I am building up my 3-phase MultiRS system and have installed two remote TBS 48V 350A Remote Battery Switches to be able to securely disconnect the DC side in case of smoke or CO alarm or when one of the emergency buttons is pressed.
The two emergency buttons (one in the house, one in the garage near the installation) will each control REMOTE L/H on a MultiRS. The Smoke and CO alarm operate a relay and I can use that signal with AUX_IN configured as a safety switch I assume.
I can control the RBS manually (for a start-up sequence ), or via a control wire (for emergency). In single wire mode, it allows me to operate them via a NO/NC connection and I would like to control their state via the relay in the MultiRS.
The RBS manual states:
- +Vdc continuous on brown wire to close, 0Vdc on brown wire to open.
- Control wire supply current @ 60V < 2.5mA (when active)
- Control wire threshold voltage > 5Vdc
Is it safe to put the battery supply voltage through a 1A fuse and supply the required power via the MultiRS relais? The documentation states it is rated at 1A at 70VDC. That is significantly below the 2.5mA and I don’t expect a massive inrush from a control wire.
But I could be wrong
So would it be safe to operate this way?