately.

No, the MPPT did work for a few weeks.

With the solar off or on?

With the solar panels disconnected, i.e. switched off, 0 V was measured at the solar input.

Check your fuse then. There is no connection to the battery side

Why am I getting 13.5V at the battery terminals on the MPPT, then?

Hi, probably a small misunderstanding. If, with the solar panels disconnected, there is 0 V on the PV side but 13.5 V on the battery side and no LED is lit, it seems the MPPT is faulty.

If you measure 0 V on the battery side with the solar panels disconnected, the DC fuse on the battery side seems to be faulty.

The mppt can power up from the solar side (black start) and will then output float or close to it at the battery terminals.
Some batteries will then wake up again.

So if you disconnect the solar and then there is nothing and the unit is off. The battery is not sending voltage to the mppt.
That is the side you must check now.

If you connect with Victron connect there will be more information most likely

That’s how I saw it too, dennibu. Maybe you can find a bit more in VRM?

I can’t connect to the MPPT; it’s no longer there.

I haven’t seen it in VRM since the last connection on 16 October.

If you measure the voltage on the wires going into the battery regulator and get no reading, the regulator is faulty.

If necessary, remove the wires from the regulator and measure directly on them.

Would this therefore be a warranty claim? What does the community think?

Yes.

You have performed the basic function tests.

Hello,

a completely different approach:

Is it a smart controller?

Did you password-protect the controller?

A friendly fellow citizen once switched off my unprotected controllers.

It took me a long time to get it up and running again.

Werner says it’s the smartsolar.

The smartsolar now has its own PIN code.

You can always change the PIN code using the PUK code printed on the device; that can’t be too difficult.

Yes, I did. What I can’t stop thinking about is the time of the outage, too. Surely nobody fiddles with that any more.

Hello everyone, and have a good day at work. After a bit of back and forth with the delivery company, I got a return label today to send it back to the supplier. They want to carry out their own fault analysis, so let’s see what comes of it.

I’ll keep you posted.

Cheers,
Werner