Inverter failed when battery said we had 55%

We were at 65% during the day. Didn’t get any charge from 2 hours in blazing sun. Had 55% when we went to bed and at midnight the inverter shut off for no battery. We have been boondocking for several days and research suggests that if the battery doesn’t get a full charge that the system gets confused. We are in a campground with power now and have plugged in and all systems seem to be operating normally. Any idea what happened? He have a Victrton Inverter 12000 120-50 120v, Solar charger MPPT 100/30

Battery State of Charge percentages are notoriously inaccurate.
The SoC typically gets reset to 100% when the charge is full, then it will be accurate for a while.

Drawing small amounts of current makes the inaccuracy even worse. The battery BMS simply doesn’t have a good way to measure remaining charge properly.

A Victron SmartShunt (300A or 500A) will provide a superior (though not perfect) measurement of remaining charge.

Your standby current draw of around 1 A wasn’t detected by the BMS, which is why the UVP then kicked in.

The only remedy is to synchronise it again by charging and balancing it (frequent partial charging causes the cells to become unbalanced).

Keep an eye on your cell voltages. If they’re getting close to 3 V while your BMS is still showing something like 10–20%, something’s wrong (the LiFe battery is practically empty at that point!).

What brand and model of batteries are you using? Are you using a Victron battery monitor such as a BMV-712 or SmartShunt?

We have 5 Battle Born batteries 100 volt 12 watt batteries. I’m not sure what monitor we have but assume it is a victron branded unit

Please post your settings from your battery monitor. It sounds to me like the battery monitor and/or charging settings aren’t correct.

Your charged voltage setting should be about 14.2V for those batteries and you should be charging them them to 14.4-14.6V. I think you have configuration issues. Go to Battleborn’s website and find their recommended Victron settings and then set your parameters for the battery monitor and all chargers accordingly.

That’s right, the Peukert exponent is set to 1.00, among other things. Victron’s standard is 1.05 for lithium.

What is the charger set to?

Sorry if you aren’t aware, but BattleBorn batteries have serious safety concerns, it is your batteries that are the problem, and sadly they are probably unrecoverable and dangerous to use. See: Will Prowse Battleborn Battery Saga and check the problems from multiple other Battleborn owners: https://diysolarforum.com/threads/battleborn-battery-dragonfly-energy-meltdowns-complaints-and-warranty-denials-post-them-here.125880/#post-1836303

I suggest you immediately disconnect your Battleborns if you have campground AC and look for some replacements ASAP.

Yes yes, Battle Born is probably the issue indeed, check Will Prowse on YT :D:D

Looks like I have some work to do. Thanks so much for the feedback.

Seems my batteries are working perfectly. The issue was a configuration in the victron. That and learning to read the volts and not relying on the percentages. All is well. You guys are great!

Hi Ramona,

Please check your Battleborn batteries and read around / watch some videos about them. They are a fire risk due to their poorly conceived and terrible design.

Battleborn has only ever made multiple parallel cell batteries which are not individually protected by a BMS, which is inappropriate for LFP in this day and age, and not safe in an RV / Home. They use plastic that melts in between the current carrying connections, which loosens those connections due to plastic creep after a year or two, from both heat and cold. They have dissimilar metals in the connections that oxidise after the plastic has melted or creeped (shrunk away loosening the connections) causing arcing and then the terminals overheat. An external visual sign, is the red epoxy around the terminals darkens.

The BMS thermal cutout doesn’t work when they overheat. The multiple parallel cylindrical cells individually sequentially fail, then the remaining cells have to carry more current than they are rated for, causing the internal ‘busbars’ to overheat and melt the plastic ‘sandwich washers’, and the cells overheat, this causes intermittent disconnects, similar to your symptoms where they wouldn’t charge or discharge. The terminals become loose and sometimes wiggling them will cause them to intermittently connect and disconnect.

Many Battleborn batteries have internally melted or caught fire / catastrophically vented. Battleborn looks like they are about to go bankrupt, they will be delisted from Nasdaq imminently for failure to follow the rules. They are trying to hang on by threatening, or actually sueing any youtuber that has pointed out their issues, and there are multiple stories of them not honouring their warranties anymore, There is even a class action lawsuit against them for their failures. Over on DIYsolar forum, amongst the members, they’ve discovered that so far 267 individual batteries have these issues! Some people never realised until they checked them, but the sensible advice is to not mess with them as they are just too unsafe to test properly.

https://diysolarforum.com/threads/battleborn-batteries-dragonfly-energy-is-suing-will-prowse.125758/post-1956141

Sorry to be the bearer of bad news but these batteries are not something anyone should be using.