I have an Orion XS with BMV-712 and LiTime 12v 320Ah battery. I noticed the XS was charging at 15.6 volts in bulk mode when set to 50 amp max charging. It’s configured to charge at 14.4v. When I cut back charging current to 25 amps voltage dropped to 14.5v.
At first I thought I might have a problem, then I thought the voltage was increased because of the loss over the cables (probably around 18 - 20 ft one way, factory 6 awg cable).
Am I correct that the voltage is increased to compensate for the los over the cable?
If the BMV and Orion are in Bluetooth Smart Network together, or DVCC is setup on a GX device then the Orion can use the battery voltage from the BMV to compensate for cable losses. Otherwise is should control the Orion output terminals to 14.4V.
Like LX already says; the high voltage output of the XS is not a problem during bulk charging. The XS voltage is NOT the Litime voltage. As long as the voltage of the Litime does not reach that high voltage, there is not a problem. Probably the XS is raising it’s voltage this high to be able to charge with 50A. Best way indeed is to make a network and let the Orion measure the voltage of the battery by the shunt voltage, which tells a lot more about the real battery voltage then the output of the XS.