Flash usage during update ESS setpoint every 10 seconds in Multi RS Solar

Hello,
I am using the external control mode in the Multi RS Solar to set the setpoint in order to charge or discharge based on my power usage.

I was wondering if these 10 second interval can destroy the internal flash of the device or are thse settings kept in RAM

If the dbus-obj-path starts with /Settings/… (aka all com.victronenergy.settings keys), then is stored in flash. Otherwise no.

Maybe is a good idea to tell us which setpoint you want to set… There are a quite a few of them… :slight_smile:

Sorry for my late response.
It is the ESS setpoint of the multi rs at offset 4922 (modbus com.victronenergy.acsystem)

It’s not a flash variable. So no worry.

Thanks for the info