Evcs/car stops charging

Hi all,

I have an issue i don’t know how to tackle.

The setup: 3 phase mp2 system, 80 kwh pylontech, cerbo, evcs (on mp2 out), etc… (all have the latest firmware)

The battery system works flawless, no problems there. Had a tesla model s for 11 years, never had an issue charging. So far so good.

It was time to upgrade the car, and bought the bmw ix3. Fantastic car, but when charging at home i run into the issue most of the time at random intervals the charging stops. The evcs gives no faults, the car charging screen turns red and i need to unplug and plug back in. The bmw dealership did run a diagnostic on the car, and charged it, all went well. I charged the car for an hour at a public charger, all went fine also. So at this point i’m kinda stuck. My first thought was as the tesla charged just fine for years, the problem was with the car. But bmw says it isn’t…

Any advice?

Good evening,

When you check the evcs, does it gives any alarm there?

Regards, Jeroen.

Nope, no sign of an alarm.

Good evening,

A red colour on the evcs normally tells that there is something wrong…

Do you charge only with solar or do you have it set to scheduled?

Maybe yours is listed for recall, check below;

Then the recall vehicles; • • Codes: KBA 16565R | BMW Internal Code 0061750900• Affected Vehicles: 145 units produced between November 25, 2025, and February 20, 2026.• The Defect: An anomaly in the high-voltage charging electronics can energize the metal bodywork during charging, creating a risk of electric shock.• The Fix: Complete replacement of the affected charging subsystem at an authorized service point for free.

Regards, Jeroen.

Hi,

There isn’t much sun at the moment, so I’m only charging manually.

No red light is showing.

The car was manufactured in June 2026. The garage checked everything last week; the car is completely normal, and they can’t reproduce the problem. I don’t have any problems when charging at a public charging point either. It’s very frustrating.

Hi Jochen,

The message in the BMW app caught my eye: “Battery status: not charging. Reconnect or use a DC charging station.” You say the car charged fine at the dealer’s and at a public charging point. Was it AC charging or DC rapid charging in both cases? If it was only DC, it would be useful to test at another AC charging point to check the car’s AC charging function.

To narrow down the problem further, I have a few more questions:

  • What charging current do you use at home? Does the fault also occur at a significantly lower, fixed charging current?

  • What are the exact firmware versions of the EVCS and the Cerbo? “The latest version” is difficult to compare after the fact.

  • Do you use the same charging cable at the other AC charging points? If so, have you tried a different cable yet?

  • Do you see anything unusual in VRM around the time charging stops, for example a voltage dip, a high load on one phase or an inverter warning?

Since you now say that you charge manually and the EVCS isn’t showing an error message, I wouldn’t consider OPL the main suspect for now.

I’d also ask an electrician to check the connections, neutral conductor and earthing, including the voltages between the phases and from each phase to neutral and earth, especially while charging. The fact that the Tesla charged without any problems for years is a good indication, but it doesn’t completely rule out a problem with the power supply or its interaction with the BMW.

Greetings from the Var,
Philip

Hi,

The charger in the garage and the public charging point were AC. I haven’t tried DC charging yet.

The issue occurs at all current levels: from 6 to 16 A (at home).

EVCS firmware: 2.09

erbo firmware: 3.85

I’ve tried two different cables (both from different brands and compatible with 22 kW), but the problem persists.

I’ll measure the voltages on the different phases and get back to you.

Thanks in advance, everyone, for helping me think this through.

Hello Jochen,

Thanks for the additional information. Since the BMW charges properly at two other AC charging points, and the problem occurs at home with both cables and at all charging currents, I’d try charging another electric car on your EVCS. Ideally, one that also charges on three phases and can be left charging long enough to get past the point at which the BMW usually stops.

  • If that car also stops, that points more towards the EVCS or the power supply.

  • If it keeps charging without any problems, the issue is more likely to be the interaction between the BMW and the EVCS.

I assume you’ve already checked the fuses/circuit breakers. Also take a look at the Victron console while someone starts charging the BMW: does the power increase on all three phases?

There could be a loose connection or poor contact somewhere, for example in a Wago connector, at a circuit breaker or at the EVCS connection. The fact that the Tesla used to charge properly doesn’t rule out a contact problem that has developed since then.

As an initial guide, for a typical 230/400 V installation, you’d expect:

  • Between L1–L2, L2–L3 and L3–L1: approximately 400 V.

  • Between each phase and N: approximately 230 V.

  • Between each phase and PE: also approximately 230 V.

  • Between N and PE: a low voltage, usually close to 0 V; there may be some difference under load.

The behaviour while charging is especially interesting: does the voltage on any phase drop significantly, or does the voltage between N and PE change noticeably? Normal voltage readings with no load don’t rule out a poor connection.

If this isn’t your area of expertise, have an electrician check the connections and take the measurements. Working on and measuring 230/400 V isn’t a suitable DIY job for someone without the right knowledge and test equipment.

Greetings from the Var,
Philip

Measured under load:

Voltage between the phases: 385 V

Voltage between phases and N: 224 V, 216 V and 222 V

Voltage between N and earth: 8 V

I’ve checked all the connections, and as far as I can see they’re OK. (I work with electricity every day, so that’s not a problem. However, this is a problem I can’t currently explain, other than perhaps a small communication issue between the car and the charger.)

Kind regards

(charging stopped again shortly after measuring)

The CP signal on the charging cable is referenced to the earth. If the neutral or earth are bouncing around because of poor earth bonds or a flaky neutral connection somewhere, then the EVCS can act as if the vehicle is charged and just stop charging. The signalling is at 12/9/6 volts, so a little bit of common-mode noise can make a difference.

The installation was inspected recently and met all the standards.

Is there anything else you would suggest checking?

Look at the ‘EV Charger State’ graph from the ‘Advanced’ view of VRM, and also ‘EV Charger Power’.

What is reported across your charging cycle:

  • plug car in
  • charge
  • charging fails
  • unplug car
  • plug car in
  • charging starts
  • (… charging fails)

Grab a screenshot of that timeline from the Advanced view of VRM

Update for everyone: today, just to be on the safe side, I ran an extra cable to the earth pin as a process of elimination. Although the inspection said everything was OK, the car has been charging perfectly since I added the extra cable. I hope I’m not speaking too soon and jinxing it, but so far everything looks good.

Hi Jochen,

It’s great that everything is working again. These lines caught my attention:

"Voltages between the phases and N: 224 V, 216 V and 222 V. Voltage between N and earth: 8 V "

8 V is actually too much, and L2 is 6 to 8 V behind L2 and L3. Even if everything is working now and it was supposedly okay, or is okay, I’d take another close look. N and L2 are the ones that stand out. I once had the same thing in a fuse box 75 metres from the house, where my EVCS is connected. It’s a 5G6 cable, and I had 7 V between N and PE. In the end, it was a poor connection in a Wago connector. After it was replaced, I had 0 V between PE and N.

And as Dean wrote, “The signal levels are 12/9/6 volts,” and “The signal runs via PE,” it would be worth taking a look.
Your additional grounding is the aspirin, but perhaps the cause of the headache hasn’t been dealt with ;-). Cheers

Thanks, Dean, I learned something new again :slightly_smiling_face:

I’m carrying out a full inspection of all the connections this weekend!

Update:

After installing the additional earth cable, charging is noticeably better, but still not fault-free. Charging is still interrupted once or twice per session.

All connections from the consumer unit to the charger have been checked and are in good condition.

The voltage between earth and neutral is now 1 V.

The voltage difference (216 V compared with 222 V and 224 V on the other phases) starts at the MultiPlus itself, as measured at the MultiPlus out terminals, so it is not due to a poor connection here either.