Inverter Stop at Low Voltage pre Alarm in ESS

Hello everyone
I have an customers Installation with Sodium ion (NA+) Batteries. We know for shure we can not take the full capacity of the batteries, because we dont get down to the dicharge volteges needed for that. Thats a fact, and we have to live with that limitation. But as we try to get the maximum out of the system, we have found some limits where i am not 100% shure if these are really limits or just a configuration issue.

System Setup:
3x MP-II 48/3000 (3 Phase)
CerboGX
SmartSolar MPPT 250/70
CarloGavazzi EM 3Phase (RS485)
Fronius Symo 7kw (on AC input)

Battery:
Natbatt NA+ Sodium Ion
Undervoltage/ Discharge Protection 30.0V recovery at 35.2V
CVL 63.0V Overvoltage Protection 63.5V

We got the Batteries Charged up to the 62.5V with AC an DC Solar after that, then Feed back to the Grid. So far is all Fine. (Actual Charge Setting is at 62.5V will be set to 63.00V in future)

During Dischaging we got the VE.Bus Low Voltage warning at around 41.5-42.5V (the Alarm is muted in the cerbo do there not every time get a message/ Alarm Contact and Buzzer off)

at 40.65Vthe system shuts off Feeding from Battery and only taking power from Grid.
Settings are made all to the absolute minimum (36.0V Low voltage Cut OFF and 41.2V Low voltage Pre Alarm and also 41.2V Restart)

Is there any clue where the 40.65V limmiting is coming from? according to datasheets the MP-II should go down to at least 38.0V or 36.0V as Ve.Configure lets me do.

Could this may be an fixed Limit in the ESS Assistant?
As we plan to do more installations in future, we would like to know why thats happening so we can figure out how to deal with it.

Thanks for your Support
Oliver

Could be a hard limit to protect the electronics from malfunctions caused by undervoltage (pulsed switching operations that could cause internal voltage drops, potentially leading to undefined states in the microcontrollers).

What does Victron say about this?

The minimum voltage of the 48V MP II is 38V.

And for stable operation, this value should not even be reached, let alone fall below it.

Try with lithium checked in the settings (I know they aren’t that) but you are basically working with a lead acid profile there as seen by the fact that you had to fix the temperature compensation.

The ess dynamic settings are supposed to override the inverter tab settings.

But of course there is a physical limit to how low it can invert from.

There is no way you can go below this voltage. I’ve been doing this with my Tesla modules for 5 years and have tried everything. It can’t be done. Sorry.