MPPT 100|30 Remote Control Enable
Hi All,
I am wanting to use the remote control feature of the MPPT 100|30.
So far I am requesting external control mode via VE.Direct with this command:
SEND :80E2000021D - REQUEST MODE 02 EXTERNAL CONTROL MODE
RESP :80E2000021D - CONFIRMATION RESPONSE
Then I immediately check the network status register to see a change of mode:
SEND :70F20001F - REQUEST READ 0x200F
RESP :70F2000041B - 04 UNIT OPERATES STAND-ALONE (NETWORK STATUS REGISTER)
But I think the returned code 04 means the MPPT is still in stand-alone.
Looking at the capabilities register:
SEND :74001000D
RESP :740010076EF090897 - DATA 0x0809EF76
I believe external control support (Bit 15) is set, I think that means the MPPT is capable of remote control.
Does anyone know if this is the correct way to gain remote control using VE.Direct?
Thanks,
Matthew
FYI here is a solution I found:
:80E20000916:801200098088C:81520000C000C
First packet - Set network mode @ 200E TO 0x09
Second packet - Charge voltage set-point @ 2001 to example 0x0898 (22V)
Third packet - Charge current limit @ 2015 to example 0x0c (1.2A)
Cheers,
Matthew