Can the Victron EVCS switch back based on voltage?
I have a Renault 5 E-Tech and currently still have a single-phase 16A charging point.
There’s a 4x 2,5mm2 cable with an earth braid, about 30 metres long, running from the meter cupboard to the garage. I joined 2x2 of the cores together, which allowed me to reduce the voltage drop when charging at 1x 16A. From that cable in the garage, there’s another roughly 15 metres of 3x 4mm2 cable running to the charging point.
The Renault 5 is sensitive to undervoltage, and I often see 208v on the HomeWizard kWh meter in the garage in the evening.
I have a three-phase Victron home battery system with a Multiplus 48/5000, Cerbo GX and 27kwh of batteries.
If I buy a Victron EVCS, I could connect it to the 4x 2,5mm2 cable and, for example, charge at 3x 10A, which would let me charge effectively twice as fast with less load on each core. Ideally, I’d run a 5x6mm2 cable to the garage, but that’s quite a lot of work.
There are also times when, because of solar power, the car gets a full 236v, and then I’d actually like to be able to charge at 3x16A.
Can you have the Victron EVCS measure the voltage and set the maximum charging current accordingly, so that it reduces the power if the voltage is at risk of getting too low?
I hope I’ve explained it clearly? I could use AI to clarify it, but I understand that isn’t appreciated.
I have an idea you could try, or look into before buying the EVCS.
According to the EVCS specifications, you can set the fixed charging current via a parameter, with a minimum of 6 A. Or you can have it adjust dynamically according to solar production. But I haven’t seen any function for setting the charging current dynamically based on voltage. However, it does seem possible to control it from Venus OS.
Perhaps someone can confirm the following for you, or check whether anyone has already posted about it: use Node-Red to read the voltage from a meter connected to the EVCS and change the EVCS’s fixed charging current setting accordingly. Repeat the process every few seconds or minutes. As you see the voltage rise, gradually increase the current, then read the voltage again and keep increasing it. If the voltage drops, gradually reduce the current again. Once the voltage is comfortably high, you could even switch to dynamic mode so it can regulate itself according to solar production.
I think it should be feasible and would be a good solution.
Let’s see if someone can confirm whether this idea, or a better one, is possible.
Cheers :waving_hand:
I can answer - we don’t have that functionality. But you can buld it yourself in nodered, should be easy
When charging the home battery at 10 kW, I don’t see a voltage dip on one or more phases. It seems I’m having problems with phase imbalance due to outdated infrastructure between my house and the local substation. I suspect that switching to three-phase charging will greatly reduce the voltage drop, so I’m going to start looking into buying the Victron EVCS. Thanks for your input.
If you might want bidirectional charging in the future, I’d wait for the Victron EVCS v2, which should become available sometime towards the end of this month.
I do indeed have a Renault 5 E-Tech with a 52 kWh battery that can do that. Bidirectional capability could be a big plus. I hope the price is reasonable.
It is more expensive than the current model, and the bidirectional module will be a separate option (so it costs extra too).
yes, it brings a lot of extra functionality (Ethernet, Meter, RCD, relay on each phase NFC etc)