# Loads connected to AC in during external anti-islanding disconnection

**URL:** <https://community.victronenergy.com/t/loads-connected-to-ac-in-during-external-anti-islanding-disconnection/59840>\
**Category:** Q&A and troubleshooting\
**Tags:** parallel, expert, multiplus-ii\
**Created:** [28 June 2026 18:54 UTC](https://community.victronenergy.com/t/loads-connected-to-ac-in-during-external-anti-islanding-disconnection/59840 "2026-06-28T18:54:26Z")\
**Posts on this page:** 5\
**Page:** 1

<div class="post-metadata">

**Author:** ![gallowayoffgrid](https://avatars.discourse-cdn.com/v4/letter/g/439d5e/32.png) [@gallowayoffgrid](https://community.victronenergy.com/u/gallowayoffgrid)\
**Post date:** [28 June 2026 18:54 UTC](https://community.victronenergy.com/t/loads-connected-to-ac-in-during-external-anti-islanding-disconnection/59840/1 "2026-06-28T18:54:26Z")

</div>

Hi Friends, can anyone help me with this?

I am building a grid-parrallel multiplus-2 based system, it is for the UK and therefore requires G99 anti-islanding. I am providing this by using an external Ziehl based relay, which disconnects the whole installation.

The relay is remote to the inverter, with only one set of cables linking them. I expected I could simply connect the AC supply/loads to the AC in of the multiplus, but I am now worrying that the inverter will isolate the loads which are on its AC in once the G99 relay activates, despite the fact that there will be no grid code set.

Is this the case? Will the inverter cease powering loads on its AC in once AC grid is disconnected? These are almost all the loads ! Is there a way around this if so?

Thanks in advance

James

---

<div class="post-metadata">

**Author:** ![chrigu](https://avatars.discourse-cdn.com/v4/letter/c/ba9def/32.png) [@chrigu](https://community.victronenergy.com/u/chrigu)\
**Post date:** [28 June 2026 19:08 UTC](https://community.victronenergy.com/t/loads-connected-to-ac-in-during-external-anti-islanding-disconnection/59840/2 "2026-06-28T19:08:24Z")

</div>

Gridcode set or not doesnt matter, loads on the ACin are never powered in island condition.

The proper way would be to place the MP in place of the Ziehl relay, since the MP2s are certified to work without an external anti islanding relay.

A workaround could be to use the external tranfer switch firmware.

> **[External Transfer Switch application](https://www.victronenergy.com/media/pg/MultiPlus-II_External_Transfer_Switch_application/en/index-en.html)**

But in any case, you will need additional cables between the point of grid disconnection and the MPs. Question is just if its cables rated for the whole load or just voltage measurment and relay coil

---

<div class="post-metadata">

**Author:** ![gallowayoffgrid](https://avatars.discourse-cdn.com/v4/letter/g/439d5e/32.png) [@gallowayoffgrid](https://community.victronenergy.com/u/gallowayoffgrid)\
**Post date:** [10 July 2026 18:55 UTC](https://community.victronenergy.com/t/loads-connected-to-ac-in-during-external-anti-islanding-disconnection/59840/3 "2026-07-10T18:55:11Z")

</div>

Thanks. Is there any way to set the inverter so that the grid can be connected to the AC out terminals?

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [10 July 2026 19:25 UTC](https://community.victronenergy.com/t/loads-connected-to-ac-in-during-external-anti-islanding-disconnection/59840/4 "2026-07-10T19:25:33Z")

</div>

No. They are not designed for that.

Grid is always connect to ac input.

---

<div class="post-metadata">

**Author:** ![system](https://europe1.discourse-cdn.com/victron/original/1X/21a9a7b5db7c6339715f993568736a7053199995.png) [@system](https://community.victronenergy.com/u/system)\
**Post date:** [24 July 2026 19:25 UTC](https://community.victronenergy.com/t/loads-connected-to-ac-in-during-external-anti-islanding-disconnection/59840/5 "2026-07-24T19:25:55Z")

</div>

Closed on 24 July 2026 19:25 UTC

This topic was automatically closed 14 days after the last reply. New replies are no longer allowed.