Help with understanding max charging power settings for MP2 + EVCS on ACin

On demand I’d like to charge my MP2 batteries and EVCS/car at the maximum possible power.
The MP2 is 48/10k, the EVCS/car can draw up to 32A on ACin. There is 6.5kWp of AC coupled PV on ACin and 1.6kWp MPPT PV.
There is an ET112 configured as a Grid Meter on the incoming grid tails. The grid is 240V 50Hz in the UK. The grid fuse is 60A.
All domestic loads are on ACout1
In VEconfigure my AC limit is set at 52A which may be equivalent to approx 13kW

I would like the EVCS on ACin to charge constantly at its pre-set manual amps and for the MP2 to charge the house batteries at whatever rate brings the Grid meter power up to the MP2 grid limit (currently at 52A).

I’m finding the system doesn’t perform like this. I’m finding that the EVCS (set to 24A) and MP2 charge rates are constantly hunting and the Grid current is displayed somewhere between 9kW and 11.5kW. The MP2 battery charge current is around 6.5kW and the EVCS about 2kW.

These figures seem about the same during a dull day when the PV was contributing somewhere under 1kW to the mix, and during a more sunny day.

I imagine that the figures will be similar during night time off peak too.

It seems to me that the MP2 may be summing the total current in the Victron devices and keeping that sum below the grid current limit rather than noticing that there are other generators contributing on ACin that are not metered by the ET112.

I’d like to know more about how these charge rates are negotiated by the different system components and how I can steer the priorities given to MP2 charging and EVCS charging.

What would be the effect of me increasing the 52A grid current limit in the MP2 up to or beyond the grid fuse value?

Thanks for reading any any insights.

Hi David,

What you set in the MultiPlus doesn’t necessarily reach the home or car battery. Both batteries have a Battery Management System that tells the Victron system how many amps they want to draw at that moment. There’s no point setting the MultiPlus to more than the household fuse can handle, and it won’t help either — I think your problem lies elsewhere. Cheers, Phil

Thank you Phillip

In the example figures above , both the car and the battery SoCs were low so I can’t see a reason why they wouldn’t draw their maximum.
In the case of the car this would be 32A and in the case of the house batteries, this would be up to the max rate of 7x Pylontech which comfortably exceed the 140A max of the MP2.

I think the total of these is about 14kW which seems achievable with a 60A grid fuse.

I was billed for 22kWh imports in a 2 hour period and this agrees with the VRM grid import display.

Where else do you think I should look?
Many thanks.

Confirm you haven’t set up anything like peak shaving?

Hi David,

If I understand you correctly, you have a single MP2 48/10000? In that case, around 6.5 kW into the house battery is already pretty close to its maximum charging power. At 50–52 V, that works out at about 125–130 A, compared with the maximum of 140 A you mentioned. Depending on the temperature and operating conditions, that difference would be quite understandable.

A low SOC also doesn’t automatically mean full charging power. My Pylontech bank dynamically adjusts the permitted charging current and reports it to the Cerbo. Have a look at what “Charge Current Limit” your BMS is actually allowing at that moment, and whether an additional limit is set in DVCC.

Image: changing CCL controlled by Pylontech bank (8xUS5000)

Your EVCS is connected to AC-in, so its power doesn’t have to go through the MP2. That still doesn’t explain why only around 2 kW is available there when it’s set to 24 A. However, 24 A is just what’s being offered to the car—the vehicle decides how much of it to draw.

Is peak-load limiting or another limit on grid import set anywhere? And what connection capacity does your electricity contract provide? I’ve seen in Spain that the contractually available power was significantly lower than you’d expect from the fuse rating. It would need checking to see whether that plays any part in your connection.

For now, I’d compare the BMS limit and the actual currents of the MP2 and EVCS at the same time. Increasing it to 52 A is unlikely to help much if the limit is imposed somewhere else.

Regards,
Phil

Thank you @lxonline . I can confirm I haven’t set up any peak shaving - just the 52A grid current limit which is either a default or has been carried over from my previous (smaller) MP2.

Thank you @Philip_Collette for this detailed reply.
I’ve arranged some Advanced page widgets for the 2-hour period in question which may confirm what I’m seeing and may answer some of your queries.

Agreed: the MP2 is charging near its advertised maximum of 140A. Happy with that.
We can see that a few minutes before the main charge period there is a little burst of EV charging - I pressed the wrong button and charging started outside of the off-peak period. I mention this because we can see that the car was drawing slightly more that 5kW - which is pretty close to the setting of 24A . Happy with that.

My bad : I do now have an explanation that may explain why the EVCS charge rate is reduced during the 2-hour period and this is that I’ve realised that another uncontrolled load connected to ACin was operating at this time. My HeatPump started a hot water cycle about 30 mins after the MP2 started charging. Here’s a graph of electrical power input to the pump for more-or-less the same time period.

So this explains most of my queries including the reduced EVCS power, but a couple of queries remain.

  • The MP2 looks to be targeting a max grid current of about 46A when I have set it to 52A
  • The Grid current and the EVCS current have quite spiky graphs. Much more spiky than the graph of the HP current. Is this necessary?
  • Is there a technique where we can flip the priority between home battery and car battery charging so that the car charges as a high priority and the house battery takes any remaining headroom?

I think I understand a little more now. Thanks for your explanations about the effect that the BMS could be having. I think I’ll try increasing the max grid current from 52A up to my 60A fuse value and see if that elevates all of the graphs by 8A during the next similar off-peak charge event.

It looks like my settings in the EVCS might be part of my blockage. I have a 50A limit in “input current limit” which I think I should change up to my the Grid current limit of 60A.

If there is no more elegant way to set priority between EVCS and MP2 charge power, I suppose the nuclear option (forcing the EVCS to behave unconstrained at its set charge power) would be to disable GX communication. That would then force the MP2 to do its best to respect the Grid Current Limit, but it is less than ideal to increase the number of unmanaged high-power devices in this way.