Hi folks,
this is a little out of left field but please bear with me…
I am considering options for an off grid system, for a friend…
We are talking about a 15KVA Quatro, BYD battery I think, I am not entirely sure, but I do know it is a stock implementation, currently with 5 kW of solar, AC coupled on the output, using a Fronius, a generator available on AC In 2 and a small hydro generator on AC In 1.
I am well aware of the 1:1 rule and reasonably confident that I have a handle on AC settings, weak AC, dynamic loading, boost factor… ETC
The issue is the Hydro, it is currently regulated by a governor, linked to a deflector, for speed and an AVR for voltage.
The overall regulation is OK but not great, especially when there is a step change in load. Obviously if it gets too fast or too slow AC In disconnects as it should.
The issue is the methodology… A deflector, by definition, is wasting water all the time, it has to so that it can both add and reduce generator torque, quickly. add to this the fact that the inverter is following the turbine generators voltage and frequency when it is connected and the whole thing starts to look, well; suspect, at best.
One option would be to rectify the turbines output and connect it via a PV inverter but that is a load of smoothing for a single phase generator and brings its own complications’, all be it without any of them being generator frequency.
This may be the best option, but I wanted to explore before committing to something I expect to be harder than I currently expect, to do well at least.
So that brings me to AC coupling…
In short, assuming it is properly synchronised, can I connect a generator to the AC output, exactly as a PV inverter would be, and leave the Quatro to manage the frequency by loading or unloading the generator?
I realise that in this mode the AVR would effectively need to be used to manage power factor, but that is a separate topic. (Save to say it will be required to change the voltage in response to reactive current so that voltage can drive the system I am talking about below.)
Given that the Quatro would be dominating the system, the turbine is only good for about 5.5kW, I would expect the system as a whole to operate like any other grid connected generator…
EXEPT…
I have no idea, and cant find much info about, specifically how the Quatro responds to voltage increase or how fast it can do that.
I would welcome any and all thoughts on the subject…
I have also listed below some of my assumptions and reasoning which may help guide comments without the need to ask further, although I am happy to answer anything.
Thanks for looking,
Al
Why…
Because I believe this would allow the Quatro to hold a stable frequency, forcing the turbine to adapt, or disconnect.
Testing and Caution…
I don’t want to hook this up and find that I missed something fundamental, only when a ball of molten copper and a load of smoke shoots me in the foot.
General…
I am very comfortable with AC connected motors in regeneration and grid connected alternators. I even have experience with C2C configured induction motors on single and split phase grid systems, as generators, some of them quite big.
I know what a synchroscope is and how to use/configure one, but on that note if connecting an alternator, or motor in regen, to AC out is a possibility, I wonder if I couldn’t leverage AC In to do the sync, as it normally would, and then connect AC OUT, to the generator, before disconnecting AC IN, allowing the Quatro to pull the frequency back to its setpoint.
On that thought, is there any way to connect to AC In, with its inherent protection, but then prevent the generator from driving the systems frequency, functioning as if it were an AC coupled energy source on the AC output. The two or physically linked at that point after all, so the differing behaviour has to be soft, right?