I recently updated my firmware:  
Cerbo GX: v3.66  
Quattro 48/8000/110-2x100 rev2: v588  
SmartSolar MPPT RS 450/100: v1.26  
ESS active.

I have noticed some changes.

Normally the SOC is between 75 and 80% by 07:30. It is now 100%.

There is no power from the PV Charger.

I normally change the inverter mode to inverter only and hence stop the power coming in from the grid.

The PV Charger then starts bringing in power.

I have just (07:40) switched the mode to On and the PV Charger does not bring in power. 100 - 120W coming from the grid.

What has changed, and why?

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/6/2/62507ac71342c5b83f309d00eb99178e77a7903d.png)

Mode: On

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/0/9/096bed6f2755b85adfcd88cebb438ee40b746331.png)

Mode: Inverter only.

---

<div class="post-metadata">

**Author:** ![mac](https://avatars.discourse-cdn.com/v4/letter/m/cc9497/32.png) [@mac](https://community.victronenergy.com/u/mac)\
**Post date:** [30 September 2025 06:46 UTC](https://community.victronenergy.com/t/firmware-updates-to-quattro-what-was-changed/46226/2 "2025-09-30T06:46:12Z")

</div>

After a firmware update on a quattro it is reset to factory defaults, [see manual](https://www.victronenergy.com/media/pg/VictronConnect_configuration_guide_for_VE.Bus_products/en/firmware-updates.html#UUID-ffb3824e-89bc-2ffa-b183-d04c22757bad). This means you have to restore from a backup or go through the setup process again.

---

<div class="post-metadata">

**Author:** ![STosen](https://avatars.discourse-cdn.com/v4/letter/s/e95f7d/32.png) [@STosen](https://community.victronenergy.com/u/STosen)\
**Post date:** [30 September 2025 07:11 UTC](https://community.victronenergy.com/t/firmware-updates-to-quattro-what-was-changed/46226/3 "2025-09-30T07:11:09Z")

</div>

Thank you kindly. I will look into this.

---

<div class="post-metadata">

**Author:** ![STosen](https://avatars.discourse-cdn.com/v4/letter/s/e95f7d/32.png) [@STosen](https://community.victronenergy.com/u/STosen)\
**Post date:** [30 September 2025 08:40 UTC](https://community.victronenergy.com/t/firmware-updates-to-quattro-what-was-changed/46226/4 "2025-09-30T08:40:39Z")

</div>

Quite correct, I see that the last version (RVCS file) of the settings is not compatible with the firmaware and will have to go through the setup again using VE Config 3 and then download the RVSC file as a backup.

---

<div class="post-metadata">

**Author:** ![STosen](https://avatars.discourse-cdn.com/v4/letter/s/e95f7d/32.png) [@STosen](https://community.victronenergy.com/u/STosen)\
**Post date:** [30 September 2025 11:45 UTC](https://community.victronenergy.com/t/firmware-updates-to-quattro-what-was-changed/46226/5 "2025-09-30T11:45:41Z")

</div>

Managed to get that sorted out.

The problem was when I tried upload the last VE Config file an error message came up indicating that is was not compatible with the firmware - a direct link between the firmware and the VE Config file.

This meant I would have to download the default VE Config file on the VRM Portal and apply the settings from the last VE Config file.

I opened both files and ensured I appled the settings from the old file and then uploaded.

It is looking good so far with a little (30 - 100W) power being fed in from the grid.

I will need to check tomorrow morning to see if ESS #1 and 2 display when the SOC is below 100%.

I have not inculded the firmware version in the configuration filename.

@Mac, once again, a hearty thanks for your information.

---

<div class="post-metadata">

**Author:** ![STosen](https://avatars.discourse-cdn.com/v4/letter/s/e95f7d/32.png) [@STosen](https://community.victronenergy.com/u/STosen)\
**Post date:** [1 October 2025 05:43 UTC](https://community.victronenergy.com/t/firmware-updates-to-quattro-what-was-changed/46226/6 "2025-10-01T05:43:27Z")

</div>

This morning the inverter is “behaving” as expected.