Dear friends,
I have system:
3x Quattro 10000
1x Fronius Verto 30.0
4x MPPT 250/100
30x Pylontech US3000C with LV-hub
1x GRID energymeter EM540 (connected to CERBO)
5x energymeters EM540 measuring all AC_out loads in house (connected to RPI5 with NODE-RED)
and MK3 lastest cerbo GX connected with victron system and with FRONIUS as modbus device.
Victron is the best for stable system with creative opportunity to tune this system and collect data from.
I programmed own dashboard, where due NODE-RED from victron palette I’m able to collect all kind of informations and send it into RPI5 with NODE-RED, where all work is done.
My victron system has AC-OUT only and all power loads are connected after 5 energymeters EM540 so I calculate real AC_OUT consumption - my question is simple:
real consumption of house (sum of energymeters): 2142W //detailed L1-L3 on picture
AC_out information from QUATTROs (system node->venus system->AC Consumption L1-L3): 2324W //detailed L1-L3 on picture also red color difference
battery: -3052W
till today, when I had no AC_OUT powermeters I understood difference battery and AC-OUT…it was clear for me, that difference is internal consumption of QUATTROS when transforming dc/ac
But today… whole day I was monitoring these values and see 2 differences in system and would like to understand:
difference is battery and AC_out (-54 w is GRID) 3052-2324-54=674wat
difference real AC_out and AC_out measured by powermeters 2324-2142=182W
Please…I just want to know…if I’m right in this mathematic and where is 856W missing?
the battery rate is the dc-side. You can’t compare it with AC-Side values without considering conversion losses from dc to ac.
so, you have (2324 + 54) / 3052 ~ 77%. For a 30kW Inverter running at ~ 2400W ( 8% Load) a quite common figure I’m afraid. Inverters have their efficiency sweet-spot between 30% to 70% load usually and low load is… to be avoided.
I also have Pylontech batteries, and to add a small “relaxation” on that: They usually display their DC-Power to high and therefore during discharging also underestimate their soc. You may have noticed them stucking for quite long around 10/11%, where they “correct” their reporting error by awaiting Voltage-Thresholds to be reached.
So, another 5ish% “apparent efficiency loss” are burried in the overreported dc power as well.
Thanks a lot for the professional and clear explanation, it makes total sense regarding the low load efficiency sweet-spot and the Pylontech BMS reporting behavior.
I have a follow-up question: Would adding a Victron SmartShunt (3 quattros will be connected via it) on the negative DC bus (connected via VE.Direct to Cerbo-GX) help mitigate the DC power over-reporting?
And if Cerbo uses the Shunt for DC measurements while keeping the rest of the Pylontech data, would that clean up the power balance numbers?
The smartshut is considered very precise. So, that would indeed deliver “better” dc-power values than the pylontech bms.
Unfortunately I have no personal experience with it, so I can’t say how it works together with an actual BMS, where you want to keep communication. The smartshunt could be added and shown as additional battery monitor for sure, but as long as you want dvcc to utilize the BMS values (CCL, CVL), the Pylontech monitor needs to be the active one in dvcc and will provide the “big” DC-Power value visible in the tile.
A possible solution could be to create a 3rd, virtual battery monitor in Node-Red, give it all the pylontech values, but the power values from the shunt - and select that monitor as your default system-monitor.
For the soc, you would need to see, who does it better. Since a while, I have a serial-cable attached to my pylontechs and read all the individual module values… and since then I would tend to say: The shunts calculated soc would probably be better.
Side Node
Background for my assessment: Each Module reports quite different currents [and therefore dc power] the main-module just accumulates all those. I have seen module soc drifts of upto 20%, only above 90 and bellow 11% they start to show common sense…
Different soc and different power values are most likely the result of not very accurate current measurements, so that error propagates everywhere, where Voltage is currently not the leading factor.
I’ve run some tests, discharging them totally at a constant rate, and they all line up nicely again before hitting their advertised 5%. So, technically they work fine and as promised, also no “real” differences in discharging - just the guessing in the “free flight zone” is quite inaccurate:
Here, the module that hit 11% first was happily discharging at 11% for almost 1h and 20min, before it reached its “actual” 11% voltage at about the same time as the others:
In system setup on the GX you can choose the SmartShunt as the battery monitor so the SOC, voltage and current displayed for the battery on the GX will come from the SmartShunt. Under DVCC you would make sure the pylontech is selected for the managing BMS so you still get the correct CCL & CVL.