Feature request: Dynamic per-phase allocation of ESS/DESS grid charging

Hi,

I have a 3-phase ESS/DESS system with 3 x MultiPlus-II 48/5000, MPPT 450/200, Cerbo GX and VM-3P75CT ( and 135 kWh in batt. ).

I am wondering if DESS can make better use of the available current on each individual phase when charging the battery from the grid.

As a simple example, my grid connection is 3 x 20A. Assume the house is currently using:

L1: 8A
L2: 5A
L3: 18A

This leaves 12A available on L1, 15A on L2, but only 2A on L3.

If DESS wants to charge the battery with around 6kW, is there any way for the three MultiPlus units to use more charging power on L1 and L2 and less on L3 ?

In other words, I would like the system to dynamically use the available headroom on each phase, while never exceeding 20A on any individual phase.

There is enough total capacity in the example above ( 12 + 15 + 2 = 29A ), but it is very unevenly distributed between the phases.

I know about the ESS “Total of all phases” and “Individual phase” settings, but I am not sure if either of them can actually do what I describe above when DESS is charging from the grid.

I also found the earlier discussion about the 3-phase grid current limit issue. As I understand it, that is not quite the same question. I am specifically interested in using the different available current on each phase for battery charging.

Is this already possible with ESS/DESS?

If not, I think it would be a useful feature, similar to dynamic load balancing on a 3-phase EV charger.

/BR

Erling Anderberg

This is exactly how it currently works. It respects the maximum allowed current on each phase and will pull up to that current when charging.

Here I had a constant 2kW load on L2, and there was battery charging scheduled at 7:00. Current on all phases increased to 20A (4.6kW) and the batteries got 2kW less power than they could have due to that load. Actually, due to charger losses, they got about 3kW less than the theoretical 13.8kW.

Then at 7:15 less charging power was scheduled so there was still equal power being pulled from all 3 phases even though there was still a 2kW load on L2

Thanks, this is very useful and I think your graphs actually show the difference I am asking about.

I agree that the system respects the 20A limit on each phase.

But in your example, when you have a 2kW load on L2, the grid power still goes to about the same 4.6kW on L1, L2 and L3. This means the 2kW load on L2 reduces the power available for battery charging, instead of the chargers using more of the available capacity on L1 and L3.

That is the part I would like to improve.

For example, if the loads are 8A / 5A / 18A with a 3x20A connection, there is 12A / 15A / 2A headroom left. I would like DESS to be able to use more of the 12A and 15A available on L1/L2 and very little on L3, while still keeping every phase below 20A.

So I think the current system provides per-phase current limiting, but not dynamic redistribution of the requested battery charging power between the phases.

Or am I misunderstanding how it works ?

/Erling

I can see.

As of now, this is not under DESS control. DESS only sees the inverters as one logical unit and tells them to charge 12.000 W for example.

So, each unit would logically charge with 4.000W. But If the inverter on L1 for example could only pull 2000W before hitting the AC-Current limit for that phase, the total charge rate would only be 10.000, the 2.000W are lost. This is, because the “hard limit” to the ac current is happening per-phase inside the inverters signle-unit-control itself. It is not telling other inverters about this, so they would not know that they have to compensate something.

You could check, if switching the Phase-Mode in the ESS Settings (Individual vs Total of all phases) would make a difference on that behaviour. If so, a simple node red changing that mode during dess-charging could eventually already achieve what you want.

Thanks, that sounds worth testing.

Before I change anything, has anyone actually tried using “Individual phase” during DESS grid charging for this purpose ?

In particular, does it allow the other phases to take more charging power when one phase reaches its AC current limit, so that the total DESS requested charging power can still be reached ?

If someone has tested this with a 3-phase MultiPlus system, I would be very interested to know the result.

/Erling

I do use individual phase regulation. This still has a similar issue.

If I set ESS at +3200W, and the loads are L1-0, L2-0, L3-800W, then it will charge at 2400/3=800W on each of the phases. So L1 will input 800W, L2 will input 800W, L3 will input 1600W, and each inverter will charge with the same current.

But as soon as a current limit steps in, this unnecessarily limits charge power.

If I set ESS at +10000W, and the loads are L1-0, L2-0, L3-800W, then it will try to charge at 9200/3=3067W on each of the phases. So L1 will input 3067W, L2 will input 3067W, L3 will try to input 3867W, hit an input current limit, and will not increase the input on L1 and L2.

There is a simple way around this, provided that the current limit is the only limit that matters.

Set the setpoint at +30000W. All phases will simply hit the current limit. This only works if you want the maximum charge rate possible, and if your grid operator limits the input current, not the input power. E.g. in my case, if I were to charge this way during the day, when grid voltage is high, I would slighly exceed my 11.1kW input limit.

Thanks, that is exactly the test I was looking for.

So Individual phase does not solve it either. The charging power is still divided equally between the three inverters, and when one phase reaches its AC current limit, the unused part is not redistributed to the other phases.

Your +30kW workaround is also interesting, because it shows that the individual AC current limits can effectively use the available headroom on each phase when maximum charging is wanted.

But as you say, that does not solve the general case where DESS wants a specific total charge power, for example 6kW, and that 6kW should be distributed according to the available headroom on each phase.

That is exactly the function I was looking for.

/Erling