I am researching and prepping for a DIY project. I have a TNCS electrical supply to the property, UK based.
I want to install Multiplus2 - attached is a block diagram as a first draft to help get my head around it all. (Am new to Victron). Please feel free to mark my homework as im very open to being corrected!
My key unknown/question is this:
in the event of a grid outage, i know the Multiplus will open Line and Neutral on AC-INPUT. It will also bond neutral to the chassis (load side, i think).
If it bonds neutral to chassis/earth, then doesn’t that earth path go back to the installation origin, rejoin neutral at the DNO cutout, and travel through back up all the neutrals, then through the loads, etc…
Thus should/must a changeover always switch be installed, if Multiplus2 is to be grid connected?
Or is my understanding simply lacking on what is actually happening during the grid outage condition.
I suppose a better way of asking my question is, is the Multiplus2 compliant in UK suring power cuts. Sure it has to be, we have something called rhe ENA Type Test Register, and the model does show up on there as approved. Its just I dont know if a chanegeover switch is part of how its supposed to be installed.
Fault condition during power cut is what concerns me, where fault current would actually go. There would still be a path to the DNO’s PEN conductor from the multiplus chassis, up the supply circuit earth, and so on.
Don’t overlook In the UK the regulations stipulate you now MUST have a dedicated earth installed if you were to use islanding mode during a grid outage in TNCS arrangements. This is because in the event the N from which the E is derived is severed, there will be no safe path for earth fault currents. It means having an dedicated earth rod installed for system that operate in island mode.
100% I will install an earth rod, no issues there.
I may be ovwr thinking it / missing something, but if we imagine an earth fault, during power cut condition. Circuit is on AC-OUT-1, solar power coming in, Power Assist working.
Fault current>cpc of circuit>Multiplus>earth rod, but ALSO > multiplus casing > AC supplying circuit cpc > earth bar > DNO cutout > neutral > up the PEN onto the grid network
This is my concern.The fault current in my mind would preferentially take the 0.25 Ohm route up to the DNO cutout, as oppose to the 80 Ohms route down the earth rod.
RCBOs set up on AC-OUT-1 will open anyway, but I am interested to hear what people think.
When islanding, the MP links N and E. A fault from L to E is also a L N fault, so it’ll be a race between MCB or RCD trip. The E fault won’t leave the house.
There’s no 0.25 ohm unless neutral is still connected into the islanded part, which it isn’t as the MP breaks L and N.
IIRC the rod connects directly to the MET via a 10mm cable.