Generator when connected causes a L1 overload alarm

Hi,

I need assistance, my system is not accepting the generator fully and when it does the batteries don’t seem to be charging at full rate. my system consists of :

2x Victron multipluss 2 48v 500 / 70-50 running in Parelle

colour controll gx running Venus os 3.85

8 x rolls 6cs 21p 6v flooded lead acid batteries in 48 v 683 ah bank

and my generator is an excel power xl-dk-11s diesel generator rated to 10kva single phase.

The main issue is getting the generator to connect to the ac power in 1 I have been able to get the system to accept the power but I have had to change the charge setting right down to 5a before it will allow the connection then once its connected I can restore it back up to the desired charging status and it remains connected.

when it is running its at ac input: 233v

frequency: 50.4-50.6hz

ac input current: 6.8a

ac input power displayed at: 827w

and battery voltage at 50.1v

battery charging current: 14a

and charge status: bulk

I have checked many settings and currently its set to

DVCC enabled with max charge set at 30a

multipluss ac input set to 20A

both units appear in the gx, the master shows steady led on charger main in and then bulk and the slave is flashing mains on and inverter on as it should.

the ve config files show that i have set the multi plus to the same parameters i am now just confused.

DO i need to edit some settings or am i just missing something perhaps a ramped startup of the generator? i have attached a few pics to show the issue and system a bit better. Apologies for log message

HQ1920MRH3W.TXT (1.7 KB)

HQ1920A6XHQ.TXT (1.7 KB)

Just a side note, the CCGX support stopped at 3.55 as it lacked resources to reliably run the new versions.
3.56 has just been released to address the PHP security issues.
There was way too many unexplained issues that seemed to happen when a CCGX went past the recommended and support limit, not necessarily related to this, but something you should be aware of as there no testing that goes on with the model any longer.

Thankyou, i knew this and i have updated it via usb to the lastes firmware, but i dont think the ccgx is the casue for this issue as you mentioned in your reply.

@timbaber

I could not charge my LFP battery with my MP2 as the resistance a battery connection high leading to 2V drop of voltage from MP2 to battery terminal.

Check voltage an MP2 terminals and battery bank. If they diff a lot, maybe add a “V-sense” connection.
Consider checking terminals and wiring with a thermal camera.
Consider adding a “bat temp” sensor.
Double check “charger” settings in VeConfigure to match your battery.

Is the lead acid battery maintained? E.g. filled and acid measured?

Hope this helps to get a step closer to a solution…