# Should a Lynx Power In busbar be connected to the house's earth (PE)?

**URL:** <https://community.victronenergy.com/t/faut-il-relier-un-busbar-lynx-power-in-a-la-terre-pe-de-la-maison/63593>\
**Category:** DIY\
**Tags:** busbar, beginner, cerbo-gx\
**Created:** [6 October 2026 08:50 UTC](https://community.victronenergy.com/t/faut-il-relier-un-busbar-lynx-power-in-a-la-terre-pe-de-la-maison/63593 "2026-10-06T08:50:08Z")\
**Posts on this page:** 7\
**Page:** 1

<div class="post-metadata">

**Author:** ![Monial](https://avatars.discourse-cdn.com/v4/letter/m/71e660/32.png) [@Monial](https://community.victronenergy.com/u/Monial)\
**Post date:** [6 October 2026 08:50 UTC](https://community.victronenergy.com/t/faut-il-relier-un-busbar-lynx-power-in-a-la-terre-pe-de-la-maison/63593/1 "2026-10-06T08:50:08Z")

</div>

**System architecture** : Single-phase 220V 50hz installation, communication between equipment = VE.CAN and LAN network, MultiRS 48V\_600Va MPPT 450\_100 (firmware V1.31), Cerbo GX MK2 + GX Touch 50 (firmware V3.80), VM-3P75CT energy meter (firmware V1.11), Renon Ebricks batteries (2 x 5,12Kwh), Trinasolar PV modules TSM-455NEGR9R.28 (10 x 455Wc), Victron Lynx Power-in busbar, Siemens 3NP1133-1CA10 battery isolator

Question: Should a Lynx Power in busbar be connected to the house’s earth (PE)?

Hello,

My two Renon E-Brick batteries are connected to the MultiRS 48/6000 as follows: Batteries → Lynx Power in → Siemens DC isolator → MulriRS 48/6000

The Victron documentation states: _Connect the earth wire → This only applies if the system requires an earth connection. There should be only one earth connection per system. The earth connection must be made after the Lynx Smart BMS, the Lynx Shunt VE.Can or the battery monitor shunt. For more information about system earthing, see the Wiring Unlimited book._

I have no idea whether my system needs the Lynx to be connected to earth (in fact, the negative terminal, as the earth connection point is on the negative busbar). The Wiring Unlimited documentation is very well written, but it doesn’t help me decide.

For information: the chassis of all the equipment in the installation is connected to the house’s earth.

If anyone can shed some light on whether or not I should connect the Lynx Power In to the house’s earth, I’d appreciate it. If you can also provide a simple explanation of why, that would help me understand a little better what I’m doing.

Thanks in advance

---

<div class="post-metadata">

**Author:** ![Radunre](https://avatars.discourse-cdn.com/v4/letter/r/cdc98d/32.png) [@Radunre](https://community.victronenergy.com/u/Radunre)\
**Post date:** [6 October 2026 09:03 UTC](https://community.victronenergy.com/t/faut-il-relier-un-busbar-lynx-power-in-a-la-terre-pe-de-la-maison/63593/2 "2026-10-06T09:03:08Z")

</div>

In a fixed installation, DC side does not have to be earthed.

Mandatory earth connection is for inverter, PV modules **frame** , battery **case** and MPPT’s as shown [here](https://www.victronenergy.com/upload/documents/Manual-and-Drawing-MultiPlus-II-15kVA-3Phase-MPPT-250-100-Lynx-Power-In-Distributors-Cerbo-GX-Touch-GX-LTE-4G-BYD-Flex-Lite.pdfruc).

---

<div class="post-metadata">

**Author:** ![Monial](https://avatars.discourse-cdn.com/v4/letter/m/71e660/32.png) [@Monial](https://community.victronenergy.com/u/Monial)\
**Post date:** [6 October 2026 09:13 UTC](https://community.victronenergy.com/t/faut-il-relier-un-busbar-lynx-power-in-a-la-terre-pe-de-la-maison/63593/3 "2026-10-06T09:13:20Z")

</div>

Hello **[Radunre](https://community.victronenergy.com/u/radunre),**

Thank you for the quick reply.

You seem to have experience, and although I don’t understand all the implications, I’ll take your advice and not connect the Lynx Power In (= the negative busbar) to earth.

If anyone else has the patience to explain the “why and how” or point me towards a suitable tutorial, this novice would be grateful.

Have a good day, everyone.

Kind regards

---

<div class="post-metadata">

**Author:** ![Radunre](https://avatars.discourse-cdn.com/v4/letter/r/cdc98d/32.png) [@Radunre](https://community.victronenergy.com/u/Radunre)\
**Post date:** [6 October 2026 09:22 UTC](https://community.victronenergy.com/t/faut-il-relier-un-busbar-lynx-power-in-a-la-terre-pe-de-la-maison/63593/4 "2026-10-06T09:22:45Z")

</div>

A lot of information is also available from Victron, please have a look [here](https://www.victronenergy.com/media/pg/The_Wiring_Unlimited_book/en/ground,-earth-and-electrical-safety.html#UUID-fabf5ed2-dc13-b8ea-4a66-c51f78776887).

---

<div class="post-metadata">

**Author:** ![Karl-Heinz](https://avatars.discourse-cdn.com/v4/letter/k/ad7895/32.png) [@Karl-Heinz](https://community.victronenergy.com/u/Karl-Heinz)\
**Post date:** [6 October 2026 12:21 UTC](https://community.victronenergy.com/t/faut-il-relier-un-busbar-lynx-power-in-a-la-terre-pe-de-la-maison/63593/5 "2026-10-06T12:21:25Z")

</div>

There is protective earth, functional earth and equipotential bonding. On board a boat, there is also radio earth.

Three different types, some of which use the same wire colour (gl/gn or YL/GN).

In fixed PV installations, there is a type of earth connection from the generator array to the inverter that is not marked green/yellow and is used for insulation monitoring.

The subject is complex, so it was a good idea to ask here. If in doubt, and for safety-related measurements, contact your electrician.

---

<div class="post-metadata">

**Author:** ![Monial](https://avatars.discourse-cdn.com/v4/letter/m/71e660/32.png) [@Monial](https://community.victronenergy.com/u/Monial)\
**Post date:** [21 October 2026 07:44 UTC](https://community.victronenergy.com/t/faut-il-relier-un-busbar-lynx-power-in-a-la-terre-pe-de-la-maison/63593/6 "2026-10-21T07:44:14Z")

</div>

Bonjour tout le monde,

Vous trouverez ci-après les questions posées à Renon concernant la mise à la terre (PE) des batteries ainsi que leurs réponses :

**Questions :**

Hello Renon Support,

I have two Renon EBrick batteries (Model R-EB005161 – 51,2V 100 Ah- BMS 5.218 EMS 3.010) connected to a Victron Multi RS Solar 48/6000 and a Cerbo GX MK2.

The metal enclosures of both batteries are connected to the same protective earth (PE) as the Multi RS chassis, the PV module frames and the AC distribution board.

Neither the positive nor the negative DC battery terminal is intentionally connected to PE. The PV positive and negative conductors are also isolated from earth.

Could you please clarify the following points regarding the EBrick batteries and their integrated BMS?

1. Does the battery or its BMS include DC insulation monitoring, i.e. monitoring the insulation resistance between the positive/negative battery terminals and the metal enclosure or PE?
2. Does the BMS detect an insulation fault or an accidental connection between either DC pole and the protective earth?
3. If the positive or negative DC conductor accidentally contacts a grounded metal enclosure, what protection or fault detection is provided by the battery and its BMS?
4. Does Renon require or recommend any specific connection between the battery positive or negative terminal and PE, or should both DC poles remain isolated from earth?
5. Is there a technical document describing the battery’s insulation monitoring, grounding requirements and earth-fault protection?

I would appreciate answers based on the specifications of my EBrick battery model.

Thanks in advance.

Best regards

**Answers:**

Hello,

Here is the response regarding EBrick batteries—DC insulation monitoring and earth-fault protection:

1. EBrick batteries do not have built-in insulation monitoring functionality; this function is typically handled by the inverter, which requires a common ground connection between the inverter and the battery.

2. Both the positive and negative terminals of the battery must remain isolated from the earth.

3. Requirements regarding battery grounding are covered in the battery user manual; since this specific battery model lacks insulation monitoring capabilities, there are no technical documents available for that specific function.

Best regards.

---

<div class="post-metadata">

**Author:** ![system](https://europe1.discourse-cdn.com/victron/original/1X/21a9a7b5db7c6339715f993568736a7053199995.png) [@system](https://community.victronenergy.com/u/system)\
**Post date:** [4 November 2026 07:45 UTC](https://community.victronenergy.com/t/faut-il-relier-un-busbar-lynx-power-in-a-la-terre-pe-de-la-maison/63593/7 "2026-11-04T07:45:00Z")

</div>

Closed on 4 November 2026 07:45 UTC

This topic was automatically closed 14 days after the last reply. New replies are no longer allowed.