Generator goes haywire with MULTIPLUS

Hello

I have two MultiPlus 5000/48/70 units running in parallel with a Cerbo and a 7 kVA generator. I get power peaks of just over 10 kW when motors start, and a running load of around 5 kW. When the generator starts, most of the time it goes crazy and revs up to full speed. I have limited the current either in VEConfigure or on the GX screen itself, but either I have to stop the generator or it eventually trips due to overload. We also have two identical generators, one as a backup, and the same thing happens with both. They are the same make and model. Can anyone tell me whether the problem is with the generators or with Victron? If I connect the generators directly to the installation, they work perfectly.

Your generators are undersized for the inverters.

What is your input current limit set to for the system? It would have to be much less than 19A total.

Have you followed the suggestions here.

What does your setup look like?

Is Weak AC enabled?