# Grid current limit setting not enforced

**URL:** <https://community.victronenergy.com/t/grid-current-limit-setting-not-enforced/64764>\
**Category:** DIY\
**Tags:** easyplus, victron\_community, diy\
**Created:** [5 November 2026 16:23 UTC](https://community.victronenergy.com/t/grid-current-limit-setting-not-enforced/64764 "2026-11-05T16:23:16Z")\
**Posts on this page:** 3\
**Page:** 1

<div class="post-metadata">

**Author:** ![dolflombard](https://avatars.discourse-cdn.com/v4/letter/d/87869e/32.png) [@dolflombard](https://community.victronenergy.com/u/dolflombard)\
**Post date:** [5 November 2026 16:23 UTC](https://community.victronenergy.com/t/grid-current-limit-setting-not-enforced/64764/1 "2026-11-05T16:23:17Z")

</div>

I have a 5kva multiplus easy solar with 4kw solar and 10kwh batteries. I have a backup generator connected to it. This is at our original offgrid house and we then added another house with 2 x 5kva Quatros in parralel with 8kwh battery without its own solar.

The house with solarpanels provide a grid connection to the second house.

I set the grid current limit on the second house to 6 amp and the batteries are charged at that rate. When a load is drawn on the quatros it exceeds the 6 amps and will go as high as is drawn to the point where the easysolar trips.

I had the quatros at my house in town on grid and it never exceeded the grid connection. It suplemented the grid with battery or solar but never ecceeded the grid. The only difference was that I had a gridmeter installed. The power assist function doesn’t make difference.

I tried different settings but it doesn’t make a difference. I want it to work when it was connected to a grid, just use up to the limit supplied and supply the difference from battery.

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [5 November 2026 19:41 UTC](https://community.victronenergy.com/t/grid-current-limit-setting-not-enforced/64764/2 "2026-11-05T19:41:36Z")

</div>

> [@dolflombard](#):
>
> exceeds the 6 amps

You can’t set them this low (are you using ess?). And it is certainly trickier with the parallel as well now.

---

<div class="post-metadata">

**Author:** ![Fideri](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/fideri/32/2275_2.png) [@Fideri](https://community.victronenergy.com/u/Fideri)\
**Post date:** [6 November 2026 06:29 UTC](https://community.victronenergy.com/t/grid-current-limit-setting-not-enforced/64764/3 "2026-11-06T06:29:16Z")

</div>

@lxonline is exactly right. I had a low current limit on my quattro and it was ignored. I raised it and it started working.