Hi,
I need assistance, my system is not accepting the generator fully and when it does the batteries don’t seem to be charging at full rate. my system consists of :
2x Victron multipluss 2 48v 500 / 70-50 running in Parelle
colour controll gx running Venus os 3.85
8 x rolls 6cs 21p 6v flooded lead acid batteries in 48 v 683 ah bank
and my generator is an excel power xl-dk-11s diesel generator rated to 10kva single phase.
The main issue is getting the generator to connect to the ac power in 1 I have been able to get the system to accept the power but I have had to change the charge setting right down to 5a before it will allow the connection then once its connected I can restore it back up to the desired charging status and it remains connected.
when it is running its at ac input: 233v
frequency: 50.4-50.6hz
ac input current: 6.8a
ac input power displayed at: 827w
and battery voltage at 50.1v
battery charging current: 14a
and charge status: bulk
I have checked many settings and currently its set to
DVCC enabled with max charge set at 30a
multipluss ac input set to 20A
both units appear in the gx, the master shows steady led on charger main in and then bulk and the slave is flashing mains on and inverter on as it should.
the ve config files show that i have set the multi plus to the same parameters i am now just confused.
DO i need to edit some settings or am i just missing something perhaps a ramped startup of the generator? i have attached a few pics to show the issue and system a bit better. Apologies for log message
HQ1920MRH3W.TXT (1.7 KB)
HQ1920A6XHQ.TXT (1.7 KB)