# Integrating Fronius Symo

**URL:** <https://community.victronenergy.com/t/forius-symo-einbinden/63958>\
**Category:** DIY\
**Tags:** pv-inverter, fronius\_symo, beginner, multiplus-ii\
**Created:** [15 October 2026 05:33 UTC](https://community.victronenergy.com/t/forius-symo-einbinden/63958 "2026-10-15T05:33:18Z")\
**Posts on this page:** 6\
**Page:** 1

<div class="post-metadata">

**Author:** ![T.M](https://avatars.discourse-cdn.com/v4/letter/t/ad7895/32.png) [@T.M](https://community.victronenergy.com/u/T.M)\
**Post date:** [15 October 2026 05:33 UTC](https://community.victronenergy.com/t/forius-symo-einbinden/63958/1 "2026-10-15T05:33:18Z")

</div>

Hello everyone, I have a question about connecting a Fronius Symo.

This is how my system is currently set up.

[Seite 2 Anlage.pdf](https://community.victronenergy.com/uploads/short-url/xrf9A7eT7qQBtsCSV0nFJvZ3m9i.pdf) (48.7 KB)

The inverter is supposed to be connected to the ACout.

Where exactly should the Symo go: before the RCD and changeover switch, or after the changeover switch? What difference would it make? I’ve marked the two possible locations on the diagram.

Best wishes

---

<div class="post-metadata">

**Author:** ![Radunre](https://avatars.discourse-cdn.com/v4/letter/r/cdc98d/32.png) [@Radunre](https://community.victronenergy.com/u/Radunre)\
**Post date:** [15 October 2026 06:37 UTC](https://community.victronenergy.com/t/forius-symo-einbinden/63958/2 "2026-10-15T06:37:18Z")

</div>

Your Fronius should have it’s own MCB/RCBO and placed **after** Eaton changeover, on the consumers side. This way, if Victron part need maintenance, the Fronius will still produce energy.

---

<div class="post-metadata">

**Author:** ![BjoernK](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/bjoernk/32/89_2.png) [@BjoernK](https://community.victronenergy.com/u/BjoernK)\
**Post date:** [15 October 2026 20:32 UTC](https://community.victronenergy.com/t/forius-symo-einbinden/63958/3 "2026-10-15T20:32:52Z")

</div>

I’d install the MP2’s RCD between the changeover switch and the house.  
I’d also fit an MCB on at least AC\_in, and preferably on AC\_out as well.  
This protects the cables and lets you de-energise the MP2 for maintenance.

 ![IMG_1187](https://europe1.discourse-cdn.com/victron/original/3X/6/4/6469a7abc03d03308299bc7e32feb38df54b0eed.jpeg)

---

<div class="post-metadata">

**Author:** ![T.M](https://avatars.discourse-cdn.com/v4/letter/t/ad7895/32.png) [@T.M](https://community.victronenergy.com/u/T.M)\
**Post date:** [16 October 2026 04:42 UTC](https://community.victronenergy.com/t/forius-symo-einbinden/63958/4 "2026-10-16T04:42:51Z")

</div>

You mean the RCD for the Fronius? That was my plan too: changeover switch–RCBO–basement consumer unit

Could a 30 mA RCD trip unnecessarily because of leakage currents, for example from its mains filters? I would have gone for a 100 mA one.

 ![20261016_064209](https://europe1.discourse-cdn.com/victron/original/3X/d/f/dfdd85035177df15deb38aa2fce0c8ef14aa4b77.jpeg)

---

<div class="post-metadata">

**Author:** ![BjoernK](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/bjoernk/32/89_2.png) [@BjoernK](https://community.victronenergy.com/u/BjoernK)\
**Post date:** [16 October 2026 15:08 UTC](https://community.victronenergy.com/t/forius-symo-einbinden/63958/5 "2026-10-16T15:08:37Z")

</div>

Ob für den Fronius eventuell ein 100-mA-RCD erforderlich oder sinnvoll ist, weiß ich nicht.

Ich habe für jeden Verbraucherstromkreis einen eigenen FI/LS-Schalter mit 30 mA.

Wenn man vor einem Erzeuger einen zusätzlichen RCD installiert, muss dieser natürlich größere Ableitströme tolerieren, also 100 oder 300 mA.  
Gegebenenfalls muss man auch prüfen, ob er allstromsensitiv sein muss.

Vor meinen Mikrowechselrichtern (insgesamt 7600 W) habe ich keinen RCD, sondern nur Leitungsschutzschalter und Überspannungsschutz.

Meine Konfiguration sieht also so aus:  
Netz - SLS - LS - MP2 - LS - Umschalter - FI/LS - Verbraucher  
Meine AC-PV-Anlage hängt ebenfalls hinter dem Umschalter parallel zu den FI/LS-Schaltern, jedoch nur mit Leitungsschutzschalter und Überspannungsschutz.

Die Leitungsschutzschalter an AC\_in und AC\_out der MP2 dienen in erster Linie dem Leitungsschutz (8 m 10-mm²-Kabel) und in zweiter Linie dazu, die Anlage für Wartungsarbeiten stromlos zu schalten.

Ich habe dir auch noch ein Bild meiner Verteilung angehängt. Links unten sind die Leitungsschutzschalter für AC\_in, AC\_out1 und AC\_out2. Entsprechend habe ich auch die gesamte Verteilung getrennt für AC\_out1 (links) und AC\_out2 (Mitte) aufgebaut.  
AC\_out2 wird je nach SOC durch den Relay Assistant abgeschaltet.

 ![Image](https://europe1.discourse-cdn.com/victron/original/2X/0/060886018e3e9e91c6464824885d4d2f4c180416.jpeg)

---

<div class="post-metadata">

**Author:** ![T.M](https://avatars.discourse-cdn.com/v4/letter/t/ad7895/32.png) [@T.M](https://community.victronenergy.com/u/T.M)\
**Post date:** [17 October 2026 04:54 UTC](https://community.victronenergy.com/t/forius-symo-einbinden/63958/6 "2026-10-17T04:54:20Z")

</div>

The distribution board is a dream. When we bought our house, a brand-new meter cabinet had been installed, but it was far too small. So I put everything in a Rital metal cabinet.