Continuing the discussion from DESS API Not Refreshing UK Octopus Prices :
Responding to Dave Walker
Hi Dave
I am having to start a new topic since I am limited to three replies to the previous topic.
Here is the screen shot of Node Red for my Myenergi Zappi charger
Many thanks for helping. James
JAF065
September 15, 2026, 3:37pm
2
Message above is for @DaveWalker
DaveWalker
(dave walker)
September 15, 2026, 3:47pm
3
How are you planning to use the Victron system
Ess with I presume scheduled charging 11.30pm to 5.30am
Dess and that takes care of the charging using the fix schedule.
Asking because it will change how we get it to behave when the car is plugged in
Also do you want the battery to charge or simply not discharge when the car is charging ?
Dave
JAF065
September 15, 2026, 4:04pm
4
Probably easier just to stick with ESS since that is already working well with Octopus. If it were possible to get the battery to charge from the grid in the smart charging slots that would be good.
DaveWalker
(dave walker)
September 16, 2026, 8:21am
5
You need to add 3 nodes from the bottom of the pallet . Custom input, custom output and virtual switch
Setup the switch as a toggle with name Autocharge. This will enable us to turn off function from VRM dashboard/remote console
In both the custom input and output select these drop downs - the slightly cut-off word on the screenshot is state
Dave
DaveWalker
(dave walker)
September 16, 2026, 8:28am
6
Now add two change nodes from near the top of the pallet and connect like this
Set the change node connected to the custom input like this. Make sure you set the dropdowns to Flow and Msg
Here is the setup for the change node connected to the Toggle switch
DaveWalker
(dave walker)
September 16, 2026, 9:40am
7
Slight mistake we need to remove a connection
and now final push - blue arrows are switch nodes, red arrows are change nodes
Change the zappi info inject node to inject automatically at a interval of 1 min - do not go faster of you will get rate limited
In use change mode is set up like this - change the values so they only turn on and off when mains not solar charging
you add the second condition via the + near the bottom
Here are the rest of the nodes - we use these to set the correct values, enable auto charging with the toggle and to prevent constantly trying to set a mode when it is already in that mode
Hopefully that all makes sense
Dave
JAF065
September 16, 2026, 11:44am
8
I think I have done all that. I have three separate flows now:
Is that correct or should they be linked together somehow?
Thanks
DaveWalker
(dave walker)
September 16, 2026, 11:57am
9
No they are separate. The status is passed between by using the flow context which you should have set
Once deployed you should also have a toggle switch on the vrm dashboard seen by pressing here
This will enable you to turn the function off it it causes problems
Dave
JAF065
September 16, 2026, 1:32pm
10
Brilliant. I think that is working (I had a problem that I hadn’t spotted the variables had to be set to be numbers not strings but fixed that). I will have to do some more testing with the car plugged in but all seems to be good for now.
Thanks very much for your help.
James
DaveWalker
(dave walker)
September 16, 2026, 1:36pm
11
No probem at all glad to help.
Dave
p.s. you are a qualified node red programmer now