OGPS
(Ed @ Off-Grid Power Systems - offgridps.com)
1
In North America, we split a single phase AC grid connection into two phases with 180° phase rotation. This question could also be applicable to three phase systems connected to one or two phases on the AC input. In either case, “switch as group” would be disabled in VE.Bus System Configurator to allow connection to just one phase on the input side.
The question: Does the firmware in the inverters properly handle the ground relay in such a configuration?
Let’s say we have an RV or a boat that has a 50A shore power system. In North America, that means four wires: L1, L2, N, G with L1 & L2 180° out of phase and L1-N=120V, L2-N=120V, L1-L2=240V. In a mobile system, we want the ground relays in the inverters to open when there is an AC source and close when in inverting mode. That’s simple, and easily understood.
However, if “switch as group” is disabled and only one of the two phases is available, one inverter will pass-thru AC power (and potentially charge) while the second inverter is inverting. If the ground relays are configured in both inverters, then one inverter would open its ground relay (the one with an incoming AC phase) while the other inverter has its relay closed (inverting).
Since the neutral is common to both inverters and presumably there is a N-G bond at the AC source, why doesn’t the use of two inverters (without an AT or external ground relay) with their ground relays enabled in VEconfigure create a second N-G bond when only one phase is connected to the input?
Does the firmware handle this? I’ve not tested this since it occurred to me this morning and it will be a few days until I can build a test system to check for myself.
I’ve not experienced issues with GFCI outlets inside the RV/boat stemming from a single-phase input and multiple N-G bonds, and I’m a little embarrassed that I didn’t think about this until now.
However, I thought that “the rule” was that if you use the Ground Relay, you should only enable it on the L1 Master to avoid multiple ground bonds. Problem is, I cannot remember where I read that “rule”.
There should only ever be one neutral to ground Bond per separately derived system.
You won’t see any issues on downstream GFCIs, from their perspective everything’s fine.
But if you had an upstream GFCI, it would immediately trip. Most 50 amp outlets are not GFCI protected though, so power will stay on, but you can have weird currents going places they shouldn’t.
Can’t speak to how Victron stuff should be configured, but they should have some documentation on that as it’s pretty important.
What Rick says does make sense to me.
OGPS
(Ed @ Off-Grid Power Systems - offgridps.com)
6
Yes, no question there. Since the neutrals and grounds are common (at least in our installations) there hasn’t been and isn’t likely to have a problem, even when running degraded on a single-leg 15A or 30A dogbone. But, it is a change we’ll make going forward since it’s the right thing to do. I was mostly curious if the firmware had any awareness of the duplicate ground relays in a split-phase configuration with switch as group disabled and two ground relays. I don’t have any definitive knowledge on that, but I don’t think it does. The practical upshot is for the vast majority of RVs that don’t have 240V loads inside (some large coaches do have 240V loads) AND when plugged into one leg of shore power where one inverter is passing-through and the other is in inverter mode, so long as the dogbone adapters are standard and the system is installed with proper neutrals and grounds, there wouldn’t be an issue.
For large coaches that have 240V loads and want to plug into 15A or 30A single-leg shore power, then it’s probably advisable to disable the ground relays internally, use an AT with its single N-G relay (but an AT is against NEC code in article 551), or disable the ground relays and use an external ground relay that works whether one or both legs are present.