Hello,
So I’m new to the community so having searched using as many ways as I can, I can find the answer.
I have a 48v system in my van which charges from 2 mppt chargers, and also via a Multiplus 48/3000. It will charge from the van through a bidirectional 12/48 charger when it’s finally connected.
All good so far! Now comes the interesting part I have a temp/backup 48-12 converter and I measure the load on this with a smart shunt which displays as my DC loads on the Cerbo.
still all good
I have just added a 48v AC system and wanted to know the draw (nice to know) and was going to put a second smart shunt on this load, but can I display this directly on the CERBO?
Basically having 2 DC loads displayed ,1 for 12V circuits like I have and 1 for 48V AC ?
My current screen DC load is my 12v smart shunt as DC meter. As you can see the battery is pulling 348w so AC is pulling 300ish I guessSo being really SAD I’ll reply to my own post in case anyone searches the same.
it works !!! With both Shunts set as DC Meter and DC Load, the power from the 48v shunt is added to the power from the 12v shunt.
Clicking DC Loads on the Cerbo opens a window showing both shunts and their information