How do i configure my system for grid failure backup?

2x Multis, 6x Pylontec US5000, Solar MPPT, heat pump, Venus GX.

---

<div class="post-metadata">

**Author:** ![Netrange](https://avatars.discourse-cdn.com/v4/letter/n/7ab992/32.png) [@Netrange](https://community.victronenergy.com/u/Netrange)\
**Post date:** [27 October 2026 05:05 UTC](https://community.victronenergy.com/t/grid-failure-setup/64429/2 "2026-10-27T05:05:46Z")

</div>

Everything connected to AC Out1 will continue to be supplied automatically. Under normal circumstances, AC Out2 switches off if AC In is unavailable. The heat pump can still be supplied if it’s single-phase and doesn’t need too much power.

We don’t know much about your system yet … but with too little PV, a heat pump doesn’t make much sense. 6 US5000s aren’t too bad, but a heat pump runs for quite a while … and then there are all the other important loads on top.

---

<div class="post-metadata">

**Author:** ![DuivertNL](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/duivertnl/32/279_2.png) [@DuivertNL](https://community.victronenergy.com/u/DuivertNL)\
**Post date:** [27 October 2026 05:13 UTC](https://community.victronenergy.com/t/grid-failure-setup/64429/3 "2026-10-27T05:13:06Z")

</div>

Take a look at this manual:

> **[6292-ESS\_design\_and\_installation\_manual-pdf-en.pdf](https://www.victronenergy.com/upload/documents/Energy_Storage_System/6292-ESS_design_and_installation_manual-pdf-en.pdf)**
>
> 1228.45 KB

---

<div class="post-metadata">

**Author:** ![Fideri](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/fideri/32/2275_2.png) [@Fideri](https://community.victronenergy.com/u/Fideri)\
**Post date:** [27 October 2026 10:59 UTC](https://community.victronenergy.com/t/grid-failure-setup/64429/4 "2026-10-27T10:59:37Z")

</div>

In addition, there are multiple ways to make AC Out 2 behave differently.

---

<div class="post-metadata">

**Author:** ![Richardweir77](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/richardweir77/32/42070_2.png) [@Richardweir77](https://community.victronenergy.com/u/Richardweir77)\
**Post date:** [28 October 2026 17:59 UTC](https://community.victronenergy.com/t/grid-failure-setup/64429/5 "2026-10-28T17:59:30Z")

</div>

How do you know I don’t know very much about my system?

---

<div class="post-metadata">

**Author:** ![Richardweir77](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/richardweir77/32/42070_2.png) [@Richardweir77](https://community.victronenergy.com/u/Richardweir77)\
**Post date:** [28 October 2026 18:00 UTC](https://community.victronenergy.com/t/grid-failure-setup/64429/6 "2026-10-28T18:00:10Z")

</div>

Such as? Please give examples

---

<div class="post-metadata">

**Author:** ![Netrange](https://avatars.discourse-cdn.com/v4/letter/n/7ab992/32.png) [@Netrange](https://community.victronenergy.com/u/Netrange)\
**Post date:** [28 October 2026 18:03 UTC](https://community.victronenergy.com/t/grid-failure-setup/64429/7 "2026-10-28T18:03:35Z")

</div>

😑 that’s the downside of “translation” … the correct meaning can quickly get lost here. “Almost lost in Translation” …

WE all still don’t know much about your system … that has nothing to do with your knowledge …

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [28 October 2026 18:08 UTC](https://community.victronenergy.com/t/grid-failure-setup/64429/8 "2026-10-28T18:08:51Z")

</div>

> [@Richardweir77](#):
>
> 2x Multis, 6x Pylontec US5000, Solar MPPT, heat pump, Venus GX.

Is it installed and programmed?  
Or is that the advice you are wanting?

Whatvis your electrical system? Single phase three phase. Are you backing up only alone phase?  
What size inverters are they?  
Do you have solar panels? What mppt is that?  
How big is the heat pump? Do you want the system to power it specifically or the whole property?

---

<div class="post-metadata">

**Author:** ![Richardweir77](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/richardweir77/32/42070_2.png) [@Richardweir77](https://community.victronenergy.com/u/Richardweir77)\
**Post date:** [28 October 2026 21:51 UTC](https://community.victronenergy.com/t/grid-failure-setup/64429/9 "2026-10-28T21:51:16Z")

</div>

Yes the system is installed all working. It’s single phase, I only need to backup 1 x socket for essential stuff. I have 2 x 5kw inverters (Multis).  
I have 11 solar panels on a MPPT 250/100 charge controller. The heat pump is 14kws and can use up to 40kw per day. The batteries are 28kwh. The system won’t power the HP off grid. If there was a lengthy grid failure I could use the power to run my gas boiler, but this is unlikely. Back up is just for a few cooking essentials.

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [29 October 2026 10:25 UTC](https://community.victronenergy.com/t/grid-failure-setup/64429/10 "2026-10-29T10:25:58Z")

</div>

> [@Richardweir77](#):
>
> system is installed all working

> [@Richardweir77](#):
>
> How do i configure my system for grid failure backup?

It either is or isn’t configured.  
Does it have ESS assistant on the inverters?

---

<div class="post-metadata">

**Author:** ![pcdewolff](https://avatars.discourse-cdn.com/v4/letter/p/4491bb/32.png) [@pcdewolff](https://community.victronenergy.com/u/pcdewolff)\
**Post date:** [29 October 2026 11:25 UTC](https://community.victronenergy.com/t/grid-failure-setup/64429/11 "2026-10-29T11:25:38Z")

</div>

I think the answer is: read the manual about AC-out-1.  
You can then connect your critical devices to that AC-out-1. They will always work, even if the grid goes down. Those critical devices must not exceed the power rating of the RS or the maximum discharge capacity of the US5000. AC-Out-1 does need to be protected by a separate fuse.

I don’t understand Fideri’s comment about AC-out-2. It can’t do anything, since it’s a 1:1 connection to AC-In. No AC-in, no power to AC-out-2.