MP2 3000/48 as a backup charger

Hello, I’m using a 4 MP2 as a charger for the Pytes V5 battery. The MP2 is powered by a 5 kVA diesel generator with AVR regulation. The MP2 charges the Pytes for about 2 minutes and then shuts down for no apparent reason. In VEConfig, I’ve configured the MP2 for no grid, extended frequency range, dynamic current limiting, UPS disabled, and poor input voltage.

The input frequency is set to a maximum of 52.2 Hz, and the current is set to 13 A. That should be fine, but the MP2 still shuts down after about 1 to 3 minutes.

The system is a three-phase ESS setup and runs without any problems.

What could be causing this?

Best regards,
Thorsten

Para nur MP2 ladegerät für Notstrom Diesel.vsc (5.9 KB)

How do the generator’s voltage and frequency behave when the Multi is charging?
Does the generator run steadily, or does the RPM fluctuate?

The settings look pretty good, so it should work.

The voltage is 232 V; at 2,000 W, the frequency fluctuates between 51.4 and a maximum of 52.2 Hz.

Try specifying a lower charging power—just charge at 1,000 watts—and see what it does then?

I tried a few things today, and now everything is working as it should.

  • Updated the firmware to v.568. There was an issue with the old FW where AC IN wasn’t activated properly due to poor voltage.
  • Changed the Crid code from None to Other-no compliant and also disabled LOM monitoring.

In case anyone else has a similar problem.