ESS MultiPlus no longer does zero feed-in!?
Good afternoon,
For years, I’ve been running a MultiPlus II 3000 as an ESS system with 2 MPPT controllers and a 10 kW battery. It worked brilliantly and without any problems as a zero-feed-in system until 31 October.
With these settings, it should start supporting the grid again above 73%, at a maximum of 1,500 W. But it no longer does.
All the devices are running the latest firmware, and the Ekrano is also running version 3.85.
The behaviour is exactly the same even when I run the device without Node-RED support.
If I now manually set the grid setpoint to, for example, -300 W, it regulates to that value. I’ve already powered down the Victron Smart Meter, rebooted all the devices and disconnected them from the power, but the fault keeps recurring. There’s no error message, either. Downgrading to version 3.81 hasn’t changed this behaviour. I’m a bit at a loss and would be grateful for any ideas.
hello,
what’s configured as the grid measurement? the smart meter or the Multi?
if it’s regulating the grid setpoint at the Multi, it’ll probably be the Multi!
cheers
Thanks, but yes, everything is set up that way. SmartMeter dictates it.