After upgrading to v1.33, Error 41 for the isolation resistance popped up.
During operation, the resistance is at around 50-60Meg, when the unit is off, it drops to around 1Meg. The error happend twice during shutdown in the evening when the unit was turning off. Not sure if this is related, but I have slightly overcommited the unit, so the generator resistance might be more at the lower end, but well within spec of the unit in terms of short circuit current of the panels. Max. System voltage as reported is at around 370V. 48V Lithium battery system.
I downgraded again to v1.29 and the system is back to normal - just flagging here in case others see the same behavior.
Fair, but the error also does not reset once the iso resistance is back to normal, and also cannot be cleared without a full restart of the GX. Which seems kind of off.
Anyhow, I will check some connections - although, as said, the resistance values are ok. I saw them fluctuating a lot when the current controller does larger jumps in the power (e.g. when going from ~600W to about 1800W abruptly, due to clouds, the iso resistance jumps from 53Meg down to 14Meg, and then at the same power point back up to 53Meg). So there could be some hidden bug in the firmware which was previously not seen due to the error not beeing reported. A small time delay, slower frequency or a grace period after large power point / state machine changes could solve that.
You should be grateful that this notification appeared with the update. Your PV array is in urgent need of an inspection of all connections, as well as a check of all PV cabling for integrity.
It would seem you aren’t understanding the gravity of what is happening there.
Check everything.
Cable chafing maybe
Water ingress or dew or something water related with a possible bad mc4 or join letting it in.
Panel fault
Editing to check
It is triggering here not at the 100k ohms? But at the MΩ range?
I ma noting the time during shutdown in the evening when the unit was turning off from your post
No not really, the exact value is not logged - timing just always coincides with the boost shutting down.
I’m sorry, but I dont really look for safety or electical advice, the post was more meant for victron so they can start working on a fix or an improvement. EEng, PHd, several national and international EE safety committees, I kind of write the rules you guys need to adhere to. So yeah, please, just someone at victron have a look at how the iso meas is currently interacting with the converter stage - again since this was not properly distributed via CAN before or not handles in the GXs, please recheck with different panal impedance arrangements in terms of panel SCC and then come up with a fix. Or dont, whatever.
further info: if either channel is removed, the error goes away. It cont. discharges the powerless panels at night, and wen both channels are active, it seems like it then also spoils the measurement. Contact me for a screen recording if required. It also seems like the amount of channels matters and the value displayed is not in line with parallel/series connection so I suspect something with the way the stage searches for enough power available. I habe around 45-65V at night on the panels due to street lights though…
And to make a bug report without doing the due diligence isn’t exactly ruling out installation issues. And Victron cannot make a physical check over the internet.
Appreciate that you didn’t come looking for advice or electrical troubleshooting but without more specifics also for your particular installation it is also impossible to then investigate a potential bug. Good to know you are a professional
Then you would know how to report a potential problem and it would be more information. Like qualifying this statement.
And being more specific about your installation.
Trying to work out whether it is triggering because at day end voltage is dropping off and therefore power and by association resistance maybe as a cause. Would mean a change in how things are detected.
So investigative questions need to be asked and the conditions specific to your trigger explored.
In your Victron connect history has the error been reported before?
The thing that has changed is that is pushes the notification to the GX. So it is possible that the error has been detected before but not noticed.
For me its constantly alarming in the meg ohm range nothing has changed in over four years , there seems to be a bug. Doesn’t matter if its night or day, alarm is triggering all the time.
There is no error here. If the system is in good working order and everything is within acceptable tolerance limits, the insulation resistance will always be 100 MΩ in dry weather, even under load. In rainy weather, I have observed it drop to 60 MΩ, but I have never seen it go any lower than that.
High-quality components and proper installation are the key to flawless operation!
I think the error is meant to be permanent not transient in case it is missed.
It shouldn’t be necessary to reboot the GX but switching the mppt of and on should clear it (or a FW roll back). It does seem like there are a few random systems where the detection would have to be revised a bit.
I have plenty in the field without issues on the new firmware.
Yes I think this MPPT might be a bit sensitive as my other two are almost identical configurations and don’t have the issue and swapping to one of the other MPPT arrays still gives the error so I have rolled back to 1.29 on that MPPT only.