Simple question: How do I change the charge voltages of an RS MPPT with a BYD BMS enabled? Or it’s impossible?
I want to change the params to those recommended by Victron here. I am using Victron Connect (see screenshot). It appears the higher values there are set by BYD. I can’t deactivate BYD BMS briefly. I can only restart it. Even if Expert mode is toggled on, I can’t change the values.
I understand that under normal operation, my new values will simply be ignored. I want to set them only as fallback in case of an error.
Currently, the charger is in float mode, so the watt figure makes sense.
A related question just out of curiosity: Why does Victron recommend higher absorption voltage (56.5v) for the MPPT but lower absorption voltage (55.2v) for the quattro charger in the same doc? I would think they should be the same.
Those settings are ignored as they are under external control.
You would typically configure “backup” settings beforehand but once under external control they are irrelevant and overruled.
You would have to disconnect comms and power cycle the charger.
Why does Victron recommend higher absorption voltage (56.5v) for the MPPT but lower absorption voltage (55.2v) for the quattro charger in the same doc?
Ok, you mean the BYD config doc. Looks like an oversight. The voltages match for the off-grid use case. Can’t see why you would set it higher than the inverter charger.