Inverter VE Direct 500VA - LED Alarm/Error Sequence

I have a the inverter powering an efficient fridge and a couple of other low power items – LED lighting and TV. When powering these devices the inverter is fine with no alarms and battery voltage is approx 25.75-85V.

I am using the remote switch to turn it off with a NC relay, so when I switch on shore power or a 3000VA inverter to supply higher power devices, the NC contacts are opened.

When using shore power, charge only and 0 amps on the Multiplus remote panel i.e. in the AC transfer mode, the NC relay contacts are open. However, the 500VA keeps starting and then giving a slow flashing red LED with a double pulse green LED. The app shows a low voltage alarm but rather uselessly doesn’t provide the actual voltage.

According to the manual the green signal is off and waiting and the red is low battery. Inverter supply cables are 10mm2 and less than 1m long from main DC panel which is supplied by 70mm2 cables from 25kWh battery. Battery voltage is 25.78. Dynamic cut off is disabled as the battery supplies other loads (warning in the app) and ECO mode is off.

It doesn’t really make sense why the 500VA is continually restarting??
I guess I’ll have to raise a ticket.

Have you measured the actual minimum voltage at the terminals of the 500VA inverter, using a multimeter, under various loads and initial turn on?

Do you have a Bluetooth VE.direct dongle so you can get info from VictronConnect app? Or is it hooked to a GX device?

What’s the total load on the inverter? 500VA isn’t a lot of watts.

And is this a new version of the same problem you shared last year? VE Direct 24/500 Inverter Starts By Itself

Are there leakage currents from filters that could cause a transfer of potential (for example, battery terminals connected to the shield, which happens all too often without any thought)? Or are there galvanic equalising currents somewhere that activate the inverter due to a high static voltage?

What exactly does your setup look like?

Have you measured the actual minimum voltage at the terminals of the 500VA inverter, using a multimeter, under various loads and initial turn on?

No. When this happens there is no load on inverter. I am reading the voltage directly from the Connect App. Voltage on other sensors including BMV 602 are the same.

Do you have a Bluetooth VE.direct dongle so you can get info from VictronConnect app? Or is it hooked to a GX device?

Yes - BT dongle and App

What’s the total load on the inverter? 500VA isn’t a lot of watts.

When the 500VA is in use, the load is 2 domestic fridges. 2 x 45W and the occasional LED T8 lamp tube - 8W.

When I have higher loads, I switch on another AC source - 3000VA inverter, 230V 16A shore power or 230V 48A generator. The V500 remote is then switched off by opening NC relay contacts. Or I can use a switch wired in series in the wheelhouse.

And is this a new version of the same problem you shared last year? VE Direct 24/500 Inverter Starts By Itself

Yes. I am trying to get to the bottom of the issue. It is annoying that it is happening.

Are there leakage currents from filters that could cause a transfer of potential (for example, battery terminals connected to the shield, which happens all too often without any thought)? Or are there galvanic equalising currents somewhere that activate the inverter due to a high static voltage?

I’m not sure what filters I might be using but nothing I know of or galvanic currents. I have an isolation transformer and no GI.

What exactly does your setup look like?

See diagram .

On the V3000VA inverter I have 3 remote NO switches wired in parallel and they all work perfectly.

Can you explain the relay logic? Or show an electrical schematic with details - there is insufficient information.
It looks like there could be overlap of generation from both units - although I may be misinterpreting the wiring.

It takes time for the Multiplus to generate power to activate the relays and thus turn off the Inverter, so they are possibly simultaneously generating power for a brief instance while switching over.

Thanks.

The contactors CN11 and 25 are normally open and only close when their coils are energised. Their NC contacts are open if the contactor is closed.

Normally the V500 is switched on - say 18-20/24 hours/day. So the CN11 coil circuit is energised via the NC contacts on the CN25 contactor and NC contacts in the relay. There is a mechanical interlock between the 2 contactors, so only 1 inverter can physically supply the AC panel.

When the V3000 is switched on, the relay coil is immediately energised. Although V3000 power is also available at the CN25 input terminals, it can’t yet supply the AC panel because of the contactor mechanical interlock. The CN11 coil circuit and the V500 remote switch is opened by the relay NC contacts becoming open. The CN11 contactor then opens, disconnecting power to the AC panel, and closes the NC contacts completing the CN25 coil circuit and the CN25 coil is energised, closing the contactor and supplying V3000 to the AC panel. The change over is pretty instantaneous UPS style, e.g. the TV if switched on doesn’t even flicker. Going the other way, the AC does drop off for a few seconds, which is not an issue.

I accept that both inverters can be supplying power but only one can be connected to the AC panel at any time because of the mechanical interlock. Also wiring the coil circuits using the other contactor’s NC contacts means that any AC from the other inverter should only be residual.

Although with the V500 switching itself on, it means the V500 AC supply is live to the CN11 input. But it can’t go anywhere if CN25 is energised!

All industry standard kit.

Let’s see some photos of the installed components and the setup!

It has to be a V500 inverter issue. With the relay remote contacts open, there is no continuity between the green inverter remote plug terminals. If the plug is removed from the inverter, it doesn’t switch on.
If the plug is inserted, the V500 starts mucking about. It is as if the remote wiring is acting as an aerial. But I can’t believe that Victron wouldn’t have more robust anti interference measures.

I think I’ve just fixed it. Swapped the remote wires around in the green plug. I’m not sure it makes much sense.

This is well strange.

With the V500 remote terminal wired through 2 serial switches - left V500 terminal contact to NC relay contacts to manual switch and back to the right contact - the V500 keeps restarting when the relay contacts are open.

If wired - left V500 terminal contact to manual switch and then NC relay contacts back to the right terminal contact - the V500 behaves as expected and stays shut down when the relay contacts are open.

All the contacts are no volt and there is no low voltage anywhere in the circuits.

It is well strange and the manual should have a note that if the remote switch produces odd results, switch the wires round!!

If the Remote terminal Left (H) input sees a positive voltage (eg battery positive), it will switch on. If you have a short to positive (even just 1 strand of fine wire) or leakage of voltage onto that pin, its likely to come on.

If you disconnect the remote terminal and measure with a DC voltmeter and AC voltmeter, are you seeing any voltage on the wire that normally goes to the left terminal? (e.g. between wire and ground, wire and battery +, wire and battery -, wire and the other terminal wire?) If so, trace it back to the origin.

e.g. check if there is any induced voltage across the remote connector relay contacts of the contactors.

Are these contactors approved by a regulatory authority? e.g. TUV, UL, CSA, ABYC. There’s a lot of counterfeit or poor quality stuff that can be bought online.

Consider tidying up all the wires and putting the contactors in a proper electrical box, as there is less shock hazard.

Thank you.

There is no proper low voltage anywhere. With the electrics in the mode that caused the problems, I’ve measured the voltages both AC and DC from +ve/L to -ve/N and ground. DC is millivolts in the order of 100-200mV from either wire going into the terminal block. No more than the multimeter reads open circuit. AC readings are nonsense - 54V on the lead end into the left hand terminal that caused problems, 80V on the other lead end that doesn’t cause problems - which is on the left hand terminal at the moment and all is fine.

Or the V500 is super sensitive to anything. Which arguably it shouldn’t be.

There certainly isn’t a 12V DC to switch on the V500VA.

The contactors were bought from a UK electrical distributor Control Gear Direct in 2004/5. I attach a pic of the CN25 data label. Look pretty legitimate to me. Even have UL.

I’ll tidy up the wires with a few cable ties once I’m certain that the fiddling is finished with. As for a box - they are in a box - it is called the engine room. I’m sure the “professionals” might throw their hands up in horror. But in my experience, their workmanship isn’t always brilliant anyway. Just yesterday I had a look inside a gremlined central heating oil burner LOA24 control box. There in the snakes wedding of wires was a single choc block connector. I would have expected at least a proper cable crimp joint. And “professional” jobs in my house have been bodged on both gas and electric stuff. As the old adage says “If one wants something done, do it oneself”.

This sounds like you have leakage currents, either a galvanic isolation problem or bad bonding.

Perhaps you can get a second set of eyes on this, eg a licensed marine electrician. Maybe buy them a coffee and have them take a fast look. It would be good to verify the bonding is in place between the chassis of the two inverters and anything else as appropriate.

No friendly nearby marine electrician in rural France!! I’m beginning to learn more about this inverter than I really wish to know.

Everything and anything that has a ground/earth terminal has a generous cable to a single ground point, a 25mm x 6mm x 500mm solid pure copper ground bar firmly bolted to clean steel in a steel hull along with all the DC negatives. The earth bar in the AC circuit breaker box also goes to the ground bar.

3 inverters, AC 12kVA generator and shore isolation transformer ship side have one AC leg bonded to the ground bar to create the neutral.

2 MPPT controllers also have ground bonds as do 2 AC drives. And a charger. The propeller shaft is also bonded.

If anything out of order happens on the AC side, RCDs start tripping. I’ve had tripping as AC machines have started failing e.g. air compressor motor windings.

I’ve just done more measuring, but I don’t have a LoZ.

V500 right hand remote terminal has DC battery voltage on it wrt to DC-ve/ground. So 25.68V at the moment. I don’t recall reading that in the manual, just that voltage on the left hand terminal switches on the inverter. Left hand terminal wrt to DC-ve 4mV.

DC at relay NC contacts 16.4V to DC-ve. Remote cable resistance including through both switches 3.3 ohms. Cable ends to DC-ve infinity ohms.

DC across remote cable ends, disconnected from inverter, 3-4mV. Remote plug terminals to DC-ve 1-200mV, same as the meter reads open circuit.

With the 230V coil relay energised, there are induced voltages in the remote switch cables. The relay terminal next to the coil is at 240mV AC, the furthest terminal is at AC 0V. Across the remote plug terminals is 3-4mV. And each plug terminal to ground is 55V on one and 81V on other. Why that is I don’t know, but Chat GPT Luna tells me induced voltage from the 230V relay coil.

55V + 25.68V battery = 80.68V. So a 55V mystery.

Induced voltage in the contactor/relay contacts is concerning.

These 2 voltages are measured at the remote plug removed from inverter. One side of the circuit is one plug terminal, out through manual closed switch and then to open relay contact. Other side of circuit is other plug terminal to other side of relay contact. NC contacts are open as 230V relay coil is energised.

This isn’t making sense to me. If you are measuring the voltage on the green remote plug not plugged into the inverter, there should be NO voltage at all. ZERO.

When plugged in, and the switches/relay contacts are open, you’ll find a DC voltage across the two pins (less than battery voltage).

I’m out of suggestions at this point.

I’d want to find a safe way to unplug the 500VA AC output to verify it switches on/off properly without LED errors, using the control wiring you have.

That would test if there is any brief instant of backfeed of AC from the 3000VA into the AC output of the 500VA.

Good luck Colin!

Yup, baffling.

But it now works as it should.

I’ll wait for the Victron support to reply to my ticket and see if they have any ideas. But I am not hopeful.

Which DC negative conductors are connected to the PE busbar?

Normally, this is a no-go, as it can cause potentials to be transferred and electrochemical corrosion to occur or even be promoted (because the potential of the components is no longer neutral), depending on the material combination.

It can also cause stray currents to flow through components (cables, Bowden cables) where there should be none. In a case I know of, a vehicle braked by itself because currents flowing through the brake pipes caused the fluid to expand and the moisture it contained to boil, which temporarily led to partial failure of the system.

Properly designed earthing, on the other hand, is essential.

I don’t follow.

All DC negatives eventually go to a single ground point - in my case a substantial copper busbar. Each individual local DC panel around the vessel has a negative busbar with a cable to the main ground busbar. The busbar is connected to the House battery through a BMV shunt.

Together with the AC grounds from equipment and bonded AC legs from AC producing equipment - isolation transformer, inverter and generator - to create the neutral.

Just as described in several marine electrical books I have.