Mains meter configuration
I got an EasySolar-II GX connected to L1 and today I got the VM-3P75CT connected to all three incoming phases to my house.
But it looks like I got something configured wrong? Most of the load is on L1, the same phase as the EasySolar is connected to, but it is invisible. I expected it to show up under AC Loads, and it would indicate what is made up for on that phase?
To doublecheck you can also see pretty much all PV power going into the battery. And while it shows Grid 0 W in VRM, the energy meter on my house is showing around 500-1000w being imported from the grid.
However…
When there is some additional loads on any of the other phases, the load on L1 shows up under AC Loads, as well as the L2 and L3 loads. This is how I expected it would be all the time.
Also it shows the PV power being put into the inverter, instead of all of it going into the battery.
Are there some configuration which could make it behave like this?
I figured it out… After the L1 CT clamp got pushed into place in the distribution board the latch snapped open. All clamps are now held closed by the latch and a zip-tie, and the measurements are as I expect them to be. :grinning_face: