# MPPT 150/45 high voltage error

**URL:** <https://community.victronenergy.com/t/mppt-150-45-high-voltage-error/20627>\
**Category:** DIY\
**Tags:** mppt\_controllers, domestic, parallel, beginner\
**Created:** [31 January 2025 17:39 UTC](https://community.victronenergy.com/t/mppt-150-45-high-voltage-error/20627 "2025-01-31T17:39:16Z")\
**Posts on this page:** 6\
**Page:** 1

<div class="post-metadata">

**Author:** ![Erik1](https://avatars.discourse-cdn.com/v4/letter/e/8e8cbc/32.png) [@Erik1](https://community.victronenergy.com/u/Erik1)\
**Post date:** [31 January 2025 17:39 UTC](https://community.victronenergy.com/t/mppt-150-45-high-voltage-error/20627/1 "2025-01-31T17:39:17Z")

</div>

On my shed there are 12 Gintech 260MB6A panels of 260 Wp. Output voltage of these panels is 32.38V (at 8 Amp). I connected these panels to an MPPT; mounting: 4 panels in series (4x33V = 132V) and 3 of such sets in parallel (3x 8 A = 24A). Solar Charger used: Victron MPPT 150/45 rev3. Firmware v 1.64

In the summer I occasionally had an Error code #33 for a few seconds: ‘Input voltage too high’. But now, in the middle of winter, I also have that error message with a certain regularity. And the duration of the errors seem to grow.

 ![image](https://europe1.discourse-cdn.com/victron/original/2X/6/69d1c363d7cc8d6754d56462f249153f919e2ef5.png)

The solar charger is connected to 48V batteries.  
Does anyone have an idea what could be the cause?

---

<div class="post-metadata">

**Author:** ![Netrange](https://avatars.discourse-cdn.com/v4/letter/n/7ab992/32.png) [@Netrange](https://community.victronenergy.com/u/Netrange)\
**Post date:** [31 January 2025 17:43 UTC](https://community.victronenergy.com/t/mppt-150-45-high-voltage-error/20627/2 "2025-01-31T17:43:30Z")

</div>

In winter, you can easily add 20% yield voltage due to the low temperatures. Your Mppt is running at the limit of the input voltage. It is best to change your wiring to 3 panels in series

---

<div class="post-metadata">

**Author:** ![Erik1](https://avatars.discourse-cdn.com/v4/letter/e/8e8cbc/32.png) [@Erik1](https://community.victronenergy.com/u/Erik1)\
**Post date:** [31 January 2025 17:45 UTC](https://community.victronenergy.com/t/mppt-150-45-high-voltage-error/20627/3 "2025-01-31T17:45:46Z")

</div>

Thank you. And that would be OK for the summer too?

---

<div class="post-metadata">

**Author:** ![Netrange](https://avatars.discourse-cdn.com/v4/letter/n/7ab992/32.png) [@Netrange](https://community.victronenergy.com/u/Netrange)\
**Post date:** [31 January 2025 17:48 UTC](https://community.victronenergy.com/t/mppt-150-45-high-voltage-error/20627/4 "2025-01-31T17:48:05Z")

</div>

In summer, the internal resistance increases due to the higher temperature … the PV voltage drops … but you have more sun throughout the day and not such strong peaks

---

<div class="post-metadata">

**Author:** ![Erik1](https://avatars.discourse-cdn.com/v4/letter/e/8e8cbc/32.png) [@Erik1](https://community.victronenergy.com/u/Erik1)\
**Post date:** [31 January 2025 17:50 UTC](https://community.victronenergy.com/t/mppt-150-45-high-voltage-error/20627/5 "2025-01-31T17:50:27Z")

</div>

Many thanks

---

<div class="post-metadata">

**Author:** ![DSeptembre](https://avatars.discourse-cdn.com/v4/letter/d/dbc845/32.png) [@DSeptembre](https://community.victronenergy.com/u/DSeptembre)\
**Post date:** [31 January 2025 19:48 UTC](https://community.victronenergy.com/t/mppt-150-45-high-voltage-error/20627/6 "2025-01-31T19:48:01Z")

</div>

I suggest using the Victron MPPT Calculator to make sure you are within the parameters of this charge controller. You can enter your location and module specifications here and it will tell you which MPPT to use. It will also give you a graph of the solar yield for each month of the year.

> **[MPPT Calculator - Victron Energy](https://www.victronenergy.com/mppt-calculator)**
>
> MPPT Calculator - Victron Energy