# Low battery Alarm

**URL:** <https://community.victronenergy.com/t/low-battery-alarm/17757>\
**Category:** Q&A and troubleshooting\
**Tags:** parallel, beginner, bms\
**Created:** [6 January 2025 17:18 UTC](https://community.victronenergy.com/t/low-battery-alarm/17757 "2025-01-06T17:18:04Z")\
**Posts on this page:** 11\
**Page:** 1

<div class="post-metadata">

**Author:** ![innocentephraim](https://avatars.discourse-cdn.com/v4/letter/i/85e7bf/32.png) [@innocentephraim](https://community.victronenergy.com/u/innocentephraim)\
**Post date:** [6 January 2025 17:18 UTC](https://community.victronenergy.com/t/low-battery-alarm/17757/1 "2025-01-06T17:18:04Z")

</div>

Dear friends, i am sure you remember my issue with parallel connection a few days ago. i also attempted to reconfigure the two inverter in 120 degree set up, but the inverter kept giving me a no grid alarm which was weird as grid was on. io finally decided to connect one inverter instead and now i have a new problem. i have endless low battery alarm. i checked all connections which at\re all tight. is there anything i should look out for?

 ![Screenshot 2025-01-06 at 20.13.36](https://europe1.discourse-cdn.com/victron/original/2X/0/08a681a58baaf8ee0437ac2880d490169d486cf7.png)  
 ![Screenshot 2025-01-06 at 20.14.12](https://europe1.discourse-cdn.com/victron/original/2X/d/d2ebd6d6ba25b4ed6d976c6ec9f693eea77350c4.png)  
 ![Screenshot 2025-01-06 at 20.14.33](https://europe1.discourse-cdn.com/victron/original/2X/d/dea8a92749db7b2f8bde6aef29c34700d7ce21cc.png)

---

<div class="post-metadata">

**Author:** ![Komar](https://avatars.discourse-cdn.com/v4/letter/k/85f322/32.png) [@Komar](https://community.victronenergy.com/u/Komar)\
**Post date:** [6 January 2025 18:23 UTC](https://community.victronenergy.com/t/low-battery-alarm/17757/2 "2025-01-06T18:23:29Z")

</div>

Battery settings in the inverter?  
What baterry, BMS you use?

---

<div class="post-metadata">

**Author:** ![innocentephraim](https://avatars.discourse-cdn.com/v4/letter/i/85e7bf/32.png) [@innocentephraim](https://community.victronenergy.com/u/innocentephraim)\
**Post date:** [6 January 2025 18:55 UTC](https://community.victronenergy.com/t/low-battery-alarm/17757/3 "2025-01-06T18:55:14Z")

</div>

I am using 4 freedom won con nected in parallel, i use the battery BMS

---

<div class="post-metadata">

**Author:** ![Komar](https://avatars.discourse-cdn.com/v4/letter/k/85f322/32.png) [@Komar](https://community.victronenergy.com/u/Komar)\
**Post date:** [6 January 2025 20:23 UTC](https://community.victronenergy.com/t/low-battery-alarm/17757/4 "2025-01-06T20:23:25Z")

</div>

Well, I don´t have an experience with this battery. But normaly it is good to follow inwerter settings recomended by bat. manufacturer or by Victron for your battery… I belive you checked it…

---

<div class="post-metadata">

**Author:** ![Komar](https://avatars.discourse-cdn.com/v4/letter/k/85f322/32.png) [@Komar](https://community.victronenergy.com/u/Komar)\
**Post date:** [6 January 2025 20:43 UTC](https://community.victronenergy.com/t/low-battery-alarm/17757/5 "2025-01-06T20:43:09Z")

</div>

As I see the hraph, the voltage measured by battery and by inverter is dfferent. What about wire dimensions, lenght? Did you tryied to measure voltage depth between the battery and the iverter? It looks, that resistance is too big, voltage is dropping down especially when you take more power from the battery, bat pictude is a bit small to be sure with it.

---

<div class="post-metadata">

**Author:** ![innocentephraim](https://avatars.discourse-cdn.com/v4/letter/i/85e7bf/32.png) [@innocentephraim](https://community.victronenergy.com/u/innocentephraim)\
**Post date:** [7 January 2025 07:06 UTC](https://community.victronenergy.com/t/low-battery-alarm/17757/6 "2025-01-07T07:06:22Z")

</div>

I figured it out, i chargenged the master battery to a different one, it worked. looks like the bms of the first battery was messed up.  
Thank you Martin

---

<div class="post-metadata">

**Author:** ![farmeroz](https://avatars.discourse-cdn.com/v4/letter/f/cdc98d/32.png) [@farmeroz](https://community.victronenergy.com/u/farmeroz)\
**Post date:** [16 January 2025 09:31 UTC](https://community.victronenergy.com/t/low-battery-alarm/17757/7 "2025-01-16T09:31:00Z")

</div>

quattro 48/10000  
victron PV 450 inverter charging 48V  
Victron smart li batteries  
2 strings each 200aH  
cerbo  
victron bms  
autocharge set at 50% (active)

 ![victron lowbat](https://europe1.discourse-cdn.com/victron/original/2X/f/f4c2cf4675d58f0101fccc0603480de26d9d2dfe.jpeg)

Low battery alarm, irritating  
not really enough info on the alarm  
“low battery” could be

1. Quattro thinks the battery voltage is low
2. An individual cell is low
3. something else thinks its low.

Clearly with DOC at 67% and Vbatt at 52.2V there should be no low battery warning.  
So what is triggering it?  
It would be mightly helpful if error messages said what was causing the error, rather than some generic error.

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [2 March 2025 18:11 UTC](https://community.victronenergy.com/t/low-battery-alarm/17757/8 "2025-03-02T18:11:22Z")

</div>

ESS assistant is probably triggering it.  
Alternatively the final volt drop is not being captured in the 60s between logs and the FW voltage does collapse a bit under sudden loads.

Is everything [programmed accordingly](https://www.victronenergy.com/live/battery_compatibility:freedomwon)?

---

<div class="post-metadata">

**Author:** ![Victorokuna](https://avatars.discourse-cdn.com/v4/letter/v/d6d6ee/32.png) [@Victorokuna](https://community.victronenergy.com/u/Victorokuna)\
**Post date:** [9 August 2025 05:01 UTC](https://community.victronenergy.com/t/low-battery-alarm/17757/9 "2025-08-09T05:01:53Z")

</div>

Victron is just over rated.

I have got a 5 kva multiplus inverter running 3 batteries of BYD and the inverter is tripping on low voltage while the byd batteries are 54 volts.

---

<div class="post-metadata">

**Author:** ![system](https://europe1.discourse-cdn.com/victron/original/1X/21a9a7b5db7c6339715f993568736a7053199995.png) [@system](https://community.victronenergy.com/u/system)\
**Post date:** [25 August 2025 17:30 UTC](https://community.victronenergy.com/t/low-battery-alarm/17757/10 "2025-08-25T17:30:14Z")

</div>

This topic was automatically closed 14 days after the last reply. New replies are no longer allowed.

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [25 September 2025 05:44 UTC](https://community.victronenergy.com/t/low-battery-alarm/17757/11 "2025-09-25T05:44:28Z")

</div>

> [@Victorokuna](#):
>
> tripping on low voltage

Ypu have scome to the conclusion and not explained any troubleshooting or how you came to the conclusion.

Is it the ve bus giving the low warning? Is it the battery sending the low warning?

Almost all low battery warning we have dealt with in the field have a cause and can be corrected with adjustments. Or in one case replacements.